    I am having a bad day and can't remember is it acceptable to have a heat register vent directly into the garage?

    Inspection Referral

  2. #2
    Join Date
    Dec 2008
    Location
    Mesa, Arizona
    Posts
    45

    Default Re: register in garage

    No, not into garage if origin is home

    Jeff Moore AZ Cert#49250
    Level II Thermographer
    http:www.quantumhomeinspections.com

  3. #3
    Cory Bates's Avatar
    Cory Bates Guest

    Default Re: register in garage

    heat.jpg
    So this is not okay?


  4. #4
    Join Date
    Aug 2007
    Location
    Memphis TN.
    Posts
    4,311

    Default Re: register in garage

    Quote Originally Posted by Cory Bates View Post
    heat.jpg
    So this is not okay?
    Cory,
    If it's combustion air for the furnace OK.

    Not OK.
    *doesn't matter if it's a supply or return. Possible for car exhaust to enter the conditioned

    It Might have Choked Artie But it ain't gone'a choke Stymie! Our Gang " The Pooch " (1932)
    Billy J. Stephens HI Service Memphis TN.

  5. #5
    Join Date
    Mar 2007
    Location
    Knoxville, TN
    Posts
    2,560

    Default Re: register in garage

    That does not look like combustion air.
    It looks like a return, and no its not allowed.


  6. #6
    Join Date
    Mar 2007
    Location
    Columbus GA
    Posts
    3,747

    Default Re: register in garage

    Don't forget the sediment trap also.

    ' correct a wise man and you gain a friend... correct a fool and he'll bloody your nose'.

  7. #7
    Join Date
    Nov 2009
    Location
    St Paul, MN
    Posts
    1,630

    Default Re: register in garage

    Is it just me? Isn't that a downdraft furnace in the garage? Doesn't appear to be ductwork shared with the house. Looks like the furnace sits above the register. Cover for the furnace is in the lower right corner of the picture. Looks fine to me.

    MinnesotaHomeInspectors.com
    Minnesota Home Inspectors LLC
    ASHI #242887 mnradontesting.com

  8. #8
    Join Date
    Mar 2007
    Location
    Plano, Texas
    Posts
    4,245

    Default Re: register in garage

    It looks like a downdraft furnace with a register open to the garage but an establishing shot would be helpful.
    Any conditioned air duct is not allowed to be open to the garage.

    Jim Luttrall
    www.MrInspector.net
    Plano, Texas

  9. #9
    Join Date
    Aug 2007
    Location
    Memphis TN.
    Posts
    4,311

    Default Re: register in garage

    Quote Originally Posted by Ken Rowe View Post
    Is it just me? Isn't that a downdraft furnace in the garage? Doesn't appear to be ductwork shared with the house. Looks like the furnace sits above the register. Cover for the furnace is in the lower right corner of the picture. Looks fine to me.
    Or an updraft split system with a Goofy combustion air draw.

    It Might have Choked Artie But it ain't gone'a choke Stymie! Our Gang " The Pooch " (1932)
    Billy J. Stephens HI Service Memphis TN.

  10. #10
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: register in garage

    Is that duct board around the unit just there for looks (ugly looks, but still for looks) or is that the supply (or return) plenum?

    If that is supply or return plenum, then the entire thing leaking air to the garage or sucking air from the garage.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  11. #11
    Join Date
    Mar 2007
    Location
    Plano, Texas
    Posts
    4,245

    Default Re: register in garage

    GARAGE DUCT INSTAllATION

    R302.5.2 Duct penetration. Ducts in the garage and ducts penetrating the walls or ceilings separating the dwelling from the garage
    shall be constructed of a minimum No. 26 gage (0.48 mm) sheet steel or other approved material and shall have no openings into the garage.

    Jim Luttrall
    www.MrInspector.net
    Plano, Texas

  12. #12
    Join Date
    Oct 2011
    Location
    california
    Posts
    65

    Default Re: register in garage

    Quote Originally Posted by Cory Bates View Post
    I am having a bad day and can't remember is it acceptable to have a heat register vent directly into the garage?
    No only if it has all solid 26 gage sheet metal all the way back to the unit to maintain the fire envelope

    - - - Updated - - -

    Quote Originally Posted by Cory Bates View Post
    I am having a bad day and can't remember is it acceptable to have a heat register vent directly into the garage?
    No only if it has all solid 26 gage sheet metal all the way back to the unit to maintain the fire envelope

    - - - Updated - - -

    Quote Originally Posted by Cory Bates View Post
    I am having a bad day and can't remember is it acceptable to have a heat register vent directly into the garage?
    No only if it has all solid 26 gage sheet metal all the way back to the unit to maintain the fire envelope

    - - - Updated - - -

    Quote Originally Posted by Cory Bates View Post
    I am having a bad day and can't remember is it acceptable to have a heat register vent directly into the garage?
    No only if it has all solid 26 gage sheet metal all the way back to the unit to maintain the fire envelope

    - - - Updated - - -

    Quote Originally Posted by Cory Bates View Post
    I am having a bad day and can't remember is it acceptable to have a heat register vent directly into the garage?
    No only if it has all solid 26 gage sheet metal all the way back to the unit to maintain the fire envelope

    - - - Updated - - -

    Quote Originally Posted by Cory Bates View Post
    I am having a bad day and can't remember is it acceptable to have a heat register vent directly into the garage?
    No only if it has all solid 26 gage sheet metal all the way back to the unit to maintain the fire envelope

    - - - Updated - - -

    Quote Originally Posted by Cory Bates View Post
    I am having a bad day and can't remember is it acceptable to have a heat register vent directly into the garage?
    no only if 26 gage metal ducting to maintain fire envelope


  13. #13
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: register in garage

    Quote Originally Posted by frazier jeffery View Post
    No only if it has all solid 26 gage sheet metal all the way back to the unit to maintain the fire envelope
    Not even then.

    The question was not about "duct work" in the garage, the question was about a supply register open to the garage.

    NO supplies or intakes (returns) in a garage for a unit/system which is for the living space ... NONE.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com