    Sanyo spit system A/C compressor in attic.

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Member Benefits1

  2. #2
    Join Date
    Aug 2007
    Location
    Memphis TN.
    Posts
    4,311

    Default Re: Seeing is believing

    Quote Originally Posted by Richard Roshak View Post
    Sanyo spit system A/C compressor in attic.
    Well t is New Jersey.

    Plus it sure will slow down them Pesky AC Crooks.

    It Might have Choked Artie But it ain't gone'a choke Stymie! Our Gang " The Pooch " (1932)
    Billy J. Stephens HI Service Memphis TN.

  3. #3
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: Seeing is believing

    Quote Originally Posted by Richard Roshak View Post
    Sanyo spit system A/C compressor in attic.
    Yeppers, there is a reason they are rated for 'Outdoor Use' ...

    Where to start - improperly installed in an improper location without sufficient clearances ... corrective action is to remove from attic and locate in a proper outdoor location.

    The wiring between the two units was thermostat cable or what other type? I ask because all of those that I have inspected called for THWN or similar copper conductors between the two units as that supplied the operating power to the indoor unit - thermostat cable was a no-no in those installations.