    It appears, from the diameter of the boiler vent pipe, that it is double wall, and passed through another single wall pipe to transition through the floor. Hot water heater is hacked in as pictured. Not sure what to think of the whole thing. It is obviously not to modern code, and will be flagged. Boiler is NG as is the hot water heater.

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    OREP Insurance

  2. #2
    Join Date
    Mar 2007
    Location
    Near Philly, Pa.
    Posts
    1,682

    Thumbs down Re: Venting

    Appears to be an oversized factory chimney without its requisite listed firestop at the floor, no support, no listed transitions to single walled pipe tat is not properly supported. That boiler is probably the one that vents under positive pressure which would mean it has to have its own listed separate venting designed for positive flue pressure. Hack, hack, hack.

    Keep the fire in the fireplace.

  3. #3
    Join Date
    Mar 2011
    Location
    Corinth, NY
    Posts
    90

    Default Re: Venting

    Thanks for the quick reply Bob.

    Russ M


  4. #4
    Join Date
    Jul 2014
    Location
    Fl
    Posts
    17

    Default Re: Venting

    As stated - multiple errors. NFPA54 lays out the proper multi appliance venting, likely the largest issue is comingled brands / types of venting with improvised (tin snips) connections. They need a lic. HVAC contractor to bring it to code... and while they're at it validate combustion air path.