Results 1 to 12 of 12
  1. #1
    Clay White's Avatar
    Clay White Guest

    Default Flex Air Duct allowed?

    Last edited by Clay White; 01-02-2008 at 02:22 PM.
    OREP Insurance

  2. #2
    Join Date
    Aug 2007
    Location
    Memphis TN.
    Posts
    4,311

    Default Re: Flex Air Duct allowed?

    Clay

    It's UGLY but I can't find anything that would prohibit it .

    It Might have Choked Artie But it ain't gone'a choke Stymie! Our Gang " The Pooch " (1932)
    Billy J. Stephens HI Service Memphis TN.

  3. #3
    Join Date
    Mar 2007
    Location
    Plano, Texas
    Posts
    4,245

    Default Re: Flex Air Duct allowed?

    If the separation wall between the house and garage puts the duct in the garage, then the duct is wrong. If the heater is "in the house" on the house side of the separation wall between the house and garage, then it would be OK.
    From what I see around here, it would be wrong since the W/H closet door would not be an approved door between the house and garage, thus the separation wall would be the back wall of the W/H closet. That would also mean the OSB would violate the separation requirement of 1/2" gypsum, assuming you are on the IRC.

    Jim Luttrall
    www.MrInspector.net
    Plano, Texas

  4. #4
    Join Date
    Mar 2007
    Location
    Healdsburg, CA
    Posts
    1,741

    Default Re: Flex Air Duct allowed?

    Clay
    Just how do you know that's a flex air duct?

    Jerry McCarthy
    Building Code/ Construction Consultant

  5. #5
    Join Date
    Aug 2007
    Location
    Memphis TN.
    Posts
    4,311

    Default Re: Flex Air Duct allowed?

    Quote Originally Posted by Jim Luttrall View Post
    If the separation wall between the house and garage puts the duct in the garage, then the duct is wrong. If the heater is "in the house" on the house side of the separation wall between the house and garage, then it would be OK.
    From what I see around here, it would be wrong since the W/H closet door would not be an approved door between the house and garage, thus the separation wall would be the back wall of the W/H closet.
    Jim L,

    IF the Left wall(duct) back wall both house walls.

    Right Wall Garage.

    Bring me up to speed on the door please

    Last edited by Billy Stephens; 10-17-2007 at 08:57 PM. Reason: vent to duct
    It Might have Choked Artie But it ain't gone'a choke Stymie! Our Gang " The Pooch " (1932)
    Billy J. Stephens HI Service Memphis TN.

  6. #6
    Join Date
    Aug 2007
    Location
    Memphis TN.
    Posts
    4,311

    Default Re: Flex Air Duct allowed?

    Quote Originally Posted by Clay White View Post
    Rear of the closet is the master bathroom.
    Right of the closet is garage space.
    Left of the closet is exterior.
    Clay,

    So The DUCT goes outside.

    It Might have Choked Artie But it ain't gone'a choke Stymie! Our Gang " The Pooch " (1932)
    Billy J. Stephens HI Service Memphis TN.

  7. #7
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,036

    Default Re: Flex Air Duct allowed?

    Clay,

    First this needs to be answered: What kind of door is it? All the door needs to be is solid core 1-3/8", i.e., just a regular old cheap 1-3/8" solid core door.

    R309.1 Opening protection.
    Openings from a private garage directly into a room used for sleeping purposes shall not be permitted. Other openings between the garage and residence shall be equipped with solid wood doors not less than 13/8 inches (35 mm) in thickness, solid or honeycomb core steel doors not less than 13/8 inches (35 mm) thick, or 20-minute fire-rated doors.



    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  8. #8
    Join Date
    Mar 2007
    Location
    Plano, Texas
    Posts
    4,245

    Default Re: Flex Air Duct allowed?

    What Jerry said.
    The entire section of R309 deals with garages and carports.
    The main theory here is "309.2 Separation required. The garage shall be separated from the residence and its attic area..." and then goes on into specifics.
    In general, the common walls and ceiling have to have gypsum board on the garage side and proper doors on any openings through the separation wall.

    Jim Luttrall
    www.MrInspector.net
    Plano, Texas

  9. #9
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,036

    Default Re: Flex Air Duct allowed?

    Quote Originally Posted by Jim Luttrall View Post
    In general, the common walls and ceiling have to have gypsum board on the garage side and proper doors on any openings through the separation wall.
    To continue what Jim said ...

    *IF* the door is one of the correct type doors, then the OSB ceiling is not a problem and neither is the duct.

    *IF NOT* (if the door is not a correct type door), then *both* are problems.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  10. #10
    Join Date
    Aug 2007
    Location
    Memphis TN.
    Posts
    4,311

    Default Re: Flex Air Duct allowed?

    Quote Originally Posted by Jim Luttrall View Post
    From what I see around here, it would be wrong since the W/H closet door would not be an approved door between the house and garage, assuming you are on the IRC.
    Quote Originally Posted by Billy Stephens View Post

    Bring me up to speed on the door please
    Quote Originally Posted by Jerry Peck View Post

    R309.1 Opening protection.
    Openings from a private garage directly into a room used for sleeping purposes shall not be permitted. Other openings between the garage and residence shall be equipped with solid wood doors not less than 13/8 inches (35 mm) in thickness, solid or honeycomb core steel doors not less than 13/8 inches (35 mm) thick, or 20-minute fire-rated doors.

    Must be a lot of Hollow core doors in Texas . I pictured some (magical) special door based on combination of what wall is who? Appendix # ****

    Thanks

    It Might have Choked Artie But it ain't gone'a choke Stymie! Our Gang " The Pooch " (1932)
    Billy J. Stephens HI Service Memphis TN.

  11. #11
    buddy brault's Avatar
    buddy brault Guest

    Default Re: Flex Air Duct allowed?

    Clay the door is the key as everbody says but if it is a solid door, looks like there may be some combustion air issues.


  12. #12
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,036

    Default Re: Flex Air Duct allowed?

    Quote Originally Posted by buddy brault View Post
    Clay the door is the key as everbody says but if it is a solid door, looks like there may be some combustion air issues.
    To expand on Buddy's "solid door" (not "solid core" door) statement above ...

    *Even if* it is a "louvered door" (versus a "solid door") there are likely combustion issues.

    In thinking about "the door" I 'thought right over' the combustion air issue (meaning I forgot about it ).

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •