Results 1 to 4 of 4
  1. #1
    Join Date
    Mar 2012
    Location
    Lansdale, PA
    Posts
    876

    Default How does this panel meet code?

    This panel is a Thomas and Betts 200 ampere panel installed 15 years ago. 40 slots. There are two terminal strips for neutrals and grounds each with 20 terminals. As I rear the labeling, I assume only one neutral wire is permitted per screw and two ground wires. Unless you install a bunch of two-wire 240-volt circuits how do you connect all of the wires? Am I missing something?

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    OREP Insurance

  2. #2
    Join Date
    Mar 2013
    Location
    Md and or PA
    Posts
    137

    Default Re: How does this panel meet code?

    if it comes down to needing more terminals one can install an additional ground bar for the grounds. thus freeing up terminals on the neutral bars for the neutrals.


  3. #3
    Join Date
    Mar 2007
    Location
    Plano, Texas
    Posts
    4,245

    Default Re: How does this panel meet code?

    Quote Originally Posted by Mark Reinmiller View Post
    This panel is a Thomas and Betts 200 ampere panel installed 15 years ago. 40 slots. There are two terminal strips for neutrals and grounds each with 20 terminals. As I rear the labeling, I assume only one neutral wire is permitted per screw and two ground wires. Unless you install a bunch of two-wire 240-volt circuits how do you connect all of the wires? Am I missing something?
    You don't need branch circuit ground terminals if you use conduit for the grounds, nor do you need neutrals on 240 volt circuits. It is up to the installer to add what he needs beyond the basic provisions. Chintzy but acceptable.

    Jim Luttrall
    www.MrInspector.net
    Plano, Texas

  4. #4
    Mbrooke's Avatar
    Mbrooke Guest

    Default Re: How does this panel meet code?

    The theory is that the person choosing this panel may be using MWBC, a of 240 circuits, conduit or a ground bar as mentioned above.

    I know, it encourages double and triple taps in homes, but it is what it is