    Default WH vent to draft hood connection

    Last edited by Clay White; 01-02-2008 at 02:22 PM.
    Crawl Space Creeper

  2. #2
    Join Date
    Aug 2007
    Location
    Memphis TN.
    Posts
    4,311

    Default Re: WH vent to draft hood connection

    Quote Originally Posted by Clay White View Post
    I just can't put my finger on it, but the wh vent to draft hood connection looks wrong, or am i crazy? Is there a problem?

    (note: insulation clearances are wrong, I know!)
    Clay,

    The first section of vent pipe is a 90 degree elbow that has been straightened out.

    Looks funny,Sloppy, Lazy but no problem I know of it's rated vent.

    Where is the water cut off for wh?

    It Might have Choked Artie But it ain't gone'a choke Stymie! Our Gang " The Pooch " (1932)
    Billy J. Stephens HI Service Memphis TN.

  3. #3
    Kevin Barre's Avatar
    Kevin Barre Guest

    Default Re: WH vent to draft hood connection

    Quote Originally Posted by Billy Stephens View Post
    Clay,
    Where is the water cut off for wh?
    Right there on the inlet to the right opposite the flue. Where the break in the insulation is.


  4. #4
    Join Date
    Mar 2007
    Location
    Connecticut
    Posts
    1,828

    Default Re: WH vent to draft hood connection

    The draft hood has a tapered end for a reason, right. That is so you can shove that sucker right down snug and screw it togeather. Neither of which they got right.


  5. #5
    Join Date
    Mar 2007
    Location
    Philadelphia PA
    Posts
    3,177

    Default Re: WH vent to draft hood connection

    Needs a single-wall to b-vent adapter at the draft hood I do believe.

    "There is no exception to the rule that every rule has an exception." -James Thurber, writer and cartoonist (1894-1961)
    www.ArnoldHomeInspections.com

  6. #6
    Kevin Barre's Avatar
    Kevin Barre Guest

    Default Re: WH vent to draft hood connection

    I can't see a problem based on this photo. So long as the inner liner of the flue sits properly on the diverter, it looks OK to me.