    I always look for the temper valve when inspect the radiant heat system. But not very often I can find it as pic2. Most scenarios are like pic1. Is the thermostate doing the temper valve job instead? Also I have never seen the temper valve on any indirect heated HW tank.

    Thank you

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Last edited by Peter Louis; 03-20-2014 at 03:41 PM.
    OREP Insurance

  2. #2
    Join Date
    Feb 2009
    Location
    Southern Vancouver Island
    Posts
    4,607

    Default Re: temper heat supply on radiant heat

    Peter, could you write your question in French so we can understand it better?

    A newer system will have the newer technology and the newer plumbing hardware. An old system may not or it may not be comparable. I think the operating temp of the boiler would have a lot to do with whether a tempering valve is needed.

    John Kogel, RHI, BC HI Lic #47455
    www.allsafehome.ca

  3. #3
    Join Date
    Aug 2010
    Location
    BC Canada
    Posts
    368

    Default Re: temper heat supply on radiant heat

    Quote Originally Posted by John Kogel View Post
    Peter, could you write your question in French so we can understand it better?

    A newer system will have the newer technology and the newer plumbing hardware. An old system may not or it may not be comparable. I think the operating temp of the boiler would have a lot to do with whether a tempering valve is needed.
    Thank you John, but all the radiant boiler operating Temps I have found are about 140-170F. I can only see a return pipe back to hot supply. Most chances this pipe has a partially opened shut-off valve before reaching the hot supply pipe.

    Last edited by Peter Louis; 03-20-2014 at 04:05 PM.

  4. #4
    Join Date
    Feb 2009
    Location
    Southern Vancouver Island
    Posts
    4,607

    Default Re: temper heat supply on radiant heat

    Peter, there may be a check valve which allows water into the boiler system but prevents water from the boiler from returning to the fresh water supply. That would be called a 'makeup' valve.

    Excess water in the boiler loop can only blast out of the pressure release valve.

    Maybe you are talking about something else.

    John Kogel, RHI, BC HI Lic #47455
    www.allsafehome.ca

  5. #5
    Join Date
    Mar 2007
    Location
    New Mexico
    Posts
    1,352

    Default Re: temper heat supply on radiant heat

    I'll take a shot at it. I run into this a lot, or at least I think this is what you are referring to. Typical setup: The house has a standard issue boiler connected to in floor radiant heat. Yes, there should be a tempering valve on the boiler that will allow the boiler to operate at 160-180, yet deliver water to the in floor at 120-130. Most houses do not have this, and they try to work around it by either lowering the internal temperature of the boiler or by sending hotter water to the in floor than it should have.

    I've looked up the instructions for the majority of the boilers that I see on a regular basis, and they all call for the tempering valve, often referred to as a mixing valve, if return temperatures will be below 130 degrees F.

    There are certain high efficiency boilers that are designed to run at lower temperatures. These do not require a tempering valve. The Raypak is another unit that doesn't seem to require one, as they have a built in bypass, and according to their manual can be run down to 110 deg F on the return side. The high efficiency boilers are normally a condensing type, and you will see the condensate drain system, as well as the Cat IV vent type.

    Jim Robinson
    New Mexico, USA

  6. #6
    Join Date
    Aug 2010
    Location
    BC Canada
    Posts
    368

    Default Re: temper heat supply on radiant heat

    Quote Originally Posted by Jim Robinson View Post
    I'll take a shot at it. I run into this a lot, or at least I think this is what you are referring to. Typical setup: The house has a standard issue boiler connected to in floor radiant heat. Yes, there should be a tempering valve on the boiler that will allow the boiler to operate at 160-180, yet deliver water to the in floor at 120-130. Most houses do not have this, and they try to work around it by either lowering the internal temperature of the boiler or by sending hotter water to the in floor than it should have.

    I've looked up the instructions for the majority of the boilers that I see on a regular basis, and they all call for the tempering valve, often referred to as a mixing valve, if return temperatures will be below 130 degrees F.

    There are certain high efficiency boilers that are designed to run at lower temperatures. These do not require a tempering valve. The Raypak is another unit that doesn't seem to require one, as they have a built in bypass, and according to their manual can be run down to 110 deg F on the return side. The high efficiency boilers are normally a condensing type, and you will see the condensate drain system, as well as the Cat IV vent type.
    Yes, exactly.


  7. #7
    Join Date
    Jul 2008
    Location
    Utah
    Posts
    390

    Default Re: temper heat supply on radiant heat

    Quote Originally Posted by Jim Robinson View Post
    I'll take a shot at it. I run into this a lot, or at least I think this is what you are referring to. Typical setup: The house has a standard issue boiler connected to in floor radiant heat. Yes, there should be a tempering valve on the boiler that will allow the boiler to operate at 160-180, yet deliver water to the in floor at 120-130. Most houses do not have this, and they try to work around it by either lowering the internal temperature of the boiler or by sending hotter water to the in floor than it should have.

    I've looked up the instructions for the majority of the boilers that I see on a regular basis, and they all call for the tempering valve, often referred to as a mixing valve, if return temperatures will be below 130 degrees F.

    There are certain high efficiency boilers that are designed to run at lower temperatures. These do not require a tempering valve. The Raypak is another unit that doesn't seem to require one, as they have a built in bypass, and according to their manual can be run down to 110 deg F on the return side. The high efficiency boilers are normally a condensing type, and you will see the condensate drain system, as well as the Cat IV vent type.

    I agree. The only bit I'd like to add is that the in-floor radiant heat should never exceed 105 degrees.


  8. #8
    Join Date
    Mar 2007
    Location
    New Mexico
    Posts
    1,352

    Default Re: temper heat supply on radiant heat

    Quote Originally Posted by Rod Butler View Post
    I agree. The only bit I'd like to add is that the in-floor radiant heat should never exceed 105 degrees.
    That's a pretty low number. I use 120 - 125. But, it will depend greatly on where that number is measured, and the type of system. At the return that would probably be about the same as a 120 output temperature. There is a lot of staple up here, which needs a higher delivery temperature than tubing in the slab would need.

    Jim Robinson
    New Mexico, USA

  9. #9
    Join Date
    Jul 2008
    Location
    Utah
    Posts
    390

    Default Re: temper heat supply on radiant heat

    Quote Originally Posted by Jim Robinson View Post
    That's a pretty low number. I use 120 - 125. But, it will depend greatly on where that number is measured, and the type of system. At the return that would probably be about the same as a 120 output temperature. There is a lot of staple up here, which needs a higher delivery temperature than tubing in the slab would need.
    I agree Jim that staple up should run at a higher temp, that's why I said "in-floor" radiant.