    Default Check Valve? on drain / vent pipe

    I found this behind a wall access panel directly behind the washing machine, just a few inches above the basement floor. I am sure this is where the washing machine stand pipe is connected, and the vent extends straight up vertically. Is that a check valve? If so, is that a problem? I have never seen a check valve installed on the drain / vent plumbing...



    Similar Threads:
    Inspection Referral

  2. #2
    Join Date
    Feb 2008
    Location
    Caledon, Ontario
    Posts
    4,982

    Default Re: Check Valve? on drain / vent pipe

    Is there a sewage ejector pump located in the basement? Typically a one way valve is located on the discharge side.


  3. #3
    Join Date
    Feb 2008
    Location
    Iowa City, IA
    Posts
    108

    Default Re: Check Valve? on drain / vent pipe

    Quote Originally Posted by Raymond Wand View Post
    Is there a sewage ejector pump located in the basement? Typically a one way valve is located on the discharge side.
    No pumps what so ever. This is a two story townhouse condominium with a basement connected to the city's gravity fed sanitary sewer system.


  4. #4
    Join Date
    Oct 2010
    Location
    MONTREAL QUEBEC-CANADA
    Posts
    2,075

    Default Re: Check Valve? on drain / vent pipe

    What floor is that setup on?

    Robert Young's Montreal Home Inspection Services Inc.
    Call (514) 489-1887 or (514) 441-3732
    Our Motto; Putting information where you need it most, "In your hands.”

  5. #5
    Join Date
    Feb 2008
    Location
    Iowa City, IA
    Posts
    108

    Default Re: Check Valve? on drain / vent pipe

    Quote Originally Posted by ROBERT YOUNG View Post
    What floor is that setup on?
    As I mentioned, what you see in the photo is just a few inches above the basement (concrete) floor.


  6. #6
    Join Date
    Feb 2008
    Location
    Caledon, Ontario
    Posts
    4,982

    Default Re: Check Valve? on drain / vent pipe

    Andrew,

    It is an unusual configuration. Can't tell is valve is installed correctly by photo. And a elbow tied in before the valve?

    Further questions -
    Past problem with flooding?
    Is there a back flow valve installed on the waste line?
    Any other valves on basement fixtures?
    Radon mitigation?

    Definitely needs clarification as to purpose and legality. Purchaser should be advised as to the concern and should inquire of vendor, and/or seek further clarification by a licenced plumber before close of title.


  7. #7
    Join Date
    Feb 2008
    Location
    Iowa City, IA
    Posts
    108

    Default Re: Check Valve? on drain / vent pipe

    Quote Originally Posted by Raymond Wand View Post
    Further questions -
    Past problem with flooding?
    Is there a back flow valve installed on the waste line?
    Any other valves on basement fixtures?
    Radon mitigation?
    No past flooding problems that I am aware of. It is common in this city for a backflow / backwater valve to be installed on the main waste line running out of the house to the sanitary sewer (but that is a large valve on the main horizontal waste line located below the concrete floor. No other plumbing fixtures in the basement except the floor drain. I've done thousands of inspections in this area over the last 10 years and I don't think I've ever seen a check valve, if that is what it is, installed on the drain / vent plumbing. The installation appears to have been well done, almost as if it was original, or done by a plumber.

    There is a passive radon vent installed into the sump pit, but again, very common for the area and shouldn't have anything to do with the drain / vent plumbing.

    I basically identified what it appeared to be, that it was not a typical installation, may not be installed in an "approved" manner, to ask for any information available from the seller, and consult a licensed plumber.

    I was curious if there was another fitting that I wasn't aware of that I may have been mistaken for a check valve... Or if anyone else has seen anything like this, and why?


  8. #8
    Join Date
    Feb 2009
    Location
    Southern Vancouver Island
    Posts
    4,607

    Default Re: Check Valve? on drain / vent pipe

    It is probably just a connector, and not a check valve.
    That doesn't explain why it is there, but plumbers are known for their mysterious ways.
    A cleanout or a slip joint would make a bit of sense.

    John Kogel, RHI, BC HI Lic #47455
    www.allsafehome.ca

  9. #9
    Join Date
    Oct 2010
    Location
    MONTREAL QUEBEC-CANADA
    Posts
    2,075

    Default Re: Check Valve? on drain / vent pipe

    In the basement it might be anti back water protection from being tapped down stream another waste discharge due to accessibility in the condo. In other words, non-compliant install.

    Robert Young's Montreal Home Inspection Services Inc.
    Call (514) 489-1887 or (514) 441-3732
    Our Motto; Putting information where you need it most, "In your hands.”

  10. #10
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: Check Valve? on drain / vent pipe

    Quote Originally Posted by Andrew Kolar View Post
    This is a two story townhouse condominium ...
    Robert's last post brought up a good question: is it a townhouse or a condominium?

    A townhouse is under the residential code, a condo is under the building code and other codes (the MEP codes).

    There are significant differences is various code aspects between a condo and a townhouse.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  11. #11
    Join Date
    Oct 2010
    Location
    MONTREAL QUEBEC-CANADA
    Posts
    2,075

    Default Re: Check Valve? on drain / vent pipe

    Quote Originally Posted by Jerry Peck View Post
    Robert's last post brought up a good question: is it a townhouse or a condominium?

    A townhouse is under the residential code, a condo is under the building code and other codes (the MEP codes).

    There are significant differences is various code aspects between a condo and a townhouse.
    Good point.

    Last edited by ROBERT YOUNG; 01-16-2016 at 05:44 AM.
    Robert Young's Montreal Home Inspection Services Inc.
    Call (514) 489-1887 or (514) 441-3732
    Our Motto; Putting information where you need it most, "In your hands.”

  12. #12
    Join Date
    Mar 2007
    Location
    Santa Rosa, CA
    Posts
    3,154

    Default Re: Check Valve? on drain / vent pipe

    Quote Originally Posted by Andrew Kolar View Post
    I found this behind a wall access panel directly behind the washing machine, just a few inches above the basement floor. I am sure this is where the washing machine stand pipe is connected, and the vent extends straight up vertically. Is that a check valve? If so, is that a problem? I have never seen a check valve installed on the drain / vent plumbing...
    I am unclear why you think that might be a check valve. To the best of my knowledge, a downflow check valve needs to be spring loaded. Other than the flange, was there any widening of the pipe where a check valve would be housed?

    Department of Redundancy Department
    Supreme Emperor of Hyperbole
    http://www.FullCircleInspect.com/

  13. #13
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: Check Valve? on drain / vent pipe

    Quote Originally Posted by Gunnar Alquist View Post
    I am unclear why you think that might be a check valve. To the best of my knowledge, a downflow check valve needs to be spring loaded. Other than the flange, was there any widening of the pipe where a check valve would be housed?
    It does resemble what a flanged version of these ( Spring check valve / threaded / flange / PVC - JC series - Shie Yu Machine Parts Industrial Co., Ltd. ) would look like from that angle - you would see the flange and the bulbous shape below the flange, similar to what is in the photo ... zoom in to 500% and you can see the shadows and bulbous shape somewhat.

    That was my guess as to why he thought it might be a check valve.

    I don't know why there would be one of those in that waste pipe.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  14. #14
    Join Date
    Oct 2010
    Location
    MONTREAL QUEBEC-CANADA
    Posts
    2,075

    Default Re: Check Valve? on drain / vent pipe

    Quote Originally Posted by Jerry Peck View Post
    That was my guess as to why he thought it might be a check valve.
    Resembles this type of check valve. Deluxe sump check valve.


    • This sump pump check valve features:
      • Eliminates back flow from standpipe to sump pump basin
      • Design allows for maximum pumping capacity while reducing pump cycling and vibration
      • Less frequent cycling helps prolong pump motor life
      • 2 rubber sleeves
      • 4 stainless steel hose clamps
      • Allows pump to be serviced without cutting pipe
      • Designed for low pressure systems - 4.3 psi (10' of head)
      • Deluxe model shown left


    Keep water from returning to the sump pit or crawl space after the pump shuts off with a Sump Pump Check Valve.
    https://www.plumbingsupply.com/sump_...ck_valves.html

    Tell me what you think.
    check valve a.JPG

    Robert Young's Montreal Home Inspection Services Inc.
    Call (514) 489-1887 or (514) 441-3732
    Our Motto; Putting information where you need it most, "In your hands.”

  15. #15
    Join Date
    Oct 2010
    Location
    MONTREAL QUEBEC-CANADA
    Posts
    2,075

    Default Re: Check Valve? on drain / vent pipe

    Andrew, what plumbing stations are to the right of the assembly? Either on the same level or the next level up. same level, garage utility sink? Upstairs or same level, a water closet, shower stall.

    Robert Young's Montreal Home Inspection Services Inc.
    Call (514) 489-1887 or (514) 441-3732
    Our Motto; Putting information where you need it most, "In your hands.”

  16. #16
    Join Date
    Feb 2008
    Location
    Iowa City, IA
    Posts
    108

    Default Re: Check Valve? on drain / vent pipe

    Technically the home is a condominium.

    I am not sure that what is in the picture is a check valve. The portion of the fitting I can see, just resembled check valves that I have seen, and I am not familiar with any other plumbing fitting or connectors that look like this. However, that is part of why I posted this, in hopes that someone knew exactly what it was, and why it may have been installed there.

    This pipe is inside of the wall behind the laundry appliances, and while I can not see it, I am sure the horizontal arm that comes of the T is the stand pipe drain. No other fixtures in the basement (other than the floor drain already mentioned). There is a 1/2 bathroom on the floor above the basement, and two bathrooms on the 2nd floor above that.


  17. #17
    Join Date
    Mar 2007
    Location
    Garland, TX
    Posts
    652

    Default Re: Check Valve? on drain / vent pipe


    get a bar code/qr code app
    or clear shot of bar code for later research
    no more issue identifying materials

    badair http://www.adairinspection.com Garland, TX 75042
    Commercial-Residential-Construction-EIFS-Stucco-ACMV-Infrared Thermography
    life is the random lottery of events followed by numerous narrow escapes...accept the good

  18. #18
    Join Date
    Mar 2007
    Location
    Kalamazoo, MI
    Posts
    117

    Default Re: Check Valve? on drain / vent pipe

    It may be there (and code required) to prevent sewer backups into the home (simple as that).

    - - - Updated - - -

    It may be there (and code required) to prevent sewer backups into the home (simple as that).

    - - - Updated - - -

    It may be there (and code required) to prevent sewer backups into the home (simple as that).

    RJDalga
    http://homeanalysts.com
    Kalamazoo, MI

  19. #19
    Join Date
    Feb 2008
    Location
    Iowa City, IA
    Posts
    108

    Default Re: Check Valve? on drain / vent pipe

    It would backup through the floor drain before that valve did any good...