    Smile Another ground question

    I continue to see ground wires braided in service panels and was wondering if there was a memo sent out to electricians I missed? Does anyone else see this and how do you write it up?

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Crawl Space Creeper

  2. #2
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: Another ground question

    Quote Originally Posted by Jim McClendon View Post
    Does anyone else see this
    Not as often as I used to.

    and how do you write it up?
    Yes, write it up as improperly terminated. I see two twisted groups of grounds, so they likely go to two terminals. To my knowledge, most ground terminals are rated for no more than two conductors, and there is one brand which I think might be rated for three ground conductors (someone posted that here a couple of times in response to my statement about being limited to two). Nonetheless, more than three is too many for terminals rated for three, just like more than two are too many for terminals rated for two.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  3. #3
    Jim McClendon's Avatar
    Jim McClendon Guest

    Default Re: Another ground question

    Thanks Jerry. I didn't mean to revisit this subject with you (it was covered pretty good in a previous post) ...just curious where else it showed up around the country.


  4. #4
    Join Date
    Mar 2007
    Location
    Santa Rosa, CA
    Posts
    3,154

    Default Re: Another ground question

    I see it mostly in older installations. Twisted together, sometimes in a single large terminal, sometimes with a split bolt, sometimes with one of the conductors connected to a ground screw attached to the panel.

    Department of Redundancy Department
    Supreme Emperor of Hyperbole
    http://www.FullCircleInspect.com/