    Default "Sub Panel" Connections

    This panel is connected to the main service panel and a few things don't look right to me.

    1. Can you share ground and neutral bus if a metal nipple is used for close connection? (white tape on neutral wire)

    2. Is it OK to have the neutral connections for the two single pole breakers in the sub panel located remotely in the main service panel?

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Inspection Referral
    Ken Amelin
    Cape Cod's Best Inspection Services
    www.midcapehomeinspection.com

  2. #2
    Will Hansen's Avatar
    Will Hansen Guest

    Default Re: "Sub Panel" Connections

    Quote Originally Posted by Ken Amelin View Post
    This panel is connected to the main service panel and a few things don't look right to me.

    1. Can you share ground and neutral bus if a metal nipple is used for close connection? (white tape on neutral wire)

    2. Is it OK to have the neutral connections for the two single pole breakers in the sub panel located remotely in the main service panel?
    The neutrals and EGC's cannot share the same bar in a sub panel. The ground strap needs to be removed and a separate ground bar (not bus) should be installed.

    - - - Updated - - -

    Quote Originally Posted by Ken Amelin View Post
    This panel is connected to the main service panel and a few things don't look right to me.

    1. Can you share ground and neutral bus if a metal nipple is used for close connection? (white tape on neutral wire)

    2. Is it OK to have the neutral connections for the two single pole breakers in the sub panel located remotely in the main service panel?
    The neutrals and EGC's cannot share the same bar in a sub panel. The ground strap needs to be removed and a separate ground bar (not bus) should be installed.


  3. #3
    Join Date
    Mar 2010
    Location
    Prairie du Sac, Wisconsin
    Posts
    9

    Default Re: "Sub Panel" Connections

    Quote Originally Posted by Ken Amelin View Post
    This panel is connected to the main service panel and a few things don't look right to me.

    1. Can you share ground and neutral bus if a metal nipple is used for close connection? (white tape on neutral wire)

    2. Is it OK to have the neutral connections for the two single pole breakers in the sub panel located remotely in the main service panel?
    I see a bonding screw and clip. I believe it should be removed from the sub panel. Not sure about the conduit connection. I think as long as the box is not bonded that it'd OK. Anyone else got an opinion?


  4. #4
    Join Date
    Aug 2008
    Location
    Maryland
    Posts
    1,970

    Default Re: "Sub Panel" Connections

    The ground bar is missing. Once installed the grounding conductors need to be moved to the ground bus.

    All conductors of the circuit need to originate in the same panel.

    All answers based on unamended National Electrical codes.

  5. #5
    Mbrooke's Avatar
    Mbrooke Guest

    Default Re: "Sub Panel" Connections

    Not right, remove neutral buss to case bond, add ground bar, move grounds to new ground bar. Also 2 circuits are going into the main panel rather than having all conductors originate from the the sub.


  6. #6
    Join Date
    Mar 2007
    Location
    Cape Cod, Massachusetts
    Posts
    614

    Default Re: "Sub Panel" Connections

    Quote Originally Posted by Jim Port View Post
    The ground bar is missing. Once installed the grounding conductors need to be moved to the ground bus.

    All conductors of the circuit need to originate in the same panel.
    Jim,

    I get the issue regarding the neutral and ground bars. That's what I thought but just wanted to confirm here.

    But what do you mean when you say "All conductors need to "originate" in the same panel. In the photo it looks like all the conductors for the two single pole breakers "originate" in the same panel except that the hot conductors then "protrude" into the adjacent panel.

    Can you reference a code section for this comment?
    Thanks!

    Ken Amelin
    Cape Cod's Best Inspection Services
    www.midcapehomeinspection.com

  7. #7
    Join Date
    Jul 2010
    Location
    Wisconsin
    Posts
    274

    Default Re: "Sub Panel" Connections

    Quote Originally Posted by Ken Amelin View Post
    Jim,

    But what do you mean when you say "All conductors need to "originate" in the same panel. In the photo it looks like all the conductors for the two single pole breakers "originate" in the same panel except that the hot conductors then "protrude" into the adjacent panel.

    Can you reference a code section for this comment?
    Thanks!
    Thought that was only for MWBC under 210.4(D) Grouping (2008 NEC), I'm interested to know as well.