    I inspected a detached garage with some finished rooms in the back and above. There was a subpanel in the lower finished area. The lights at the ceiling were fluorescent work lights. The only way to turn them on and off was at the breaker in the subpanel. I have never, ever known a breaker to be the on/off switch for a fixture. So I noted it in my report. An Electrician called me about it (he was fine, didn't have an attitude as some do when talking to Inspectors). He said that since there was another single light with a standard wall switch for this room, it was alright to have the ceiling lights shut off at the breaker.
    I thanked him for calling and couldn't wait to get here. I still can't get my head around the fact that it is alright to use a breaker as a standard on/off switch for a fixture. I know that besides the overload protection, a breaker and a light switch are not so different. Anyone else have a thought about that.

    Similar Threads:
    Member Benefits1

  2. #2
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,038

    Default Re: Breaker as On/Off switch

    This is the best answer I have available:

    (From Mike Holt's information)

    Electrical Circuit Breakers

    Circuit Breakers As Switches
    Both the ANSI and the NEC definitions acknowledge the potential for the legitimate use of circuit breakers as switches. Switches (pass, but do not consume electrical power) are considered as being control devices, thus one may also say that a breaker is a control device, or a controller.

    To aid in the understanding of a fine point, I offer this comparative example. A gas valve and a steam pressure relief valve are both controllers, one the fuel to the burners that aids in the development steam pressure, and the pressure relief valve that opens on excessive pressure. Both are controllers, one operating (the gas valve) the other safety (the relief valve).

    Likewise in a parallel manner; we say that a circuit breaker can control and protect an electrical circuit. An electrical relay is an example of an operating control; it opens and closes the circuit. Circuit breakers are not designed as replacements for relays, operating controls.

    There is as you may intuitively have anticipated an exception. Some circuit breakers are manufactured for use in a specific type of application. When a circuit breaker is designed to also be routinely used as an on-off switch to control 277 volt florescent luminaires they are marked SWD, for switch duty. This does not mean that a switch duty breaker can be used to manually control a traffic signal light where it will be cycled 1,000 or more times per day. The point is; the listing for switch duty (SWD) does not mean a circuit breaker can be used as a high frequency cycling operating control, such as a relay that has a life span rated in tens, if not hundreds of thousands of duty cycles.

    While circuit breakers can be legitimately and safely used as switches, the frequency and duration of such use is very limited. Routinely circuit breakers are manually operated for service-maintenance, and repair type activities. With the preceding enhancing our understanding; we can say that circuit breakers can legitimately be used as switches, generally they are not intended for prolonged frequent or repetitive manual breaking and making type control of electrical energy utilization equipment.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  3. #3
    Join Date
    Mar 2007
    Location
    Plano, Texas
    Posts
    4,245

    Default Re: Breaker as On/Off switch

    ...circuit breakers can legitimately be used as switches, generally they are not intended for prolonged frequent or repetitive manual breaking and making type control of electrical energy utilization equipment.
    Precisely my thoughts, Mr. Holt just said it better. (and first)


    Jim Luttrall
    www.MrInspector.net
    Plano, Texas

  4. #4
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,038

    Default Re: Breaker as On/Off switch

    Quote Originally Posted by Jim Luttrall View Post
    Precisely my thoughts, Mr. Holt just said it better. (and first)
    And his words carry a lot more authority than mine or yours do too.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  5. #5
    Join Date
    Mar 2007
    Location
    Chicago, IL
    Posts
    2,797

    Default Re: Breaker as On/Off switch

    Thanks for that link.


  6. #6
    James Duffin's Avatar
    James Duffin Guest

    Default Re: Breaker as On/Off switch

    I agree with the electrician. The breaker is rated as switch duty so as long as you can safely cut on a light as you enter the space the other lights can be controlled by breaker, motion, or anything thing else.

    In my other life, we had 277 volt gym lights that the only switch was the breaker. Not the best situation but legal.


  7. #7
    Peter Drougas's Avatar
    Peter Drougas Guest

    Default Re: Breaker as On/Off switch

    Thannk you everyone. I have a much better understanding. I guess we can end this thread.


  8. #8
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,038

    Default Re: Breaker as On/Off switch

    Quote Originally Posted by James Duffin View Post
    I agree with the electrician. The breaker is rated as switch duty so as long as you can safely cut on a light as you enter the space the other lights can be controlled by breaker, motion, or anything thing else.

    In my other life, we had 277 volt gym lights that the only switch was the breaker. Not the best situation but legal.
    In your other life, that was similar to one of the uses described in Mike Holt's information, as to the question which was posed, it is not.

    Even in your other life, SWD duty breakers were not really made for use as "switches" like you used them for, but especially in the use in the posted question.

    No, SWD (switch duty rated) breakers *are not* "intended" to be used as "switches" - read the information I posted from Mike.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  9. #9
    James Duffin's Avatar
    James Duffin Guest

    Default Re: Breaker as On/Off switch

    I do not need to read from Mike to quote what I experienced personally. We had over 40 gyms that the lights were controlled only by breakers.

    I've used Mike for my CE in the past so he is an old friend.


  10. #10
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,038

    Default Re: Breaker as On/Off switch

    Quote Originally Posted by James Duffin View Post
    I do not need to read from Mike to quote what I experienced personally. We had over 40 gyms that the lights were controlled only by breakers.
    James,

    Likewise, I used to have a 1967 E-Type Jaguar (XKE) and I would drive it really fast for long periods of time (say 130-140 for an hour at a time), it was 'made for that use', but, do you really think that car was designed to be driven that way *ALL THE TIME*?

    Nope.

    SWD breakers *ARE NOT* intended to be used for that use all the time either.

    Going on personal experiences, heck, those old metal case drills were made to be used drilling into fountains with the metal body of the drill down in the water up to the air vents, right? I mean, "what I experienced personally" they were - done it.

    Oh, but that's different you say? Actually, no it is not. neither example is different than using SWD breakers for everyday switching duties - NONE of the items was designed or intended to be used that way.

    SWD breakers 'could be' used for switches, but 'were not intended to be' used for switches on an everyday use.

    My old E-Type 'could be' driven that way, but it 'was not intended to be' driven that way 24/7.

    My old metal case drill ... well, it was 'a drill', was it not? And that is what I used it for. (Before GFCI protection came about.)

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  11. #11
    John Steinke's Avatar
    John Steinke Guest

    Default Re: Breaker as On/Off switch

    Breakers can have an additional rating for switching duty, even for HID lighting. Indeed, it has probably bee decades since a breaker was made that did not also have a 'swd' or 'hid' rating. Using them as one would an ordinary switch is not a problem.


  12. #12
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,038

    Default Re: Breaker as On/Off switch

    Quote Originally Posted by John Steinke View Post
    Breakers can have an additional rating for switching duty, even for HID lighting. Indeed, it has probably bee decades since a breaker was made that did not also have a 'swd' or 'hid' rating. Using them as one would an ordinary switch is not a problem.
    John,

    Did you read the other posts above?

    Breakers rated for SWD are not really rated for, or intended for, everyday switching uses. Read the information from Mike Holt, he explains it well.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  13. #13
    John Steinke's Avatar
    John Steinke Guest

    Default Re: Breaker as On/Off switch

    Jerry, I go by what UL says on this subject. From their "white book:" "A circuit breaker ... may be marked 'SWD' and is suitable for switching fluorescent lighting loads on a regular basis."

    Further, regarding the marking "HID:" "intended to switch HID lighting loads on a regular basis."

    The only way I can construe those statements is to say "It's perfectly OK to use the breaker instaed of a switch."


  14. #14
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,038

    Default Re: Breaker as On/Off switch

    Quote Originally Posted by John Steinke View Post
    The only way I can construe those statements is to say "It's perfectly OK to use the breaker instaed of a switch."
    John,

    Did you even read the first post which started this thread to see what was being discussed?

    Quote Originally Posted by Peter Drougas View Post
    I inspected a detached garage with some finished rooms in the back and above. There was a subpanel in the lower finished area. The lights at the ceiling were fluorescent work lights.


    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •