    Default Ventilation Fan In Wet Area

    Even though I cannot locate any code reference prohibiting installation of a ventilator in a "wet" area, I am reporting it as a safety hazard. I spent about an hour of my life reading a thread on another forum about proximity of the fan switch to the enclosure. I believe that per the code, the switch location is allowed. Open to comments. Thanks.

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    OREP Insurance

  2. #2
    Join Date
    Feb 2009
    Location
    Southern Vancouver Island
    Posts
    4,607

    Default Re: Ventilation Fan In Wet Area

    Call the fan location out for too wet and possible shock hazard such as if the grill is removed.
    Also cheap fans mounted on their sides like that often develop bearing problems. It is a cheezy installation and your clients will agree.

    The switch location must be outside the footprint of the enclosure so I think it is probably acceptable by your code standards. There may be a requirement for GFCI on that circuit.

    In Canada switch needs to be 3 feet away from the shower.

    John Kogel, RHI, BC HI Lic #47455
    www.allsafehome.ca

  3. #3
    Join Date
    Feb 2008
    Location
    Chicago IL
    Posts
    2,048

    Default Re: Ventilation Fan In Wet Area

    Something you should consider doing in this type of situation is pull the cover off the unit so that you can get a picture of the manufacturers label and model number. Then you can look up the unit and see if it is approved for wet locations by the manufacturer. If it isn't well then its a slam dunk. If it isn't GFCI protected write it up as D&H.
    Sometimes its better to spend an extra minute verifying than spending more time later guessing. Not trying to sound snarky, just my glowing personality.

    www.aic-chicago.com
    773/844-4AIC
    "The Code is not a ceiling to reach but a floor to work up from"

  4. #4
    Join Date
    Oct 2010
    Location
    MONTREAL QUEBEC-CANADA
    Posts
    2,075

    Default Re: Ventilation Fan In Wet Area

    Quote Originally Posted by Markus Keller View Post
    write it up as D&H.
    ???? D&H. Not with you.

    Robert Young's Montreal Home Inspection Services Inc.
    Call (514) 489-1887 or (514) 441-3732
    Our Motto; Putting information where you need it most, "In your hands.”

  5. #5
    Join Date
    Feb 2008
    Location
    Chicago IL
    Posts
    2,048

    Default Re: Ventilation Fan In Wet Area

    Dangerous & Hazardous

    www.aic-chicago.com
    773/844-4AIC
    "The Code is not a ceiling to reach but a floor to work up from"

  6. #6
    Join Date
    Feb 2009
    Location
    Southern Vancouver Island
    Posts
    4,607

    Default Re: Ventilation Fan In Wet Area

    Quote Originally Posted by Markus Keller View Post
    Dangerous & Hazardous
    D+H = Oxymoron. Better just say it's FUBAR.

    No, it's FU without the BAR.

    John Kogel, RHI, BC HI Lic #47455
    www.allsafehome.ca

  7. #7
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: Ventilation Fan In Wet Area

    Quote Originally Posted by John Kogel View Post
    D+H = Oxymoron. Better just say it's FUBAR.

    No, it's FU without the BAR.
    Well, it is not Beyond All Repair ...

    But it might better be described as PSK 'Potential Spouse Killer' or ASD 'Assisted Suicide Device' ...