    Default 2006 WATER HEATER IMPROPER VENT SLOPE

    HEY GUYS house built in 2006 with this downward slope on exhaust pipe and rusted exterior vent. i know this is a call out. but what was city inspector looking at. CVF

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    OREP Insurance

  2. #2
    Join Date
    Mar 2008
    Location
    Charlotte NC
    Posts
    2,304

    Default Re: 2006 WATER HEATER IMPROPER VENT SLOPE

    Quote Originally Posted by CHARLIE VAN FLEET View Post
    HEY GUYS house built in 2006 with this downward slope on exhaust pipe and rusted exterior vent. i know this is a call out. but what was city inspector looking at. CVF
    Doughnut crumbs in the bottom of his coffee cup?

    The beatings will continue until morale has improved. mgt.

  3. #3
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: 2006 WATER HEATER IMPROPER VENT SLOPE

    You got the gas regulator next to the ignition source, I am sure.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  4. #4
    Join Date
    Apr 2007
    Location
    WESTMINSTER CO
    Posts
    1,152

    Default Re: 2006 WATER HEATER IMPROPER VENT SLOPE

    Quote Originally Posted by Jerry Peck View Post
    You got the gas regulator next to the ignition source, I am sure.
    jerry explain--the exhaust vent should not be that close to gas meter ?


  5. #5
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: 2006 WATER HEATER IMPROPER VENT SLOPE

    Quote Originally Posted by CHARLIE VAN FLEET View Post
    jerry explain--the exhaust vent should not be that close to gas meter ?
    Charlie,

    The gas regulator and its vent should be, as I recall, either 3 feet or 5 feet from an ignition source, the a/ condenser unit is considered an ignition source.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  6. #6
    Join Date
    Apr 2007
    Location
    WESTMINSTER CO
    Posts
    1,152

    Default Re: 2006 WATER HEATER IMPROPER VENT SLOPE

    Quote Originally Posted by Jerry Peck View Post
    Charlie,

    The gas regulator and its vent should be, as I recall, either 3 feet or 5 feet from an ignition source, the a/ condenser unit is considered an ignition source.
    thanks jerry will check that out


  7. #7
    Join Date
    Aug 2007
    Location
    Memphis TN.
    Posts
    4,311

    Default Re: 2006 WATER HEATER IMPROPER VENT SLOPE

    Quote Originally Posted by CHARLIE VAN FLEET View Post
    thanks jerry will check that out
    ......

    Attached Files Attached Files
    It Might have Choked Artie But it ain't gone'a choke Stymie! Our Gang " The Pooch " (1932)
    Billy J. Stephens HI Service Memphis TN.

  8. #8
    Join Date
    Nov 2010
    Location
    Golden
    Posts
    16

    Default Re: 2006 WATER HEATER IMPROPER VENT SLOPE

    Thanks for that! ^^