    Default Determine electic furnace capacity

    I must admit i really don't know how to read an electric furnace tag to determine capactiy any advice?

    Crawl Space Creeper

  2. #2
    Join Date
    Mar 2008
    Location
    Charlotte NC
    Posts
    2,304

    Default Re: Determine electic furnace capacity

    Quote Originally Posted by cory nystul View Post
    I must admit i really don't know how to read an electric furnace tag to determine capactiy any advice?
    If the installer was kind enough to mark the label, it will be in KW. If not you would have to remove the cover to count the number of strips (that is beyond a normal HI). Conversion to BTU is approx 17000 BTU per 5KW strip.

    The beatings will continue until morale has improved. mgt.

  3. #3
    Join Date
    Mar 2007
    Location
    Knoxville, TN
    Posts
    2,560

    Default Re: Determine electic furnace capacity

    Most of the time you can not tell by the tag. Some older units have the kw rating on them, others may have a clue in the model number, but many units do not come from the factory with heat strips installed, they are added after the fact.
    On a recent inspection I found a Rheem heat pump. The m/n was RBHA21 J15SFAAI and it had 14.4 kw heat strips. You might conclude that the 15 was the heat strip rating.
    I always open the front to get a look at the heat strips. Not only can you tell what size the unit is, but you also might find melted wires, etc. Once in a while, I find a heat pump without any heat strips installed.


  4. #4
    Join Date
    Feb 2008
    Location
    Caledon, Ontario
    Posts
    4,982

    Default Re: Determine electic furnace capacity

    10 gauge AWG - 30 amp = 5 KW furnace
    6 gauge AWG - 70 amp = 10 KW furnace
    4 gauge AWG - 100 amp = 15 KW furnace

    1 KW = 3,412 BTU per hour for heating


  5. #5
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: Determine electic furnace capacity

    Quote Originally Posted by Raymond Wand View Post
    30 amp = 5 KW
    .
    .
    70 amp = 10 KW
    .
    .
    100 amp = 15 KW
    ???

    You are calculating based on 240 volts or ???

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  6. #6
    Join Date
    Mar 2011
    Location
    Lombard, Illinois
    Posts
    133

    Default Re: Determine electic furnace capacity

    Quote Originally Posted by Jack Feldmann View Post
    Most of the time you can not tell by the tag. Some older units have the kw rating on them, others may have a clue in the model number, but many units do not come from the factory with heat strips installed, they are added after the fact.
    On a recent inspection I found a Rheem heat pump. The m/n was RBHA21 J15SFAAI and it had 14.4 kw heat strips. You might conclude that the 15 was the heat strip rating.
    I always open the front to get a look at the heat strips. Not only can you tell what size the unit is, but you also might find melted wires, etc. Once in a while, I find a heat pump without any heat strips installed.
    Hi jack, not familiar with heat strips. Do you have a picture you can share.? In my area I don't see many electric furnace in area.
    Thanks

    Fidel F. Gonzales
    RELIANT INSPECTION SERVICE
    http://www.reliant-corp.com

  7. #7
    Join Date
    Aug 2011
    Location
    Bennett (Denver metro), Colorado
    Posts
    1,461

    Default Re: Determine electic furnace capacity

    Interesting. I see an electric forced air furnace maybe once every other year and a heat pump maybe once a year.

    So, I would "assume" that a 15w unit would be for a relatively small home, 1100-1400 sq ft. in a cold climate.

    If you choose not to decide, you still have made a choice.

  8. #8
    Join Date
    Feb 2009
    Location
    Southern Vancouver Island
    Posts
    4,607

    Default Re: Determine electic furnace capacity

    Hey Lonny, it's KiloWatts, not Watts.

    We expect to see a 70 to 100 amp unit for an average smallish 3 bedroom house, and they go up to 125 amp. I don't recall seeing one bigger than 125 amp here but we have mild winters so the heat pump does the bulk of the heating.

    50 amp is about the right size for a manufactured home.

    Please remember to turn off the breaker before removing the cover. This is lethal voltages and the ends of the elements are exposed when you pull the cover, a big piece of metal.

    John Kogel, RHI, BC HI Lic #47455
    www.allsafehome.ca

  9. #9
    Join Date
    Aug 2011
    Location
    Bennett (Denver metro), Colorado
    Posts
    1,461

    Default Re: Determine electic furnace capacity

    Quote Originally Posted by John Kogel View Post
    Hey Lonny, it's KiloWatts, not Watts.
    OOPS, typo.....LOL 15w is a space heater.

    If you choose not to decide, you still have made a choice.

  10. #10
    Join Date
    Mar 2007
    Location
    Columbus GA
    Posts
    3,747

    Default Re: Determine electic furnace capacity

    Quote Originally Posted by Lon Henderson View Post
    OOPS, typo.....LOL 15w is a space heater.
    No, 15 w is a night light

    ' correct a wise man and you gain a friend... correct a fool and he'll bloody your nose'.

  11. #11
    Join Date
    Feb 2009
    Location
    Southern Vancouver Island
    Posts
    4,607

    Default Re: Determine electic furnace capacity

    Fidel, just for you, two pics of an electric furnace. They are boring to see.
    This one was interesting because the builder never got around to installing any ducts in the crawlspace. So I got a shot up into the furnace from below. It was toasty warm down there too.

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    John Kogel, RHI, BC HI Lic #47455
    www.allsafehome.ca

  12. #12
    Join Date
    Mar 2011
    Location
    Lombard, Illinois
    Posts
    133

    Default Re: Determine electic furnace capacity

    Quote Originally Posted by John Kogel View Post
    Fidel, just for you, two pics of an electric furnace. They are boring to see.
    This one was interesting because the builder never got around to installing any ducts in the crawlspace. So I got a shot up into the furnace from below. It was toasty warm down there too.
    John, thanks so much for the pics and your time. Very helpfull