    Default GEC splice in panel

    GEC was spliced in the panel with a splice connector. GECs can't be spliced, correct?

    Inspection Referral

  2. #2
    Join Date
    Aug 2008
    Location
    Maryland
    Posts
    1,970

    Default Re: GEC splice in panel

    If spliced the splice must be irreversible, otherwise it needs to be continuous. A thermal weld is also allowed.

    All answers based on unamended National Electrical codes.

  3. #3
    Join Date
    Jan 2014
    Location
    India
    Posts
    13

    Default Re: GEC splice in panel

    I want to suggest for GEC splice. Firstly, you can replace splice with a single crimped connector. A single irreversible compression connection has a strong opinion for proper splice.