    Default Arc Fault Breaker Temp

    Gentlemen and Ladies,

    Question. At what temperature would you consider an arc fault breaker to be 'too hot' indicating a potential concern? Measured several today that were all around 115*. Other, non arc faults, were all room temperature, 76-77*. I typically find them to them several degrees above non arc faults but not this much warmer.

    Thanks

    Crawl Space Creeper

  2. #2
    Join Date
    Feb 2008
    Location
    Caledon, Ontario
    Posts
    4,982

    Default Re: Arc Fault Breaker Temp

    The temperature rating should be on the breaker, to my knowledge that should be about 40 celcius/104 fahrenheit.


  3. #3
    Join Date
    Mar 2007
    Location
    Charlotte, NC
    Posts
    112

    Default Re: Arc Fault Breaker Temp

    Per the attached from Eaton (a manufacturer of over-current devises, including arc faults), between 80 - 120 F is normal, with higher temps (187 F given as example) still meeting UL listing for the devise.