Results 1 to 12 of 12
  1. #1
    cory nystul's Avatar
    cory nystul Guest

    Default proximity of ges vent to roof vent.

    is there any kind of code on how close a roof vent can be to a gas vent?

    DSCN6500.jpg

    Inspection Referral

  2. #2
    Join Date
    Aug 2011
    Location
    Bennett (Denver metro), Colorado
    Posts
    1,461

    Default Re: proximity of ges vent to roof vent.

    The issue is more the height of the flue than the proximity to the roof vent which will be exhausting warm attic air. That flue should be at least 3' above the peak.

    BTW, pretty shoes.

    If you choose not to decide, you still have made a choice.

  3. #3
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,040

    Default Re: proximity of ges vent to roof vent.

    Quote Originally Posted by Lon Henderson View Post
    That flue should be at least 3' above the peak.
    It should? Where is that stated?

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  4. #4
    Join Date
    Aug 2011
    Location
    Bennett (Denver metro), Colorado
    Posts
    1,461

    Default Re: proximity of ges vent to roof vent.

    Quote Originally Posted by Jerry Peck View Post
    It should? Where is that stated?
    Yeah, I got that wrong. It is 3' above roof line or 2' for B vent and minimum of 2' within any part of the roof within 10'.

    If you choose not to decide, you still have made a choice.

  5. #5
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,040

    Default Re: proximity of ges vent to roof vent.

    Quote Originally Posted by Lon Henderson View Post
    Yeah, I got that wrong. It is 3' above roof line or 2' for B vent and minimum of 2' within any part of the roof within 10'.
    No see-gar for you on that answer either.

    Chimneys are 3 minimum above the roof and/or 2 feet higher than any part of any structure within 10 feet.

    Type B gas vents are 1 foot minimum (with the minimum going higher as the slope of the roof increases) and not within 8 feet of any vertical obstruction (wall, chimney, etc.), if there is a vertical obstruction within 8 feet then the gas vent is 2 feet minimum higher than any such obstruction within 10 feet (paraphrasing the requirements, not word for word).

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  6. #6
    Join Date
    Aug 2011
    Location
    Bennett (Denver metro), Colorado
    Posts
    1,461

    Default Re: proximity of ges vent to roof vent.

    Quote Originally Posted by Jerry Peck View Post
    No see-gar for you on that answer either.

    Chimneys are 3 minimum above the roof and/or 2 feet higher than any part of any structure within 10 feet.

    Type B gas vents are 1 foot minimum (with the minimum going higher as the slope of the roof increases) and not within 8 feet of any vertical obstruction (wall, chimney, etc.), if there is a vertical obstruction within 8 feet then the gas vent is 2 feet minimum higher than any such obstruction within 10 feet (paraphrasing the requirements, not word for word).
    Not according to my Code Check Manual

    If you choose not to decide, you still have made a choice.

  7. #7
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,040

    Default Re: proximity of ges vent to roof vent.

    Quote Originally Posted by Lon Henderson View Post
    Not according to my Code Check Manual
    Post what your Code Check manual says, I'll follow with posting the code - we can see if this is another error in the Code Check books or if it is an error in something else.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  8. #8
    Join Date
    Aug 2011
    Location
    Bennett (Denver metro), Colorado
    Posts
    1,461

    Default Re: proximity of ges vent to roof vent.

    I scanned in the page. Quality is so-so.phpqYEVgGPM.jpg

    If you choose not to decide, you still have made a choice.

  9. #9
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,040

    Default Re: proximity of ges vent to roof vent.

    Quote Originally Posted by Lon Henderson View Post
    I scanned in the page. Quality is so-so.phpqYEVgGPM.jpg
    From the 2012 IRC (unchanged for many years/decades):
    - G2427.6 (503.6) Gas vents. - - Gas vents shall comply with Sections G2427.6.1 through G2427.6.11. (See Section G2403, Definitions.)
    - - G2427.6.1 (503.6.1) Installation, general.
    - - - Gas vents shall be installed in accordance with the terms of their listings and the manufacturer’s instructions.
    - - G2427.6.2 (503.6.2) Type B-W vent capacity.
    - - - A Type B-W gas vent shall have a listed capacity not less than that of the listed vented wall furnace to which it is connected.
    - - G2427.6.3 (503.6.4) Gas vent termination.
    - - - A gas vent shall terminate in accordance with one of the following:
    - - - - 1. Gas vents that are 12 inches (305 mm) or less in size and located not less than 8 feet (2438 mm) from a vertical wall or similar obstruction shall terminate above the roof in accordance with Figure G2427.6.3.
    - - - - 2. Gas vents that are over 12 inches (305 mm) in size or are located less than 8 feet (2438 mm) from a vertical wall or similar obstruction shall terminate not less than 2 feet (610 mm) above the highest point where they pass through the roof and not less than 2 feet (610 mm) above any portion of a building within 10 feet (3048 mm) horizontally.
    - - - - 3. As provided for direct-vent systems in Section G2427.2.1.
    - - - - 4. As provided for appliances with integral vents in Section G2427.2.2.
    - - - - 5. As provided for mechanical draft systems in Section G2427.3.3.

    This is what you said "It is 3' above roof line or 2' for B vent and minimum of 2' within any part of the roof within 10'." and why I said "No see-gar for you on that answer either.":
    - It's not "above the roof line" (which indicates either above the ridge as you first stated or above the eave), it is above the roof (measured from the roof for a flat roof and from the high side for a sloped roof).

    And, yes, I was also not clear either when I said "if there is a vertical obstruction within 8 feet then the gas vent is 2 feet minimum higher than any such obstruction within 10 feet (paraphrasing the requirements, not word for word)." as that could have indicated '2 feet higher than any vertical obstruction within 10 feet' instead of '2 feet higher than any portion of the building within 10 feet'.

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  10. #10
    Join Date
    Aug 2011
    Location
    Bennett (Denver metro), Colorado
    Posts
    1,461

    Default Re: proximity of ges vent to roof vent.

    Instead of roof "line," I should have said roof "surface" as measured from the upper side of the flue base. But in any event, since the roof pitch is a factor in determining the flue height, I was still wrong.

    If you choose not to decide, you still have made a choice.

  11. #11
    Join Date
    Dec 2009
    Location
    Florida
    Posts
    553

    Default Re: proximity of ges vent to roof vent.

    Jerry, Just a suggestion. When quoting something could you quote in italics. It makes it easier to separate the wind (not that I am saying that you are windy) from the chaff.


  12. #12
    Join Date
    Jan 2011
    Location
    Marietta, Georgia
    Posts
    93

    Default Re: proximity of ges vent to roof vent.

    Ditto to what Jerry has posted. This is one of the most common issues I see with the exterior of a home; gas vents that are too low in relation to the roof pitch or if within 8 feet of a vertical wall or obstruction (now, define obstruction in this regard). Second only are improper flue caps (not listed) on newer installed gas appliances.


Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •