    Default carport rafters and bearing wall relocation

    Hello all


    First time poster looking for advice.


    We have a carport that is annoyingly just narrow enough not to allow us to park both our vehicles under it. The span of the existing rafters is ~13'6" from the house wall, where they are anchored, to the bearing wall pictured below:





    If I could relocate the bearing wall at the end of the rafters (to just under the gutter in the picture) I could squeeze both cars in without much trouble. The problem--and there's always a problem with stuff like this--is that most of the rafters do not continue past the bearing wall. That is, the little overhang that is visible in the pic (between the bearing wall and end of the roof/gutter) are shorter pieces nailed in between every few rafters. In short, most of them are 'dummies' (there's probably a term to describe those but I don't know it) and only a few rafters span the whole way.


    So, the question is: can i double up on the existing rafters and/or reinforce them in some way that would allow me to move the bearing wall further out? Thanks

    Inspection Referral

  2. #2
    Join Date
    Mar 2007
    Location
    Orlando, FL
    Posts
    1,592

    Default Re: carport rafters and bearing wall relocation

    There's always a way to re-do structure. But you have to do it safely, and it depends on how big a check you want to write.

    Your carport looks like 2x8 rafters on 24 inch centers, so it's already at or just above it's span rating.

    Have a carpenter give you a estimate based on what's actually installed, as there are far too many unseen variables in 1 or 2 photos.


  3. #3
    Join Date
    Nov 2011
    Location
    Oregon, USA
    Posts
    333

    Default Re: carport rafters and bearing wall relocation

    Why not consider inserting a new, full-length rafter midway between each of the existing rafters, and then splice (using moment-capable details) some new tails on the short members? You'd then have 2 x 8s @ 12" centers, which are able to easily span the distance you need for most species of lumber while being subject to 40 PSF liveload, 15 PSF deadload.


  4. #4
    Join Date
    Sep 2009
    Location
    Rolla, MO
    Posts
    136

    Default Re: carport rafters and bearing wall relocation

    2x8 rafters at 12" centers could span about 15.5', however I have never seen an approved moment splice for solid sawn lumber. This assumes a 20 psf snow load, which covers most of your state except for the very northern part. If a center support beam and posts wouldn't be a problem, you leave the rafters at 24" centers and have two 11 foot spans.

    Randy Mayo, P.E.
    Residential Engineering & Inspection Services
    http://www.rlmengineers.com

  5. #5
    Join Date
    Feb 2009
    Location
    Southern Vancouver Island
    Posts
    4,607

    Default Re: carport rafters and bearing wall relocation

    If you sistered each of those 2X8 joists with a full length 2X10, then I believe you could then move the support wall to the outer end of the span.
    The weakest point then would be at the attachment of the original joists to the house. The ledger board if there is one must be attached directly to the structural part of the house with lagbolts. If the original joists have any rot at the house end, then there needs to be repair work done there.

    Use double wide joist hangers with all the nail holes nailed or screwed wih the right screws.

    Then the exterior wall needs to be sheathed, with siding and flashing because it will be exposed to the weather. Build the wall so that the roof slopes away from the house, no ponds. Get a professional builder to do it and learn from him.

    Last edited by John Kogel; 02-11-2014 at 08:47 AM.
    John Kogel, RHI, BC HI Lic #47455
    www.allsafehome.ca

  6. #6
    Join Date
    Nov 2011
    Location
    Oregon, USA
    Posts
    333

    Default Re: carport rafters and bearing wall relocation

    "however I have never seen an approved moment splice for solid sawn lumber"


    Perhaps you need to get out more. With proper splice members, and appropriate connectors, such a splice would be relatively simple to construct. Mid-span support columns won't cut it, unless one doesn't mind chopping holes in the roof of his car.

    Thinking outside of the box is still legal, even though apparently not taught at your engineering school.


  7. #7
    Join Date
    Feb 2008
    Location
    Caledon, Ontario
    Posts
    4,982

    Default Re: carport rafters and bearing wall relocation

    Buy smaller compact cars. Only kidding...


  8. #8
    Join Date
    Sep 2009
    Location
    Rolla, MO
    Posts
    136

    Default Re: carport rafters and bearing wall relocation

    Hi, BridgeMan

    Glad I got your creative juices flowing. The center beam design was for a (two) bay carport option with 11 foot bays, which gives him an option to salvage most of the existing carport roof. The existing roof is over spanned at 13.5 feet, so reducing the span to 11 feet puts the existing roof rafters within acceptable design criteria. As far as the moment splices are concerned, send me some info or a link for a solid sawn lumber moment splice. I would love to have that information, but it would have to have some solid engineering behind it before I would put my stamp on it.

    Randy Mayo, P.E.
    Residential Engineering & Inspection Services
    http://www.rlmengineers.com

  9. #9
    Join Date
    Sep 2009
    Location
    Rolla, MO
    Posts
    136

    Default Re: carport rafters and bearing wall relocation

    oifla a,

    If you widen the existing carport, pay close attention to the carport's connection to the house. This is typically the weakest link in most carport roofs that rely on the house to support one side.

    Randy Mayo, P.E.
    Residential Engineering & Inspection Services
    http://www.rlmengineers.com

  10. #10
    Join Date
    Nov 2011
    Location
    Oregon, USA
    Posts
    333

    Default Re: carport rafters and bearing wall relocation

    Mr. Mayo,

    Let me see if I understand what you said--you want me to send you someone else's design and calculations, so you could then stamp them (with your P.E. stamp)? Wow.

    Most state engineering licensing agencies frown on that sort of thing, and take strong disciplinary action against the perpetrators. Things must be different in Missouri, for you to be openly soliciting work done by others for stamping as your own.


  11. #11
    Join Date
    Sep 2009
    Location
    Rolla, MO
    Posts
    136

    Default Re: carport rafters and bearing wall relocation

    BridgeMan,

    Your taking this way to personal. All I wanted to see is if you have information on a design method not example, that is approved by the Nation Design Specifications for Wood Construction (NDS). The only information on a moment splice I can find is for Glu-Lam beams. I read on some structural engineering site the Eurocode may have an approved method for a moment splice, but I have not found it. Someone's example calculations are no good to me without some empirical testing data to back it up. Send me a website link, title of a design manual, name of a consulting firm, organization or individual that has design information on solid sawn lumber moment splices.

    Randy Mayo, P.E.