    Default Condensing boilers - 4 feet horizontal from meter... source?

    Regarding high efficiency gas condensing boilers, I'm finding a consistent regulation in manufacturer instructions, "a clearance of at least 4 feet horizontally must be maintained between the vent terminal and gas meters, electric meters,...". It's so consistent, there must be a regulation somewhere, but I can't find it in the 2012 IRC or 2012 NFPA 54. Any ideas where I can find the source for this?... tia

    Member Benefits1

  2. #2
    Join Date
    Jul 2008
    Location
    Chicago
    Posts
    263

    Default Re: Condensing boilers - 4 feet horizontal from meter... source?

    NFPA 12.9.4 talks about protecting gas meters from gas vents. I don't know why the 4' distance is shown in most manufacturer's instructions.

    Mike Lamb
    Inspection Connection, Inc.