Results 1 to 5 of 5
  1. #1
    Join Date
    Mar 2011
    Location
    Corinth, NY
    Posts
    90

    Default distribution panel questions

    Scratching my head over this one. The distribution panel seen at right of the main panel, feeds a second distribution panel on the 2nd floor, that I could not remove the cover as it is blocked by closet shelving. But, isn't the feed to the dist panel suposed to go to the lugs, then the wire to the 2nd dist panel come from from the 100 amp breaker? Yes, I see there are only 2 wires to the dist panel.

    Also, notice the 2 wires comming out of the dist panel. They feed the pool, and it picks up a 3rd wire from the main panel, see at the right of the main panel, three of them going through the foundation wall.

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Member Benefits1

  2. #2
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,036

    Default Re: distribution panel questions

    First photo:
    - Looks like the service equipment panel with service entrance cable entering at the upper right.

    ... I looked at the photos and there is so much wrong there that I stopped looking at each thing and simply went with ... a competent and licensed electrical contractor needs to redo all the panels and wiring to where they meet code as a minimum and are safe.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  3. #3
    Join Date
    Aug 2008
    Location
    Maryland
    Posts
    1,970

    Default Re: distribution panel questions

    I agree with Jerry, there is more wrong than right here. The loose conductors outside of conduit. The 3 wire feed. Possibly a missing breaker hold-down.

    However, the panel is fed with 3 wires, not 2 as you state. It should have bee fed with 4.

    - - - Updated - - -

    I agree with Jerry, there is more wrong than right here. The loose conductors outside of conduit. The 3 wire feed. Possibly a missing breaker hold-down.

    However, the panel is fed with 3 wires, not 2 as you state. It should have been fed with 4.

    All answers based on unamended National Electrical codes.

  4. #4
    Join Date
    Mar 2011
    Location
    Corinth, NY
    Posts
    90

    Default Re: distribution panel questions

    I guess I meant 2 wires and ground.


  5. #5
    Join Date
    Dec 2007
    Location
    Chico,Ca
    Posts
    454

    Default Re: distribution panel questions

    It needs some attention by someone who knows what they are doing, the existing subpanel is just a good example of what not to do.


Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •