    Jun 2008
    Default copper clad aluminum branch circuits
    Just to be sure, am I correct in concluding that copper clad AL conductors also need to be upsized just the same as standard AL?
    For instance, a 20amp circuit will need #10 copper clad AL?
    Default Re: copper clad aluminum branch circuits
    Think of copper clad aluminum as aluminum conductors (they are aluminum conductors), so, yes, they get sized the same as aluminum conductors are sized.
    Copper clad aluminum conductors also only go in terminals rated for aluminum, not terminals rated only for copper.
    Jun 2008
    I was pretty sure of it but just wanted confirmation. Thanks Jerry.
    Apr 2009
    NY State
    It's not that they are "upsized", it's that AL has a different amperage rating that CU. That's why AL conductors are typically larger than CU.
    That's why they are "upsized".
    Mbrooke's Avatar
    Mbrooke Guest
    Yup!
    Just to sum it up,
    14 gauge CU would mean 12 gauge AL for 15 amps
    12 gauge CU would mean 10 gauge AL for 20 amps
    10 gauge CU would mean 8 gauge AL for 30 amps
    Above those sizes you would typically go to stranded AL. As a general rule of thumb if you see 14 gauge NM its automatically CU. If no 14 is present in the house good chance its AL or the sparky just like #12 Kitchen circuits are always 20 amp so if those are #10 they might be AL.
    Quote Originally Posted by Mbrooke View Post
    Or the builder, electrician, and/or owner are aware of voltage drop and have wired accordingly. That is unusual to find in regular production houses, but many of the builders and electricians doing high end large houses understand the need to address voltage drop and run #12 CU for 15 amp circuits and #10 CU for 20 amp circuits.
    Including #10 CU for kitchen circuits.
    Some will say it is not necessary while other understand that it is. Some places you will never see the conductor size adjusted for voltage drop or derating , other places you will see it.
    Mbrooke's Avatar
    Mbrooke Guest
    Good points. There are exceptions to rules of thumb I brought up. Of note just for the sake of it some larger houses will have sub panels on the second floor fed with 2/2/2/4 SER from the main just to address voltage drop.
    You brought up a good fact, some inspectors during construction will fail long runs with to much voltage drop others wont. Truth is if poco is supplying power at 125/250 volts I would be to worried. Even if a 1000 foot run drops it down to 114 volts its still within tolerances, but if poco is giving say 115/230 certainly its a good idea to watch out for voltage drop.
    NEC doesn't directly govern voltage drop but it recommend that a branch circuit doesn't dip below 3% under normal use.