    I have an HVAC guy wanting to argue about needing support for a furnace vent pipe that is rising about 10 ft high out of the roof to rise above an adjacent roof structure. I said the pipe needed support and he does not think it does. I do not have a code reference but would like to have one. Pic is deceptive as the pipe at the right is much taller than it looks in this picture. Thanks

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Last edited by Frank Bombardiere; 04-10-2014 at 12:06 PM.
    Member Benefits1
    If it weren't for lawyers, we would never need them.

  2. #2
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: Code ref for supporting tall vent pipes.

    From the 2012 IRC:
    - G2426.5 (502.5) Installation.
    - - Vent systems shall be sized, installed and terminated in accordance with the vent and appliance manufacturer’s installation instructions and Section G2427.
    - G2426.6 (502.6) Support of vents.
    - - All portions of vents shall be adequately supported for the design and weight of the materials employed.

    G2427.6.9 (503.6.11) Support of gas vents.
    - Gas vents shall be supported and spaced in accordance with the manufacturer’s installation instructions.


    G2427.10.9 (503.10.9) Support.
    - A vent connector shall be supported for the design and weight of the material employed to maintain clearances and prevent physical damage and separation of joints.

    Of course, then there is trying to the manufacturer's instructions and what they specify for supporting the vent above the roof,

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  3. #3
    Join Date
    Mar 2007
    Location
    Oklahoma City
    Posts
    357

    Default Re: Code ref for supporting tall vent pipes.

    Quote Originally Posted by Jerry Peck View Post
    From the 2012 IRC:
    - G2426.5 (502.5) Installation.
    - - Vent systems shall be sized, installed and terminated in accordance with the vent and appliance manufacturer’s installation instructions and Section G2427.
    - G2426.6 (502.6) Support of vents.
    - - All portions of vents shall be adequately supported for the design and weight of the materials employed.

    G2427.6.9 (503.6.11) Support of gas vents.
    - Gas vents shall be supported and spaced in accordance with the manufacturer’s installation instructions.


    G2427.10.9 (503.10.9) Support.
    - A vent connector shall be supported for the design and weight of the material employed to maintain clearances and prevent physical damage and separation of joints.

    Of course, then there is trying to the manufacturer's instructions and what they specify for supporting the vent above the roof,
    Thanks Jerry. Yeh, I am not doing that. I have always remembered any vent such as these over 5ft above the roof should be supported.

    If it weren't for lawyers, we would never need them.

  4. #4
    Join Date
    Feb 2008
    Location
    Chicago IL
    Posts
    2,048

    Default Re: Code ref for supporting tall vent pipes.

    As a POI, it hasn't been uncommon for buyers, sellers and contractors to complain 'oh that picky inspector, support smupport, no big deal, whatever, blah, blah,'. Buyer also gets push back on the lack of proper support and backs down, figures oh whatever.
    You may want to include the potential leak concerns in the report. This can be very helpful in getting the issue properly resolved. Buyer's tend to understand 'potential roof leak' better than 'lack of support'. Of course they don't want their roof to leak and demand either a fix or credit.
    Leak issue of course being the swaying pipe breaking the caulk joint or widening out the collar.

    www.aic-chicago.com
    773/844-4AIC
    "The Code is not a ceiling to reach but a floor to work up from"

  5. #5
    Join Date
    Mar 2007
    Location
    Near Philly, Pa.
    Posts
    1,682

    Default Re: Code ref for supporting tall vent pipes.

    In addition to the code references, the 5 foot rule is a good rule of thumb. Remember, it isn't just the whole stack but all those joints. What it usually forgotten is the need for support in the attic in three axis: vertical plus two intersecting horizontal planes. Failure to properly support can stress joints, especially the gores in elbows causing them to blow apart. Tall unprotected vents and chimneys run too cold. They will suffer from weak draft, condensation and sooting with wood. Then there is the leak issue as Marcus pointed out. If you need a vent that tall, it should be encased and supported in a chase.

    Keep the fire in the fireplace.