Results 1 to 5 of 5
  1. #1
    Join Date
    Apr 2008
    Location
    McKinney Texas
    Posts
    501

    Default What do you think of this water heater connection?

    What do you think of this water heater connection? Two listed metal segments connected together with PEX segment. What do you think? See photos.

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Crawl Space Creeper

  2. #2
    Join Date
    Mar 2007
    Location
    Columbus GA
    Posts
    3,747

    Default Re: What do you think of this water heater connection?

    Where does the TPR drain too on the right tank?
    No TPR drain on the left tank.

    Where do the pans drain too?
    Is there a cold water shutoff? (Don't see one)

    No sediment traps on gas line.
    Will the 1/2" Tee supply gas for two WH?

    I don't know of any thing wrong with using a pex connector

    ' correct a wise man and you gain a friend... correct a fool and he'll bloody your nose'.

  3. #3
    Join Date
    Apr 2008
    Location
    McKinney Texas
    Posts
    501

    Default Re: What do you think of this water heater connection?

    Quote Originally Posted by Rick Cantrell View Post
    Where does the TPR drain too on the right tank?
    No TPR drain on the left tank.

    Where do the pans drain too?
    Is there a cold water shutoff? (Don't see one)

    No sediment traps on gas line.
    Will the 1/2" Tee supply gas for two WH?

    I don't know of any thing wrong with using a pex connector

    Hello Rick, the installation of the water heaters was still in progress so there were other things missing as well. I agree, the PEX connector looked okay to me, I just thought I would run it up the flag pole since I don't see this type of connector that often. It appears to be a "Listed" connector.

    Thanks


  4. #4
    Join Date
    Mar 2007
    Location
    Columbus GA
    Posts
    3,747

    Default Re: What do you think of this water heater connection?

    Quote Originally Posted by Gene South View Post
    ... the PEX connector looked okay to me, I just thought I would run it up the flag pole since I don't see this type of connector that often. It appears to be a "Listed" connector.

    Thanks
    I agree
    When something is unusual, it's usually not right.

    ' correct a wise man and you gain a friend... correct a fool and he'll bloody your nose'.

  5. #5
    Join Date
    Mar 2007
    Location
    Near Philly, Pa.
    Posts
    1,682

    Default Re: What do you think of this water heater connection?

    What are the input BTU/hr ratings? if 75mbh or less must be FVIR. Can't tell on these.
    Close ups of vent connectors to vent and to draft hoods?
    TPR on L
    TPR discharge point?
    Is that CPVC on R TPR?
    Pan drainage?
    Sed. trap.
    Gas pipe sizing?
    Bollard
    strapped to wall
    MUA calculation cubic footage
    Left gas flex connector appears to be greater than 3 ft.

    PEX splice odd but allowed far as I know.

    Keep the fire in the fireplace.

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •