Results 1 to 11 of 11
  1. #1
    Join Date
    Feb 2008
    Location
    Caledon, Ontario
    Posts
    4,982

    Default Electrical Panel At Pool

    Todays defect -

    Electrical panel within 12' of in ground pool.

    Ground fault protected from main panel in house, but the completely open to the elements.

    Yes that is snow behind the panel and on the panel.

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    OREP Insurance

  2. #2
    Gerry Bennett's Avatar
    Gerry Bennett Guest

    Default Re: Electrical Panel At Pool

    [QUOTE=Raymond Wand;236499]Todays defect -

    Electrical panel within 12' of in ground pool.

    Ground fault protected from main panel in house, but the completely open to the elements.

    Yes that is snow behind the panel and on the panel.[

    Doesn't look like a raintight enclosure, looks like indoor romex wiring, and I think we should be seeing some kind of ground wire, usually #8 solid.


  3. #3
    Join Date
    Feb 2008
    Location
    Caledon, Ontario
    Posts
    4,982

    Default Re: Electrical Panel At Pool

    I agree the whole thing is wrong. I called it out for further investigation by electrician prior to close of title and that it required weather proof enclosure. You can bet that panel was not installed by any licenced electrician.

    This house was over 100 years old and an addition added and renovations completed to the original house. In my report I stressed to my client and their agent to have their lawyer check that building permit and electrical inspections were carried out prior to close of title.

    Of course the owner of the house is allegedly a contractor! Hmmm, yeah, right!

    Thanks


  4. #4
    Join Date
    Feb 2008
    Location
    Chicago IL
    Posts
    2,048

    Default Re: Electrical Panel At Pool

    Screw further investigation
    Full removal by licensed electrician prior to warm weather and yard/pool use; D&H condition; properly install exterior rated panel at secure location.
    Not only is the install hazardous but it leaves itself open to posing additional hazards based on human behaviour ... bored little boys running around the pool, ooh whats this thing, start playing with the breakers, putting their wet hands all over the panel, etc.
    Dead kids means the phone is going to ring
    Beyond that the romex could easily get damaged and pose an electrocution hazard
    Sorry but when I see pictures like that I don't write the report light

    www.aic-chicago.com
    773/844-4AIC
    "The Code is not a ceiling to reach but a floor to work up from"

  5. #5
    Join Date
    Feb 2009
    Location
    Southern Vancouver Island
    Posts
    4,607

    Default Re: Electrical Panel At Pool

    Quote Originally Posted by Markus Keller View Post
    Screw further investigation
    Further investigation of the binder twine is called for. We want to know why.
    Probably a plastic bag that blew away in the wind.

    Since the work was probably done by an amateur without a permit, Raymond is right to warn the buyer that some hidden problems may exist - further evaluation, investigation or say it another way.

    John Kogel, RHI, BC HI Lic #47455
    www.allsafehome.ca

  6. #6
    Join Date
    Feb 2008
    Location
    Caledon, Ontario
    Posts
    4,982

    Default Re: Electrical Panel At Pool

    ... and yes the 'implications' of such an installation where documented in the report.


  7. #7
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,036

    Default Re: Electrical Panel At Pool

    Quote Originally Posted by Markus Keller View Post
    Screw further investigation
    Full removal by licensed electrician prior to warm weather and yard/pool use;
    .
    .
    Sorry but when I see pictures like that I don't write the report light
    Completely agree with Markus - there is no reason for anyone to further investigate anything there - remove that sucker ASAP and replace it with the proper equipment for the job and its location.

    I would hit things like that with both barrels and follow it up with a few blasts from the old Gatling Gun, and a Surface to Air missile or two just for good measure to make sure the point was clearly made. By the time I was through explaining why it should be removed, at least seven people would be dead from it.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  8. #8
    Join Date
    Dec 2009
    Location
    Florida
    Posts
    553

    Default Re: Electrical Panel At Pool

    Quote Originally Posted by Jerry Peck View Post
    Completely agree with Markus - there is no reason for anyone to further investigate anything there - remove that sucker ASAP and replace it with the proper equipment for the job and its location.

    I would hit things like that with both barrels and follow it up with a few blasts from the old Gatling Gun, and a Surface to Air missile or two just for good measure to make sure the point was clearly made. By the time I was through explaining why it should be removed, at least seven people would be dead from it.
    Jerry, you have a way with words.......


  9. #9
    Join Date
    Sep 2007
    Location
    Fredericksburg, VA
    Posts
    895

    Default Re: Electrical Panel At Pool

    Quote Originally Posted by Jerry Peck View Post
    Completely agree with Markus - there is no reason for anyone to further investigate anything there - remove that sucker ASAP and replace it with the proper equipment for the job and its location.

    I would hit things like that with both barrels and follow it up with a few blasts from the old Gatling Gun, and a Surface to Air missile or two just for good measure to make sure the point was clearly made. By the time I was through explaining why it should be removed, at least seven people would be dead from it.
    I'm with Markus and Jerry. There is no need for further investigation or "evaluation". It's a completely bad and dangerous installation.

    The above statements are expressed solely as my opinion and in all probability will conflict with someone else's.
    Stu, Fredericksburg VA

  10. #10
    Mbrooke's Avatar
    Mbrooke Guest

    Default Re: Electrical Panel At Pool

    Fire and shock hazard par excellence.


  11. #11
    Join Date
    Jan 2014
    Location
    India
    Posts
    13

    Default Re: Electrical Panel At Pool

    All wiring installed in a common conduit system must either not be Ground Fault protected.Pool circuits shall be identified in the circuit breaker panel.


    Thanks
    epackpolymers.com


Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •