    Default Re: NM cable and food disposer

    You can use NM cable, but you would need to protect it from physical damage with flexible metal conduit and an appropriate fitting for it at the dishwasher.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  3. #3
    Join Date
    Oct 2003
    Location
    Rockwall Texas
    Posts
    4,521

    Default Re: NM cable and food disposer

    Jerry,

    For the life of me I can't understand why you can hardwire a disposer like its the same type of an appliance as a water heater. Disposer are going to need to be repaired or replaced more often than a water heater, yet you can't just disconnect a power cord after removal of the unit and be done with it.

    Most HO's won't properly connect the wiring to the disposer when replacing one that is hardwired.

    I think all appliances should be attached to a cord so that it can be easily disconnected for removal if need be but thats my opinion.

    rick

    Last edited by Rick Hurst; 11-07-2007 at 10:56 AM. Reason: Must have been having a senior moment. LOL

  4. #4
    mike huntzinger's Avatar
    mike huntzinger Guest

    Default Re: NM cable and food disposer

    Don't forget that the dishwasher is not on a air-gap device


  5. #5
    Richard Moore's Avatar
    Richard Moore Guest

    Default Re: NM cable and food disposer

    Deleted

    Last edited by Richard Moore; 11-07-2007 at 11:00 AM.

  6. #6
    Join Date
    Oct 2003
    Location
    Rockwall Texas
    Posts
    4,521

    Default Re: NM cable and food disposer

    Sorry about that Richard. It was a senior moment typing away. I went back and edited my comment.

    rick


  7. #7
    Richard Moore's Avatar
    Richard Moore Guest

    Default Re: NM cable and food disposer

    In that case...I withdraw my "Huh?".

    So...I'm guessing this wouldn't be right either...

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images

  8. #8
    Join Date
    Oct 2003
    Location
    Rockwall Texas
    Posts
    4,521

    Default Re: NM cable and food disposer

    Now thats exactly what I'm taking about. Great Pic. Richard. Do you mind I use it in my "What Not to Do Picture Book" ?


  9. #9
    Richard Moore's Avatar
    Richard Moore Guest

    Default Re: NM cable and food disposer

    Be my guest Rick. Let me know if you want the higher-res original.

    BTW, on..."Most HO's won't properly connect the wiring to the disposer when replacing one that is hardwired.

    I think all appliances should be attached to a cord so that it can be easily disconnected for removal if need be but thats my opinion."

    It's a valid point, but one problem is that disposers don't come with the appliance cord attached. The HO has to buy that and then connect it. I've seen numerous occasions where they manage to screw that up, usually by not using the clamp. I could also argue that armored flex is less subject to damage from the stuff that gets constantly tossed under the kitchen sink and might be preferable because of that.

    But, properly installed armored flex, or a properly installed appliance cord and receptacle are both "OK". Unprotected NM, no matter how it is secured and routed...not OK.

    Gotta go...I'm just hoping the damn novacaine wears off by the time I get to the inspection. I hate to drool (more than normal) in front of the clients.


  10. #10
    Join Date
    Apr 2007
    Location
    state of jefferson
    Posts
    522

    Default Re: NM cable and food disposer

    i would require a device box in the wall and then flex if romex is used. i too often see flex that just runs into the wall and it gives me pleasure to yank on it and see what comes out of the wall. the flex needs to be terminated to the device box with an approved fitting


  11. #11
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: NM cable and food disposer

    Quote Originally Posted by dan orourke View Post
    Thanks Jerry. do you happen to know of the code that allow it?
    Dan,

    From the NEC.
    - 110.3 Examination, Identification, Installation, and Use of Equipment.
    - - (B) Installation and Use. Listed or labeled equipment shall be installed and used in accordance with any instructions included in the listing or labeling.

    I'm guessing that the installation instructions will show it being installed either way - cord and plug *OR* permanently wired.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  12. #12
    John Steinke's Avatar
    John Steinke Guest

    Default Re: NM cable and food disposer

    Hooking up the disposal directly to a tail of NM is fairly common, and the 'trade' has yet to reach a consensus on the issue.

    Indeed, the very presence of a disposal is a violation of local ordinances, in some places (like New York City).

    If a piece of NM is attached to the disposal, a 'fine point' is that it be attached with a proper fitting, listed for use with NM, that provides both strain relief and abrasion protection.

    Using a cord & plug is a matter of some debate. While I personally like it (as there is a local, definite means of disconnect, and the plumber need never open an electrical box) .... various statements by UL can be read to say 'if it was supposed to have a cord, it would have had one put on by the factory.' This view is a frequent cause for debate on the sundry electrical BB's.

    If you're going to transition from, say, NM to MC .... well, that brings up the whole issue of a box (for the splice), proper mounting of the MC to the box, etc. If there's MC coming out of the wall, I'd look to see how it was connected ... and WHAT it was connected to! Plastic boxes are generally not listed for connecting MC to them - and boring a hole in the side doesn't change that fact.


  13. #13
    Michael Greenwalt's Avatar
    Michael Greenwalt Guest

    Default Re: NM cable and food disposer

    How about..."dang, thats just wrong". Can I put that in my report?


  14. #14
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: NM cable and food disposer

    Quote Originally Posted by Michael Greenwalt View Post
    How about..."dang, thats just wrong". Can I put that in my report?
    Sure, as long as you add an apostrophe ... that's ...

    Or say "Dang Bubba, that's just plain ol' wrong."

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  15. #15
    Join Date
    Oct 2003
    Location
    Rockwall Texas
    Posts
    4,521

    Default Re: NM cable and food disposer

    Everybody makes fun of "Bubba" till they need their car fixed.

    rick


  16. #16
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: NM cable and food disposer

    Quote Originally Posted by Rick Hurst View Post
    Everybody makes fun of "Bubba" till they need their car fixed.
    Then Bubba just goes out into his yard and takes the part he needs to fix it off one of those in his front yard.

    How cool is that?

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  17. #17
    Dennis Corbett's Avatar
    Dennis Corbett Guest

    Default Re: NM cable and food disposer

    The installation instructions of the disposal specify the method to connect to power, which will match the listing of the appliance, and rarely permit this type of installation. They usually specifiy a cord connection only. If is states that a permanent wiring connection is allowed, then a disconnect is required to be installed within 50' and within sight of the appliance, and the wiring method must comply with the NEC. A proper connector, protection from damage and support of the cable would all need to be in place.


  18. #18
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: NM cable and food disposer

    Quote Originally Posted by Dennis Corbett View Post
    then a disconnect is required to be installed
    Or ... a breaker lock out.

    I never make that suggestion, hoping that the electrician does not think of it as I do not think much of breaker lock outs (mainly because they are never used - sure, they 'meet minimum' code, but if they are never used 'are they safe'?).

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  19. #19
    Join Date
    Mar 2007
    Location
    Chicago
    Posts
    164

    Default Re: NM cable and food disposer

    Quote Originally Posted by Jerry Peck View Post
    Or ... a breaker lock out.

    I never make that suggestion, hoping that the electrician does not think of it as I do not think much of breaker lock outs (mainly because they are never used - sure, they 'meet minimum' code, but if they are never used 'are they safe'?).
    Hello All,

    Warning - thread drift (sort of).

    About 12 years ago a friend of mine was killed because the wrong disconnect was locked out on a commercial job.

    Corey


  20. #20
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: NM cable and food disposer

    Corey,

    Your post re-enforces (at least to me) that breaker lock-outs are just not safe to rely on. Personally, I wish they had never been allowed.

    I cannot think of any reason to save $50 (now, $15 years ago) by using a breaker lock-out instead of a disconnect and risk even one life, in this case, that of your friend.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  21. #21
    David Banks's Avatar
    David Banks Guest

    Default Re: NM cable and food disposer

    Circuit Breaker Lockout Devices

    Check out Field Lockout incidents below heading.


  22. #22
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: NM cable and food disposer

    Quote Originally Posted by Jeff Eastman View Post
    I'm not sure there is a concensus...allowed or not allowed? Or is it "depends on manufacture installation instructions?"
    I would say 'allowed unless stated otherwise in the manufacturer's installation instructions' with the caveat that 'allowed' means 'done properly' by protecting the NM cable with an approved raceway which is properly attached and secured to the disposer with a proper fitting and which extends back into the wall and is secured at the wall so it does not pull out.

    That last part is the part (and is secured at the wall so it does not pull out.") which is never there even when the NM cable is protected by a raceway.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com