    Default Snowmelt boiler

    The snow melt boiler exhaust vent had a damper on it that was drafting into the space. This isn't correct? What would cause this?
    Thanks

    phps2ugz7AM.jpgphpjj9dM7AM.jpgphpsJd5JQAM.jpg

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Crawl Space Creeper

  2. #2
    Join Date
    Mar 2007
    Location
    Spring Hill (Nashville), TN
    Posts
    5,850

    Default Re: Snowmelt boiler

    Quote Originally Posted by Wayne Edwards View Post
    The snow melt boiler exhaust vent had a damper on it that was drafting into the space. This isn't correct? What would cause this?
    Thanks

    phps2ugz7AM.jpgphpjj9dM7AM.jpgphpsJd5JQAM.jpg
    Most likely the weight on the barometric damper needs to be adjusted.

    Scott Patterson, ACI
    Spring Hill, TN
    www.traceinspections.com

  3. #3
    Join Date
    Aug 2011
    Location
    Bennett (Denver metro), Colorado
    Posts
    1,461

    Default Re: Snowmelt boiler

    Quote Originally Posted by Wayne Edwards View Post
    The snow melt boiler exhaust vent had a damper on it that was drafting into the space. This isn't correct? What would cause this?
    Thanks
    I've never seen anyone do that. Did you find any CO leakage at the damper?

    If you choose not to decide, you still have made a choice.

  4. #4
    Join Date
    Jan 2014
    Location
    UT
    Posts
    12

    Default Re: Snowmelt boiler

    Thanks, and yes I could definitely feel leakage at the damper.


  5. #5
    Join Date
    Mar 2012
    Location
    Lansdale, PA
    Posts
    876

    Default Re: Snowmelt boiler

    The damper needs to be level-from the photo it does not appear to be.

    - - - Updated - - -

    The damper needs to be level-from the photo it does not appear to be.


  6. #6

    Default Re: Snowmelt boiler

    On a natural gas installation you would be red tagged here! Barometric damper only allowed on oil burners otherwise a draft inducer is needed for a cold start up along with a "spill" detector. But that is here in Ohio.


  7. #7
    Join Date
    Feb 2008
    Location
    Caledon, Ontario
    Posts
    4,982

    Default Re: Snowmelt boiler

    There is more going on there, then just the damper, look at all the rust on the top of the boiler and rust on the damper. Water entry down the flue spilling and rusting the top of boiler, needs further investigation.


  8. #8

    Default Re: Snowmelt boiler

    No investigation needed. Products of combustion are condensing on a "cold" chimney and running back downhill. No draft inducer on the exterior of the appliance. If it ever was "code compliant" and inspected it needs to be updated because what you have is clearly not working. Hopefully this in a detached building and the CO and products of combustion are not infiltrating a living space.

    - - - Updated - - -

    No investigation needed. Products of combustion are condensing on a "cold" chimney and running back downhill. No draft inducer on the exterior of the appliance. If it ever was "code compliant" and inspected it needs to be updated because what you have is clearly not working. Hopefully this in a detached building and the CO and products of combustion are not infiltrating a living space.

    - - - Updated - - -

    No investigation needed. Products of combustion are condensing on a "cold" chimney and running back downhill. No draft inducer on the exterior of the appliance. If it ever was "code compliant" and inspected it needs to be updated because what you have is clearly not working. Hopefully this in a detached building and the CO and products of combustion are not infiltrating a living space.


  9. #9
    Join Date
    Jan 2014
    Location
    UT
    Posts
    12

    Default Re: Snowmelt boiler

    Thanks for all your observations, very helpful. The boiler was in a garage so not exactly a separate building, but all of your observations were originally noted. I was just interested in other opinions. Thanks again..

    - - - Updated - - -

    Thanks for all your observations, very helpful. The boiler was in a garage so not exactly a separate building, but all of your observations were originally noted. I was just interested in other opinions. Thanks again..


  10. #10
    Join Date
    Feb 2008
    Location
    Caledon, Ontario
    Posts
    4,982

    Default Re: Snowmelt boiler

    I feel further investigation is warranted due to corrosion occurring in areas of the flue that cannot be readily inspected. I would not want to pass it off since corrosion could be extensive, causing rust throughs or obstructions from damage of interior flue, and in and behind boiler housing and damage to heat exchanger in my opinion.


  11. #11

    Default Re: Snowmelt boiler

    "The boiler was in a garage"
    i was afraid of that! The boiler manages to get running and establish a draft then someone decides they have to exit/enter the garage through the overhead door and super cools the combustion products with sub-zero temperatures. The boiler keeps running anyway regardless of the atmospheric draft presence and just add that someone forgets to shut the car off and lets it run to "warm up" in the morning. Let's even think where the make up air is going to come from. Of course all the vent pipes are rusted from all the condensation!

    You did offer a free sign because it reminded you of a far off quite town, yes?
    Choices Nurenberg or Auschwetz


  12. #12
    Join Date
    Mar 2007
    Location
    Succasunna NJ
    Posts
    577

    Default Re: Snowmelt boiler

    If it's in a garage in cold weather climate, the vent connector needs to be double walled (B-vent)

    Darren www.aboutthehouseinspections.com
    'Whizzing & pasting & pooting through the day (Ronnie helping Kenny helping burn his poots away!) (FZ)

  13. #13
    tom daley's Avatar
    tom daley Guest

    Default Re: Snowmelt boiler

    Ronald Betschman,

    I dont understand your comment about "Nurenberg" or "Auschwetz" ? I presume that its an innocent remark, & its just me being a little over sensitive but perhaps you would explain what you mean?