    Default Venting Issues

    50,000 BTU GFAF and 40,000 BTU gas WH venting into 8" single wall pipe system passing through attic and meal chimney chase? What concerns (other than the birds nest, the rain cap and the single wall pipe passing through the attic) do others here see with this?

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Member Benefits1

  2. #2
    Join Date
    Mar 2007
    Location
    Philadelphia PA
    Posts
    3,177

    Default Re: Venting Issues

    Maybe it's the photo angle, but in the first one it looks like the wh flue pipe runs downhill.

    "There is no exception to the rule that every rule has an exception." -James Thurber, writer and cartoonist (1894-1961)
    www.ArnoldHomeInspections.com

  3. #3
    Join Date
    Mar 2007
    Location
    Colorado Springs, CO
    Posts
    1,217

    Default Re: Venting Issues

    I agree. Hard to tell from the photo angle but the WH flu does not appear to have proper slope.

    "Baseball is like church. Many attend but few understand." Leo Durocher
    Bruce Breedlove
    www.avaloninspection.com

  4. #4
    Join Date
    Aug 2007
    Location
    Memphis TN.
    Posts
    4,311

    Default Re: Venting Issues

    Quote Originally Posted by John Arnold View Post
    Maybe it's the photo angle, but in the first one it looks like the wh flue pipe runs downhill.
    Or Flat, Rust on Flue Pipe, Evidence of moisture (several places) in the attic.

    It Might have Choked Artie But it ain't gone'a choke Stymie! Our Gang " The Pooch " (1932)
    Billy J. Stephens HI Service Memphis TN.

  5. #5
    Join Date
    Mar 2007
    Location
    Near Philly, Pa.
    Posts
    1,682

    Cool Re: Venting Issues

    No listed vent system to pass through unconditioned space
    improper support
    common vent oversized
    vent not protected from damage in accessible portion of attic
    severely restricted vent termination with unlisted hardware cloth doubled
    oversized vent connector on WH (I'm guessing this WH has a 3" draft hood)
    I doubt there is an attic insulation shield and we know there is no listed firestop because there is no listed venting.

    The entire installation should be replaced with a properly sized and installed listed B-vent.
    HTH
    Bob

    Keep the fire in the fireplace.

  6. #6
    Join Date
    Mar 2007
    Location
    Chicago, IL
    Posts
    2,797

    Default Re: Venting Issues

    Thanks,

    Looks like I got it all - reading and study here and elsewhere must be doing some good!

    There was an "insulation shield', and it was even pretty clean on the attic side (no pic), but here's the bottom.

    As for the WH, it's going as Spackle does not not appear to be a permanent repair for leaking water heaters.

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images

  7. #7
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: Venting Issues

    Is there a 30" wide path to and in front of that panel shown between the two units, with at 30" x 36" working space in front of that panel? (Okay, the walkway may be 24" wide, but the working space is 30" x 36".)

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com