Results 1 to 3 of 3
  1. #1
    Clay White's Avatar
    Clay White Guest

    Default NM Liquid tight conduit installation

    Last edited by Clay White; 01-02-2008 at 02:06 PM.
    Crawl Space Creeper

  2. #2
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,036

    Default Re: NM Liquid tight conduit installation

    Yes, that is one of those newer screw-in fittings and it is not screwed all the way in.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  3. #3
    Jon Randolph's Avatar
    Jon Randolph Guest

    Default Re: NM Liquid tight conduit installation

    Not if it has a field around it to repel water.


    Seriously, I would wrtie it up for repair. The purpose of the whip is protect the wires form the elements and damage. Although it is unlikely that a lot of rain will enter (unless wind blown), it is still an entry point. If the connection at the condensing unit is lower than this level, the water will be flow into the unit.

    Write it up.


Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •