  1. #1
    Join Date
    Mar 2010
    Location
    Ocala Florida
    Posts
    138

    Default Ufer rebar

    Stilt home foundation with piers and continuous bond beam; running 5/8 rebar around perimeter. Question: How is ufer rebar attached to run? Are rebar ties sufficient or should it be welded.
    And is ufer enough or do I need additional ground rod as well. If I'm missing any elements; please fill in the blanks. Thanks

    Inspection Referral

  2. #2
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: Ufer rebar

    Minimum 20 feet of rear - sounds like you have that

    Regular steel tie wires are okay

    GEC is clamped to the rear with a clamp which is listed for CE (concrete encased), Rebar (and size of rebar), usually will also have a paper tag stating it is listed for every use, is a substitute for aspirin, and stops the aging process, etc

    Typically will be cast brass or bronze with SS or brass screws.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  3. #3
    Join Date
    Mar 2010
    Location
    Ocala Florida
    Posts
    138

    Default Re: Ufer rebar

    Quote Originally Posted by Jerry Peck View Post
    Minimum 20 feet of rear - sounds like you have that

    Regular steel tie wires are okay

    GEC is clamped to the rear with a clamp which is listed for CE (concrete encased), Rebar (and size of rebar), usually will also have a paper tag stating it is listed for every use, is a substitute for aspirin, and stops the aging process, etc

    Typically will be cast brass or bronze with SS or brass screws.
    Jerry, thanks, but still not clear on this. I want to bend rebar (ufer) at right angle, attached to one of two 20 foot sections in the bond beam, then route this ufer above grade where I will attach ground clamp and ground wire. Also; how long should the section of the ufer be as it lies along the 20 footer in the bond beam. Does this all sound correct?


  4. #4
    Join Date
    Aug 2008
    Location
    Maryland
    Posts
    1,970

    Default Re: Ufer rebar

    The UFER needs to be in contact with the earth. How would being installed in the bond beam meet this?

    https://www.google.com/url?sa=i&rct=...06404711414460

    All answers based on unamended National Electrical codes.

  5. #5
    Join Date
    Mar 2012
    Location
    Northern Indiana
    Posts
    98

    Default Re: Ufer rebar

    Quote Originally Posted by Jim Port View Post
    The UFER needs to be in contact with the earth. How would being installed in the bond beam meet this?

    https://www.google.com/url?sa=i&rct=...06404711414460
    IMO the concrete needs to be in direct contact with the earth, not the rebar.

    - - - Updated - - -

    Quote Originally Posted by mark petty View Post
    Jerry, thanks, but still not clear on this. I want to bend rebar (ufer) at right angle, attached to one of two 20 foot sections in the bond beam, then route this ufer above grade where I will attach ground clamp and ground wire. Also; how long should the section of the ufer be as it lies along the 20 footer in the bond beam. Does this all sound correct?
    As long as you have 20' or more rebar wire tied together you are good to go.

    - - - Updated - - -

    Quote Originally Posted by mark petty View Post
    Jerry, thanks, but still not clear on this. I want to bend rebar (ufer) at right angle, attached to one of two 20 foot sections in the bond beam, then route this ufer above grade where I will attach ground clamp and ground wire. Also; how long should the section of the ufer be as it lies along the 20 footer in the bond beam. Does this all sound correct?
    As long as you have 20' or more rebar wire tied together you are good to go.

    - - - Updated - - -

    Quote Originally Posted by mark petty View Post
    Jerry, thanks, but still not clear on this. I want to bend rebar (ufer) at right angle, attached to one of two 20 foot sections in the bond beam, then route this ufer above grade where I will attach ground clamp and ground wire. Also; how long should the section of the ufer be as it lies along the 20 footer in the bond beam. Does this all sound correct?
    As long as you have 20' or more rebar wire tied together you are good to go.


  6. #6
    Join Date
    Mar 2010
    Location
    Ocala Florida
    Posts
    138

    Default Re: Ufer rebar

    Quote Originally Posted by Brad Richter View Post
    IMO the concrete needs to be in direct contact with the earth, not the rebar.

    - - - Updated - - -


    As long as you have 20' or more rebar wire tied together you are good to go.

    - - - Updated - - -


    As long as you have 20' or more rebar wire tied together you are good to go.

    - - - Updated - - -


    As long as you have 20' or more rebar wire tied together you are good to go.
    I think I should be calling it a grade beam as it runs from pier footer to pier footer and is below grade. Sorry bout that. Also, still wondering if I'll need an additional and typical ground rod. This is for a personal home that I'm building. I've done others but never did the foundation before, always hired it out. Thanks


  7. #7
    Join Date
    Mar 2012
    Location
    Northern Indiana
    Posts
    98

    Default Re: Ufer rebar

    Quote Originally Posted by mark petty View Post
    I think I should be calling it a grade beam as it runs from pier footer to pier footer and is below grade. Sorry bout that. Also, still wondering if I'll need an additional and typical ground rod. This is for a personal home that I'm building. I've done others but never did the foundation before, always hired it out. Thanks
    Generally, a ufer negates the need for ground rods. Check with your local jurisdiction.


  8. #8
    Join Date
    Aug 2008
    Location
    Maryland
    Posts
    1,970

    Default Re: Ufer rebar

    The NEC does not require another electrode if the cee is used. If another is present they all need to be bonded together.

    To Brad, I agree, I was thinking of how to word that better.


  9. #9
    Join Date
    Mar 2010
    Location
    Ocala Florida
    Posts
    138

    Default Re: Ufer rebar

    Quote Originally Posted by Jim Port View Post
    The NEC does not require another electrode if the cee is used. If another is present they all need to be bonded together.

    To Brad, I agree, I was thinking of how to word that better.
    Hey, thanks everyone


  10. #10
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: Ufer rebar

    Quote Originally Posted by mark petty View Post
    Does this all sound correct?
    Nope.

    Not as I am envisioning it.

    Also "where" in my Florida? Put your city in as your location - that will help.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  11. #11
    Join Date
    Mar 2012
    Location
    Northern Indiana
    Posts
    98

    Default Re: Ufer rebar

    Quote Originally Posted by Jerry Peck View Post
    Nope.

    Not as I am envisioning it.

    Also "where" in my Florida? Put your city in as your location - that will help.
    What's wrong with it? The GEC does not have to be attached to the rebar within the concrete. Extending the rebar out of the footer for later attachment of the GEC is commonly done.


  12. #12
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: Ufer rebar

    Quote Originally Posted by Brad Richter View Post
    What's wrong with it? The GEC does not have to be attached to the rebar within the concrete. Extending the rebar out of the footer for later attachment of the GEC is commonly done.
    Maybe other places (I've seen posts where that is accepted in Texas), but I have not seen anyone approved that in Florida - the concrete encased electrode is the steel in the concrete, the rebar sticking up is not an appropriate GEC.

    Now, if one wanted to attach the GEC to a vertical stub up of rebar, and then encase that vertical stub up in concrete like the rest of the concrete encased electrode, then it would still require a clamp listed for use to be encased in concrete.

    And, to answer Mark's other question/statement, it is not sufficient to simply have 20 feet or more tied together, it needs to be 20 feet long. running a piece around the inside of a 4-1/2 foot by 4-1/2 footing (20 feet of rebar) is not going to cut it.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  13. #13
    Join Date
    Mar 2012
    Location
    Northern Indiana
    Posts
    98

    Default Re: Ufer rebar

    Quote Originally Posted by Jerry Peck View Post
    Maybe other places (I've seen posts where that is accepted in Texas), but I have not seen anyone approved that in Florida - the concrete encased electrode is the steel in the concrete, the rebar sticking up is not an appropriate GEC.

    Now, if one wanted to attach the GEC to a vertical stub up of rebar, and on then encase that vertical stub up in concrete like the rest of the concrete encased electrode, then it would still require a clamp listed for use to be encased in concrete.

    And, to answer Mark's other question/statement, it is not sufficient to simply have 20 feet or more tied together, it needs to be 20 feet long. running a piece around the inside of a 4-1/2 foot by 4-1/2 footing (20 feet of rebar) is not going to cut it.
    I will repeat. The connection of the GEC to the rebar of the concrete encased electrode does NOT need to be encased in concrete.


  14. #14
    Join Date
    Mar 2013
    Location
    Md and or PA
    Posts
    137

    Default Re: Ufer rebar

    Quote Originally Posted by Jerry Peck View Post
    Maybe other places (I've seen posts where that is accepted in Texas), but I have not seen anyone approved that in Florida - the concrete encased electrode is the steel in the concrete, the rebar sticking up is not an appropriate GEC.
    The 2014 NEC has a change in it that does allow this method.

    From the 2014 NEC

    250.68(C)(3)
    A concrete encased electrode of either the conductor type,reinforcing rod or bar installed in accordance with 250.22(A)(3) extended from its location within the concrete to an accessible location above the concrete shall be permitted

    This has been an accepted practice in many jurisdictions across the US for many years now. Maybe not Florida but many other areas.


  15. #15
    Join Date
    Aug 2008
    Location
    Maryland
    Posts
    1,970

    Default Re: Ufer rebar

    I remember reading somewhere about the rebar sticking out of the footer being accepted even though it is not concrete encased. I think the debate started due to word parsing. It really didn't make sense that if the required amount of rebar was in the footing that you could not use the same bar outside of the footer. If you took two 20 foot bars and tied them together but left a stub of a couple of foot out it was unacceptable simply because the stub was not encased.

    To Jerry, why are you saying the pier with 20 foot of bar is no good?

    - - - Updated - - -

    Thanks for posting that Jack. I couldn't remember if that was from the continuing Ed of the IAEI or somewhere else.

    All answers based on unamended National Electrical codes.

  16. #16
    Join Date
    Aug 2011
    Location
    Bennett (Denver metro), Colorado
    Posts
    1,461

    Default Re: Ufer rebar

    Quote Originally Posted by jack davenport View Post
    The 2014 NEC has a change in it that does allow this method.

    From the 2014 NEC

    250.68(C)(3)
    A concrete encased electrode of either the conductor type,reinforcing rod or bar installed in accordance with 250.22(A)(3) extended from its location within the concrete to an accessible location above the concrete shall be permitted

    This has been an accepted practice in many jurisdictions across the US for many years now. Maybe not Florida but many other areas.
    That's the way it has always been in this part of Colorado.

    If you choose not to decide, you still have made a choice.

  17. #17
    Join Date
    Mar 2010
    Location
    Ocala Florida
    Posts
    138

    Default Re: Ufer rebar

    Quote Originally Posted by Jim Port View Post
    I remember reading somewhere about the rebar sticking out of the footer being accepted even though it is not concrete encased. I think the debate started due to word parsing. It really didn't make sense that if the required amount of rebar was in the footing that you could not use the same bar outside of the footer. If you took two 20 foot bars and tied them together but left a stub of a couple of foot out it was unacceptable simply because the stub was not encased.

    To Jerry, why are you saying the pier with 20 foot of bar is no good?

    - - - Updated - - -

    Thanks for posting that Jack. I couldn't remember if that was from the continuing Ed of the IAEI or somewhere else.
    Thanks everyone for the help but still not picturing it; I just want to have it correct for the county inspector when he shows up. I've got 160' feet of grade beam connecting 16 piers with two 5/8 running rebar. I want to use a ufer but not sure how to install it. I know there will be a stub out above grade where I can connect the GEC with appropriate clamp. Its the actual piece of rebar that I will use from the two parallel sections in the grade beam to above grade. Should it be a 20 footer section already installed with a right angle going above grade or can I just use another shorter piece bent and set along side (tied) to one of the two parallel sections and then routed above grade. If the shorter piece is acceptable; how long should it be where it is tied along an already installed piece of rebar.


  18. #18
    Join Date
    Aug 2008
    Location
    Maryland
    Posts
    1,970

    Default Re: Ufer rebar

    As long as the connection is secure I don't see the difference if the stub is part of a full bar or just a couple of feet.

    All answers based on unamended National Electrical codes.

  19. #19
    Join Date
    Mar 2012
    Location
    Northern Indiana
    Posts
    98

    Default Re: Ufer rebar

    Quote Originally Posted by mark petty View Post
    Thanks everyone for the help but still not picturing it; I just want to have it correct for the county inspector when he shows up. I've got 160' feet of grade beam connecting 16 piers with two 5/8 running rebar. I want to use a ufer but not sure how to install it. I know there will be a stub out above grade where I can connect the GEC with appropriate clamp. Its the actual piece of rebar that I will use from the two parallel sections in the grade beam to above grade. Should it be a 20 footer section already installed with a right angle going above grade or can I just use another shorter piece bent and set along side (tied) to one of the two parallel sections and then routed above grade. If the shorter piece is acceptable; how long should it be where it is tied along an already installed piece of rebar.
    The total length of encased rebar must be at least 20'. Wire tied or welded sections of rebar will make up this 20'. A section of rebar properly connected to at least 20' of encased rebar would be acceptable.


  20. #20
    Join Date
    Mar 2010
    Location
    Ocala Florida
    Posts
    138

    Default Re: Ufer rebar

    Quote Originally Posted by Brad Richter View Post
    The total length of encased rebar must be at least 20'. Wire tied or welded sections of rebar will make up this 20'. A section of rebar properly connected to at least 20' of encased rebar would be acceptable.
    Jim, Brad thanks, that is what I was looking for. Sometimes its hard to paint a picture using just words.


  21. #21
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: Ufer rebar

    Quote Originally Posted by Brad Richter View Post
    I will repeat. The connection of the GEC to the rebar of the concrete encased electrode does NOT need to be encased in concrete.
    Quote Originally Posted by jack davenport View Post
    The 2014 NEC has a change in it that does allow this method.

    From the 2014 NEC

    250.68(C)(3)
    A concrete encased electrode of either the conductor type,reinforcing rod or bar installed in accordance with 250.22(A)(3) extended from its location within the concrete to an accessible location above the concrete shall be permitted

    This has been an accepted practice in many jurisdictions across the US for many years now. Maybe not Florida but many other areas.
    Keep in mind that the question came from Florida and Florida is stuck on the 2008 NEC until the new code becomes effective later this year.

    - - - Updated - - -

    Quote Originally Posted by Brad Richter View Post
    The total length of encased rebar must be at least 20'. Wire tied or welded sections of rebar will make up this 20'. A section of rebar properly connected to at least 20' of encased rebar would be acceptable.
    As long as there are not two 10 foot long pieces tied together in a bundle - that is only 10 feet in length even though there is 20 feet or rebar there. Otherwise one could tie 20 one foot pieces of rebar together and claim to have 20 feet of rebar ...

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  22. #22
    Join Date
    Mar 2012
    Location
    Northern Indiana
    Posts
    98

    Default Re: Ufer rebar

    Quote Originally Posted by Jerry Peck View Post
    Keep in mind that the question came from Florida and Florida is stuck on the 2008 NEC until the new code becomes effective later this year.

    - - - Updated - - -



    As long as there are not two 10 foot long pieces tied together in a bundle - that is only 10 feet in length even though there is 20 feet or rebar there. Otherwise one could tie 20 one foot pieces of rebar together and claim to have 20 feet of rebar ...
    You sure can come up with some odd scenarios.


  23. #23
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: Ufer rebar

    Quote Originally Posted by Brad Richter View Post
    You sure can come up with some odd scenarios.
    Brad,

    I can ... when needed to represent the extremes to show the logic missing in some thinking.

    The code wants a 20 foot long concrete encased electrode - minimum.

    Putting 20 feet of rebar in a 5 foot by 5 foot pad footing does not equate to a 20 foot long piece of steel ... to make that difference obvious I simply chopped the 20 feet of rebar into 1 foot pieces ... hey, there is 20 feet of rebar there, right?

    It's a tough job, but someone has to do it.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  24. #24
    Join Date
    Aug 2008
    Location
    Maryland
    Posts
    1,970

    Default Re: Ufer rebar

    Jerry, I am not seeing how someone could reject a 20 foot bar bent into a 5 foot square. The required amount of bar is accounted for and the code does not specify that the bar must be straight or cannot contain bends.

    All answers based on unamended National Electrical codes.

  25. #25
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: Ufer rebar

    Quote Originally Posted by Jim Port View Post
    Jerry, I am not seeing how someone could reject a 20 foot bar bent into a 5 foot square. The required amount of bar is accounted for and the code does not specify that the bar must be straight or cannot contain bends.
    I know of no inspector who would accept it as it does not meet the 20 foot length.

    Clarification: None who get out of their vehicle and actually make inspections.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  26. #26
    Join Date
    Feb 2009
    Location
    Southern Vancouver Island
    Posts
    4,607

    Default Re: Ufer rebar

    JP, would you accept a flat steel plate buried I think it is 3 feet down with a built on clamp? That is allowed here, preferred quite often in fact.

    John Kogel, RHI, BC HI Lic #47455
    www.allsafehome.ca

  27. #27
    Join Date
    Aug 2008
    Location
    Maryland
    Posts
    1,970

    Default Re: Ufer rebar

    To Jerry, I don't see any valid reason to reject it. The 20 foot has been met.

    All answers based on unamended National Electrical codes.

  28. #28
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: Ufer rebar

    Quote Originally Posted by John Kogel View Post
    JP, would you accept a flat steel plate buried I think it is 3 feet down with a built on clamp? That is allowed here, preferred quite often in fact.
    What size is the plate?

    How thick is the plate?

    That is in addition to the concrete encased electrode?

    Many questions before I can answer.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  29. #29
    Join Date
    Feb 2009
    Location
    Southern Vancouver Island
    Posts
    4,607

    Default Re: Ufer rebar

    Just the one plate req'd for the service panel about 18" X 36" buried 2 or 3 feet down.

    I found a pic for y'all to see, not that a pc is any more than an artist's conception. ufer.jpg


    Oops I mean this one.

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Last edited by John Kogel; 07-27-2014 at 04:07 PM.
    John Kogel, RHI, BC HI Lic #47455
    www.allsafehome.ca

  30. #30
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: Ufer rebar

    Quote Originally Posted by John Kogel View Post
    Just the one plate req'd for the service panel about 18" X 36" buried 2 or 3 feet down.

    I found a pic for y'all to see, not that a pc is any more than an artist's conception.
    John,

    Depends on what the CEC requirements are.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  31. #31
    Join Date
    Jul 2010
    Location
    Summerville, South Carolina
    Posts
    116

    Default Re: Ufer rebar

    Quote Originally Posted by Jim Port View Post
    The UFER needs to be in contact with the earth. How would being installed in the bond beam meet this?

    https://www.google.com/url?sa=i&rct=...06404711414460
    In my area they're putting plastic between the monolithic footing and the concrete foundation so in reality there is no direct contact with the earth....is this still acceptable?


  32. #32
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: Ufer rebar

    Quote Originally Posted by Ray Thornburg View Post
    In my area they're putting plastic between the monolithic footing and the concrete foundation so in reality there is no direct contact with the earth....is this still acceptable?
    That is an issue I raised years ago - the answer was that the edges of the slab are in direct contact with earth because the footing is required to be 12" minimum below grade.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  33. #33
    Join Date
    Aug 2011
    Location
    Hercules, CA
    Posts
    159

    Default Re: Ufer rebar

    Quote Originally Posted by Ray Thornburg View Post
    In my area they're putting plastic between the monolithic footing and the concrete foundation so in reality there is no direct contact with the earth....is this still acceptable?
    As we have very expansive soil in the Bay area, we see mostly pier and grade beam foundation systems where the grade beam spans between drilled, cast in place concrete piers. The grade beams are often required to have crushable material below them to allow expansion of the soils below and prevent uplift pressure on the bottom of the grade beam. In this case there may not be adequate contact between the soil and the grade beam to provide for adequate grounding, so we make sure that the ufer is well clamped to the pier reinforcement since the piers are well embedded into the ground. In any case, the adequacy of the ufer be checked by an ohms test.

    By the way Mark, you never want to weld rebar unless you are using A706 grade rebar with preheating and Special Inspection. The grade of steel used in rebar is subject to brittle fracture after welding, unless done properly.

    Thom Huggett, PE, SE, CBO

  34. #34
    Join Date
    Feb 2010
    Location
    Wenatchee Wa
    Posts
    301

    Default Re: Ufer rebar

    Here in Washington State we require UFER/CEE (New Construction) or you get to do a ground ring/plate which most would not want to do.

    The common practice here is to have the rebar extended above the foundation and then the GEC connected to that with a proper clamp. This connection has to be accessible.

    - - - Updated - - -

    Here in Washington State we require UFER/CEE (New Construction) or you get to do a ground ring/plate which most would not want to do.

    The common practice here is to have the rebar extended above the foundation and then the GEC connected to that with a proper clamp. This connection has to be accessible.

    Don Hester
    NCW Home Inspections, LLC
    Wa. St. Licensed H I #647, WSDA #80050, http://www.ncwhomeinspections.com

  35. #35
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: Ufer rebar

    Quote Originally Posted by Don Hester View Post
    Here in Washington State we require UFER/CEE (New Construction) or you get to do a ground ring/plate which most would not want to do.
    I can understand not wanting to do a ground ring once they realize what a ground ring actually is.

    But not wanting to do a plate? That's easy enough to install, but ... if the CEE is present, and typically there is a CEE present, then it is required to be also as all electrodes which are present are required to be used and bonded together.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  36. #36
    Join Date
    Aug 2008
    Location
    Maryland
    Posts
    1,970

    Default Re: Ufer rebar

    There is no requirement for the resistance of the cee to be proven like a driven electrode.install it and you are done. No need to test or prove less than 25 ohms.

    All answers based on unamended National Electrical codes.

  37. #37
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: Ufer rebar

    Quote Originally Posted by Jim Port View Post
    There is no requirement for the resistance of the cee to be proven like a driven electrode.install it and you are done. No need to test or prove less than 25 ohms.
    CEE is the easiest and cheapest way to go, why a contractor would resist if beyond me.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired