Results 1 to 9 of 9

Thread: Ufer ground

  1. #1
    Join Date
    Oct 2010
    Location
    MONTREAL QUEBEC-CANADA
    Posts
    2,075

    Default Ufer ground

    In concrete construction I may come across 2 aluminium conductors at the water main pipe.
    One attached to the water pipe at the sub-out, the service ground, the other exposed several inches but not connected to the main water pipe.
    My questions are, would this be a Ufer visual verification point.
    If so do you address the conductor in the report.
    Thanks in advance.
    grounding conductor.jpg

    Similar Threads:
    Crawl Space Creeper
    Robert Young's Montreal Home Inspection Services Inc.
    Call (514) 489-1887 or (514) 441-3732
    Our Motto; Putting information where you need it most, "In your hands.”

  2. #2
    Join Date
    Mar 2012
    Location
    Northern Indiana
    Posts
    98

    Default Re: Ufer ground

    If they're aluminum, it is a code violation. Ufers should be terminated at the service disconnect.
    They look like copper to me.


  3. #3
    Join Date
    Oct 2010
    Location
    MONTREAL QUEBEC-CANADA
    Posts
    2,075

    Default Re: Ufer ground

    Brad thank you.
    I concur. It certainly looks like copper.
    The patina on the copper had me confused.

    Aluminium feeds are typical in developments in my neck of the woods.
    Time to open dead fronts again when I can.
    Best regards.

    Robert Young's Montreal Home Inspection Services Inc.
    Call (514) 489-1887 or (514) 441-3732
    Our Motto; Putting information where you need it most, "In your hands.”

  4. #4
    Join Date
    Feb 2008
    Location
    Caledon, Ontario
    Posts
    4,982

    Default Re: Ufer ground

    Robert,

    I don't know about Que. but in Ontario Aluminum is not used for grounding only copper as aluminum is prone to corrosion. They do use aluminum for feeders from the street though since copper is pretty pricey.

    Judging by the valve that's an older incoming water line and me thinks that you likely have grounding rods used rather than Uffer or they used the incoming water line for ground.


  5. #5
    Join Date
    Dec 2008
    Location
    Maryland
    Posts
    2,809

    Default Re: Ufer ground

    Is there a requirement that the wire be solid???


  6. #6
    Join Date
    Feb 2008
    Location
    Caledon, Ontario
    Posts
    4,982

    Default Re: Ufer ground

    Its all stranded.


  7. #7
    Join Date
    Mar 2007
    Location
    Santa Rosa, CA
    Posts
    3,154

    Default Re: Ufer ground

    Quote Originally Posted by Garry Sorrells View Post
    Is there a requirement that the wire be solid???
    I recall asking that same question a number of years ago and the answer was no. The wire gauge is the important part. Unfortunately, I am buried right now and do not have time to look it up for you.

    Department of Redundancy Department
    Supreme Emperor of Hyperbole
    http://www.FullCircleInspect.com/

  8. #8
    Join Date
    Feb 2008
    Location
    Caledon, Ontario
    Posts
    4,982

    Smile Re: Ufer ground

    According to the Cdn Elect. Code

    1. The conductor must be bare
    2. Conductor must be copper
    3. Two ground rods minimum, sometimes more may be required.
    4. Ten feet apart

    Six ga. is minimum or larger to connect the ground rods together and back to service panel.

    For water piping -

    Ten feet is required of continuously conductive metal water piping system that is located underground at least 24 inches below finished grade.

    Concrete Encased Electrode -

    1. Single copper conductor
    2. Four ga. or larger
    3. At least 20 ft. long (min.) but can be longer

    Sections above were taken from PS KNIGHT Electrical Code Simplified based on 22nd Edition of Ont. Elec. Safety Code.


  9. #9
    Join Date
    Oct 2010
    Location
    MONTREAL QUEBEC-CANADA
    Posts
    2,075

    Default Re: Ufer ground

    Quote Originally Posted by Raymond Wand View Post
    According to the Cdn Elect. Code

    1. The conductor must be bare
    2. Conductor must be copper
    3. Two ground rods minimum, sometimes more may be required.
    4. Ten feet apart

    Six ga. is minimum or larger to connect the ground rods together and back to service panel.

    For water piping -

    Ten feet is required of continuously conductive metal water piping system that is located underground at least 24 inches below finished grade.

    Concrete Encased Electrode -

    1. Single copper conductor
    2. Four ga. or larger
    3. At least 20 ft. long (min.) but can be longer

    Sections above were taken from PS KNIGHT Electrical Code Simplified based on 22nd Edition of Ont. Elec. Safety Code.
    Thanks, in my files.
    Everyone, much thanks.

    Raymond Wand! I am truly surprised at you. Sections above were taken from PS KNIGHT Electrical Code and not the CSA electrical safety standard? ha ha ha!!!!
    Good on you mate!

    Robert Young's Montreal Home Inspection Services Inc.
    Call (514) 489-1887 or (514) 441-3732
    Our Motto; Putting information where you need it most, "In your hands.”

Tags for this Thread

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •