Results 1 to 5 of 5
    Anacortes, Washington
    Default Single plumbing stack
    I inspected a 1970's raised rancher with 3 bathrooms and kitchen. The home only had a single 4" (maybe 6) vent over one corner of the home. The kitchen sink was 20' from the vent and the master bath was about 30' from the stack. I was not able to view the attic connections due to an access issue.
    do plumbing codes allow for a single vent???
    Thanks
    //Rick
    OREP Insurance
    Rick Bunzel
    WWW.PacCrestInspections.com
    360-588-6956
    Default Re: Single plumbing stack
    Yes, if the fixture unit count is within the number of fixture*units for the 4" vent.
    In 1990's houses and newer, I would anticipate finding AAVS at the other fixtures.
    Quote Originally Posted by Jerry Peck View Post
    Or, there are branch vents that connect to the main you cannot see.
    PROFESSIONAL CONSULTING AND INSPECTION COMPANY INCLUDING FORENSIC INVESTIGATIONS
    http://jeffghooper.com/
    Quote Originally Posted by JeffGHooper View Post
    The fixture unit rating of the one vent would still be required to meet the fixture unit load.
    And unless all the fixtures were basically back to back to back, revents would be required anyway.