Results 1 to 31 of 31
    Apr 2008
    McKinney Texas
    Default Is there any condition where an outside area receptacle is not required to have GFI?
    Are there any conditions (under current codes/guidelines) where an outside/exterior area receptacle is not required to have GFI protection ? Yesterday I saw a home where there was an exterior receptacle 7 feet up on the patio wall. The receptacle was being used by a patio wall-mounted TV. The homeowner told me his electrician told him since the receptacle was above 6 feet high, it did not require GFI protection. This was a patio with a covered overhang roof but was otherwise an open-air patio.
    I have not been able to find any documentation to support that an exterior outlet can be without GFI protection.
    Default Re: Is there any condition where an outside area receptacle is not required to have G
    Nope, all exterior outlets need GFCI protection. Even the ones designed for Christmas lights high on the wall or at the soffits….
    Yes, there is a condition. If the outlet was installed before the code required it to be protected, it is still acceptable even though the outlet is not protected.
    {Note that (3) and (4) are for as follows: (3) Rooftops and (4) Outdoors }
    "Exception No. 1 to (3) and (4): Receptacles that are not readily accessible and are supplied from a dedicated branch circuit for electric snow-melting or deicing equipment shall be permitted to be installed without GFCI protection."
    I suspect that you do not have much of a call for circuits which are dedicated for "electric snow-melting or deicing equipment", and, even if you did and the circuit was then used for something else (such as the TV), then that exception would no longer be applied as the circuit was no longer dedicated for "electric snow-melting or deicing equipment".
    Apr 2008
    McKinney Texas
    Thanks guys. As we know the interpretation of "readily accessible" is subject to debate. In my opinion, this TV outlet is "readily accessible" even though is 7 feet from the floor. I am 6 feet tall, I can reach the outlet with no problem. A smaller person could easily reach it with a step stool. So that being said, (and based on you guy's comments), I view this outlet as it should have GFCI protection.
    Why are you applying that exception's "readily accessible" to "this TV outlet"?
    Once that receptacle is used for "this TV outlet" - the exception for dedicated snow melting-deicing equipment no longer applies.
    ... I view this outlet as it should have GFCI protection.
    As you should.
    Apr 2008
    McKinney Texas
    Thanks Jerry
    Mar 2013
    Md and or PA
    240 volt receptacles for one. Then there's the deicing receptacles Jerry mentioned.
    The code reads all 15 and 20 ampere 125 volt receptacles..............
    ( yes I have seen 240 volt receptacles outside)
    For Canadian inspectors, a different rule. 9 feet above the ground, no GFCI required.
    Lansdale, PA
    I believe the code did not require GFCI protection for receptacles at second floor decks at some time in the past. Maybe back at that time that also applied to receptacles above 6 feet, but I cannot say for sure.
    Oct 2014
    The new wording requiring GFCI protection in the 1971 NEC, Section 210-21(d) was simple: "For residential occupancies all 120-volt, single phase 15- and 20-ampere receptacle outlets installed outdoors. . ." It gave an effective date of 1/1/73. (This was presuming the 1971 NEC was adopted locally by then without this being amended out.)
    The new wording requiring GFCI protection in the 1971 NEC, Section 210-21(d) was simple: "For residential occupancies all 120-volt, single phase 15- and 20-ampere receptacle outlets installed outdoors. . ." It gave an effective date for this radical new requirement of 1/1/73. (This was presuming the 1971 NEC was adopted locally by then without this being amended out.)
    Refer to notes in this: http://jerrypeck.com/IFCN/Other%20It..._page-2014.pdf
    Useful thread for me.
    Apr 2008
    McKinney Texas
    Hi Jerry, thanks for posting the GFCI location sheet.
    Questions...
    1. Look at the Laundry/Utility column, where it says "Xc". I cannot find a "c" footnote.
    2. I read the sheet but it is not clear to me if currently a dedicated kitchen refrigerator receptacle should be GFCI protected??
    Gene
    Questions...
    Gene
    Questions...
    Gene
    Gene, a receptacle for the refrigerator does not require GFI protection unless it serves the countertop or called for in the manufacturers instructions.
    Apr 2008
    McKinney Texas
    Gene, a receptacle for the refrigerator does not require GFI protection unless it serves the counter-top or called for in the manufacturers instructions.
    Would you consider a GFCI protected kitchen refrigerator receptacle that does not serve a counter top a "violation" ? or "not a problem" ?
    In other words in a regular house with the receptacle hidden behind the fridge, if that receptacle were GFCI protected, would you consider that a problem? I would think it would be something most home owners would at least want to be aware of.
    Just wondered your thoughts..
    Gene,
    Thanks for the heads up on that error - I'll check on it and correct it.
    A receptacle hidden behind the refrigerator would not be serving the countertop and would not require GFCI protection.
    GFCI protection is not prohibited either.
    Gene,
    I updated the list ... I corrected that note and renumbered the notes so that one number applied to one column in the table, which also reduced the number of notes.
    Should be much easier to read and apply the notes now - let me know what you think of the update.
    A refrigerator on a gfi protected circuit should not be an issue.
    The gfi itself should not be behind the refrigerator.
    For convenience, but nothing prohibits it ... unless you are aware of something that I am not.
    Mar 2009
    Colorado Front Range
    Not absolutely prohibited, but a good many folks don't consider the space behind a refrigerator as readily accessible. Some people who live in their own home are incapable of moving the fridge.
    Also, many fridges are within 6 feet of the sink and would require GFCI protection if 2014 NEC applies either to the construction or a receptacle replacement. A dead front GFCI adjacent to the fridge is probably a much better option.
    Chico,Ca
    I believe that more recent editions of the NEC require GFCI receptacles to be accessible, but do not have them handy to prove / disprove that. Common sense but common sense is not so common.
    Readily accessible ... I just had not heard that rolling out a refrigerator makes it not readily accessible.
    I can see that for some of the larger refrigerators, but had not thought of it that way about a standard every day refrigerator.
    Jerry, you might remember the person that said a gfi or afci could not be behind a couch as it was not readily accessible.
    Jim,
    From your statement I presume that person may have been me, but, no ... ... I don't remember that. When or where?
    No, I don't believe it was you Jerry. Someone that's hasn't been here in awhile IIRC.
    Ahhh ... possibly with the initials of H. G. Waston? (Oh, wait, those are more than "initials" ... )
    Chico,Ca
    It would be poorly thought out to place a GFCI receptacle behind a fridge and beyond the ability of some to access. But that could be said about my garage with one of the GFCI's being hidden by "stuff".
    Aug 2011
    I was in a home yesterday with nearly 20 GFCIs scattered through the basement. Many were redundant and many behind something. Accessibility is somewhat subjective. A GFCI might be readily accessible behind a dresser for a strapping young lumberjack and completely inaccessible for a 90 year old little lady.
    I just updated my GFCI and AFCI pages - I added the note at the bottom to make sure it is not missed.
    After clicking the link, you may need to refresh the page in case your browser is reading a cached copy of it.
