Results 1 to 15 of 15
  1. #1
    Terre G's Avatar
    Terre G Guest

    Default Air Admitance Valve in Manufactured Home

    While touring a manufactured home factory I was surprised to see they were using AAV (studor vents) and hiding them in the wall. They cover them with No access, or accessible panel. I asked the state inspector there, and he said this was accepted and approved by the state of Oregon.


    [img]StudorVentMFH.jpg[/img]

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Inspection Referral

  2. #2
    Join Date
    Mar 2007
    Location
    Plano, Texas
    Posts
    4,245

    Default Re: Air Admitance Valve in Manufactured Home

    Mobil homes and the rules are screwy, but then the AAV will likely outlast the home especially here in Tornado Alley!
    Jim

    Jim Luttrall
    www.MrInspector.net
    Plano, Texas

  3. #3
    dick whitfield's Avatar
    dick whitfield Guest

    Default Re: Air Admitance Valve in Manufactured Home

    That seems like a bad idea....


  4. #4
    Tim Moreira's Avatar
    Tim Moreira Guest

    Default Re: Air Admitance Valve in Manufactured Home

    So if you ever have to replace it you need to call a drywaller after the plumber, who took a sledge hammer to the wall to gain access.

    Atta boy.


  5. #5
    Charles Sessums's Avatar
    Charles Sessums Guest

    Default Re: Air Admitance Valve in Manufactured Home

    Quote Originally Posted by Terre G View Post
    While touring a manufactured home factory I was surprised to see they were using AAV (studor vents) and hiding them in the wall. They cover them with No access, or accessible panel. I asked the state inspector there, and he said this was accepted and approved by the state of Oregon.


    [img]StudorVentMFH.jpg[/img]
    Thats not a studor brand vent. It's a cheap knock off. Orange box stuff. Allowed in manufactured homes but not in stick built. IPC 917.4 states access shall be provided. Height is wrong also.

    Last edited by Charles Sessums; 04-07-2007 at 06:38 PM.

  6. #6
    Join Date
    Mar 2007
    Location
    Corpus Christi, TX
    Posts
    615

    Question Re: Air Admitance Valve in Manufactured Home

    Charles,
    For my "learned something new today" book, what should the height have been?


  7. #7
    Join Date
    Mar 2007
    Location
    Colorado Springs, CO
    Posts
    1,217

    Default Re: Air Admitance Valve in Manufactured Home

    2003 IRC P3114.4 Location: Individual and branch air admittance valves shall be located a minimum of 4 inches (102 mm) above the horizontal branch drain or fixture drain being vented. Stack-type air admittance valves shall be located a minimum of 6 inches (152 mm) above the flood level rim of the highest fixture being vented. The air admittance valve shall be located within the maximum developed length permitted for the vent. The air admittance valve shall be installed a minimum of 6 inches (152 mm) above insulation materials where installed in attics.

    P3114.5 Access and ventilation. Access shall be provided to all air admittance valves. The valve shall be located within a ventilated space that allows air to enter the valve.

    "Baseball is like church. Many attend but few understand." Leo Durocher
    Bruce Breedlove
    www.avaloninspection.com

  8. #8
    Join Date
    Mar 2007
    Location
    Spring Hill (Nashville), TN
    Posts
    5,851

    Default Re: Air Admitance Valve in Manufactured Home

    That is really a mechanical vent. They are black in color and can be used in manufactured homes.

    A true AAV is white to tan in color and can be used in residential construction.

    Scott Patterson, ACI
    Spring Hill, TN
    www.traceinspections.com

  9. #9
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,040

    Default Re: Air Admitance Valve in Manufactured Home

    As I was typing this I noticed Scott posted the same thing.

    That's not an AAV (not a Studor Vent and not an Oatey AAV), it is a mechanical vent.

    From the IRC.
    - R101.2 Scope. The provisions of the International Residential Code for One- and Two-family Dwellings shall apply to the construction, alteration, movement, enlargement, replacement, repair, equipment, use and occupancy, location, removal and demolition of detached one- and two-family dwellings and townhouses not more than three stories above-grade in height with a separate means of egress and their accessory structures.

    The IRC does not apply to manufactured homes.

    Different rules - DOT I think it is.


    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  10. #10
    Join Date
    Mar 2007
    Location
    Knoxville, TN
    Posts
    2,560

    Default Re: Air Admitance Valve in Manufactured Home

    Terre,
    Since it was under construction, do you know if they put an access panel for the vent?
    JF


  11. #11
    dick whitfield's Avatar
    dick whitfield Guest

    Default Re: Air Admitance Valve in Manufactured Home

    In NC mobile homes are approved by the Dept of Insurance.


  12. #12
    Terre G's Avatar
    Terre G Guest

    Unhappy Re: Air Admitance Valve in Manufactured Home

    Jack,
    I did ask. And NO, they do NOT install access panels. Manufactured Homes are not held to the same standard as site built homes. In fact, here in Oregon, double-wide (and larger) manufactured homes are NOT required to be tied down.

    When I required them be installed on a new double wide on the coastal tsunami and flood zone area, as per the manufacture's installation instructions, the installer complained to the State of Oregon Chief Inspector for Manufactured Homes, and he told the installer not to install them. He then told me that I was violating State law by requiring them! He ignored the fact that we are in a seismic design category D-2, and are in a 110 mph (3 second gust) Wind Zone, as well as in a flood plain and Tsunami Zone!


    I haven't given up on educating the home buyers.


    Terre Gift
    Building Official
    Astoria & Warrenton, Oregon


  13. #13
    Join Date
    Mar 2007
    Location
    Plano, Texas
    Posts
    4,245

    Default Re: Air Admitance Valve in Manufactured Home

    Terre, it sounds like your State official is in the pocket of the industry he is supposed to regulate, Just my opinion. I would be asking for the written regulations to do my own research. I would think that there might even be some federal requirements on this, but maybe not if manufactured within your state and not transported across state lines.
    What about HUD and FHA? If I remember correctly, there are tie-down and foundation requirements on VA loans.
    Of course we all know the train has already left the station on common sense, so that can't be applied here!
    Jim

    Jim Luttrall
    www.MrInspector.net
    Plano, Texas

  14. #14
    TCattell's Avatar
    TCattell Guest

    Default Re: Air Admitance Valve in Manufactured Home

    Hold on for the mechanical vent....Is that a screw on P-trap behind the wall??? I didn't know that was permitted without access!

    Last edited by TCattell; 07-30-2012 at 06:33 PM.

  15. #15
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,040

    Default Re: Air Admitance Valve in Manufactured Home

    Quote Originally Posted by TCattell View Post
    Hold on for the mechanical vent....Is that a screw on P-trap behind the wall??? I didn't know that was permitted without access!
    That mechanical vent requires access too - so, all they will do is put a removable access cover over it all.

    Don't forget, too, that the mechanical vent, as well as AAVs, require ventilation and are not allowed to be in the wall cavity even with a removable access cover unless that access cover is suitably louvered for sufficient and adequate ventilation.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •