    Default AC Condensate Line Blowing Cold Air Into Sink?

    Last edited by JTravis; 03-03-2015 at 02:22 PM. Reason: Wrong Section
    Crawl Space Creeper

  2. #2
    Join Date
    Mar 2008
    Location
    Charlotte NC
    Posts
    2,304

    Default Re: AC Condensate Line Blowing Cold Air Into Sink?

    Everything is correct assuming the condensate is allowed to be sent to the city sewer (that is a ordnance issue only). What has happened is the trap in the attic near the air-handler/evaporator coil has dried out. This happens during long periods of none cooling. One solution is to remove the cap and pour a 1/2 cup of water into the trap through the cleanout; longer lasting results can be obtained by using mineral oil that does not evaporate as quickly.

    I just looked at you diagram and did not see a trap in the drawing. There needs to be a trap at the cleanout.

    Last edited by Vern Heiler; 03-03-2015 at 02:35 PM.
    The beatings will continue until morale has improved. mgt.

  3. #3
    Join Date
    Mar 2015
    Location
    Texas
    Posts
    3

    Default Re: AC Condensate Line Blowing Cold Air Into Sink?

    Hi Vern,

    Thank you very much for taking the time to reply! There is not a trap anywhere between the condenser and the sink. Does not having a trap at the clean out cause any damage or problems?


  4. #4
    Join Date
    Mar 2008
    Location
    Charlotte NC
    Posts
    2,304

    Default Re: AC Condensate Line Blowing Cold Air Into Sink?

    Quote Originally Posted by JTravis View Post
    Hi Vern,

    Thank you very much for taking the time to reply! There is not a trap anywhere between the condenser and the sink. Does not having a trap at the clean out cause any damage or problems?
    The lack of a trap is what is allowing cold air to blow out of your sink drain. I am guessing that you are in cooling mode, somthing I did not originally think of. The condensate trap is more important on a heat pump than it is with air conditioning system with a furnace. Don't know which system you have.

    The beatings will continue until morale has improved. mgt.