Thread: Support for A/C

  1. #1
    Jeff Eastman's Avatar
    Jeff Eastman Guest

    Default Support for A/C

    Last edited by Jeff Eastman; 12-11-2007 at 07:47 PM.
    Member Benefits1

  2. #2
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: Support for A/C

    Absolutely write it up.

    That pad should either be on terra firma or on a support bracketed of the structure, not on a teeter totter.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  3. #3
    Join Date
    Aug 2007
    Location
    Memphis TN.
    Posts
    4,311

    Default Re: Support for A/C

    Jeff,

    No weep holes visible in Photo.

    It Might have Choked Artie But it ain't gone'a choke Stymie! Our Gang " The Pooch " (1932)
    Billy J. Stephens HI Service Memphis TN.

  4. #4
    Richard Rushing's Avatar
    Richard Rushing Guest

    Default Re: Support for A/C

    Why is that suction line burried?? Problemo.

    rr


  5. #5
    Join Date
    Oct 2003
    Location
    Rockwall Texas
    Posts
    4,521

    Default Re: Support for A/C

    A few other observations,

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images

  6. #6
    Richard Stanley's Avatar
    Richard Stanley Guest

    Default Re: Support for A/C

    Electrical outlet / receptacle?
    Electrical disconnect?


  7. #7
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: Support for A/C

    Don't forget 'too close to the wall' and 'under the roof runoff' (unless there is a gable end above or a gutter).

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  8. #8
    Join Date
    Oct 2003
    Location
    Rockwall Texas
    Posts
    4,521

    Default Re: Support for A/C

    Jerry,

    I have had several HVAC contractors tell me that the run-off from the roof is not detrimental to a condensing unit.

    I've always commented if the diverter was not present on the edge of the roof, but have been shot down so many times on it I've just about quit commenting on it.

    rick


  9. #9
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: Support for A/C

    Quote Originally Posted by Rick Hurst View Post
    Jerry,

    I have had several HVAC contractors tell me that the run-off from the roof is not detrimental to a condensing unit.

    I've always commented if the diverter was not present on the edge of the roof, but have been shot down so many times on it I've just about quit commenting on it.

    rick
    Rick,

    Every single installation instruction I've read in the past 10 years as stated *NOT* to locate the condenser unit where roof run off will strike the condenser unit.

    I trust the manufacturer more than those HVAC techs, besides, does the code say to install them in accordance with what the techs say, or in accordance with the installation instructions?

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  10. #10
    Evan Grugett's Avatar
    Evan Grugett Guest

    Default Re: Support for A/C

    The condenser pad should not be on the wood planter border that will eventually rot and cause the unit to be out of level. Jerry is right, the condenser should also not be under the roof runoff. The manufacturers instructions are actually the "Code" (and always have been around here) but are often disregarded by installers. Write it up. Electrical disconnect switches must be in sight of the motor for the last 50 years, that should be written up as well.


  11. #11
    Scott Regan's Avatar
    Scott Regan Guest

    Question Re: Support for A/C

    Hi
    My name is Scott Regan; an I have been in the HVAC field for over 20 years.
    I have seen this on numerals actions and every time my heat skip a beat.
    First thing is the malfunctions installation says the unit must maintain a 3 inch clears on all sides. The unit must not tilt more the 15 degrees, in any direction. There is no code or any specs on how to ache this, just my must. To answer your questions, this unit is up to code, yet personally I would make a not note in the report that the concert pad resting on the pillar will cause the pillar to decayed or even brake down the wall if not corrected.
    I hope this help you.


  12. #12
    Join Date
    Oct 2003
    Location
    Rockwall Texas
    Posts
    4,521

    Default Re: Support for A/C

    Quote Originally Posted by Scott Regan View Post
    Hi
    My name is Scott Regan; an I have been in the HVAC field for over 20 years.
    I have seen this on numerals actions and every time my heat skip a beat.
    First thing is the malfunctions installation says the unit must maintain a 3 inch clears on all sides. The unit must not tilt more the 15 degrees, in any direction. There is no code or any specs on how to ache this, just my must. To answer your questions, this unit is up to code, yet personally I would make a not note in the report that the concert pad resting on the pillar will cause the pillar to decayed or even brake down the wall if not corrected.
    I hope this help you.
    What is a malfunctions installation?

    rick


  13. #13
    Join Date
    Aug 2007
    Location
    Memphis TN.
    Posts
    4,311

    Default Re: Support for A/C

    Quote Originally Posted by Rick Hurst View Post
    What is a malfunctions installation?

    rick

    Rick,


    This Sure Looks Like One.(Malfunctions as more than one malfunction)

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    It Might have Choked Artie But it ain't gone'a choke Stymie! Our Gang " The Pooch " (1932)
    Billy J. Stephens HI Service Memphis TN.

  14. #14
    Join Date
    Apr 2007
    Location
    gainesville fl
    Posts
    122

    Default Re: Support for A/C

    Scott, what part of the country are you from, and is your keyboard broke?


  15. #15
    Richard Rushing's Avatar
    Richard Rushing Guest

    Default Re: Support for A/C

    I know Scott meant manufacturer's instructions... not malfunctions instictions.

    By the way Scott... do you have something to support the "15 degrees in any direction" thingy...

    rr

    Last edited by Richard Rushing; 11-11-2007 at 10:29 AM. Reason: f'd-up

  16. #16
    Join Date
    Oct 2003
    Location
    Rockwall Texas
    Posts
    4,521

    Default Re: Support for A/C

    One HVAC contractor told me that the 15 degrees was not true, others have said it can cause damages to the compressor.

    I personally don't call it out.

    rick


  17. #17
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: Support for A/C

    I have seen one or two manufacturer's installation instructions which said 10 degrees, 15 degrees or something like that, however, other than those rare instances, they all say 'on a level mounting surface' or words to that effect.

    Scott Regan (before I continue ... welcome to the board, Scott) said "To answer your questions, this unit is up to code," - which is incorrect as that installation does not meet code in several ways.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com