  1. #1

    Default Can a service panel be considered grounded with only metalli conduit

    Our local utility requires a continuous unbroken ground wire from the ground rod through the meter to the neutral buss in the service panel on new construction. Many of the older services we inspect do not have a ground wire from the meter in and rely only on the conduit for grounding. How do you handle this, does the NEC require the continuous ground wire or is this local preference

    Similar Threads:
    OREP Insurance

  2. #2
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: Can a service panel be considered grounded with only metalli conduit

    The GEC (Grounding Electrode Conductor) is required to be continuous between the first grounding electrode and the service equipment (or meter, depending on where the utility wants it connected).

    No splices (except for exothermic welded or irreversible compression connector).

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  3. #3

    Default Re: Can a service panel be considered grounded with only metalli conduit

    Quote Originally Posted by Jerry Peck View Post
    The GEC (Grounding Electrode Conductor) is required to be continuous between the first grounding electrode and the service equipment (or meter, depending on where the utility wants it connected).

    No splices (except for exothermic welded or irreversible compression connector).
    Let me try a little harder. If the meter is grounded as above,does metallic conduit leading from the meter base to the service panel provide a proper grounding source or does the ground wire have to continue to the service panel?


  4. #4
    Join Date
    Mar 2012
    Location
    Northern Indiana
    Posts
    98

    Default Re: Can a service panel be considered grounded with only metalli conduit

    Yes, provided the metallic conduit and fittings are of the proper type and installed properly.


  5. #5
    Join Date
    Oct 2010
    Location
    MONTREAL QUEBEC-CANADA
    Posts
    2,075

    Default Re: Can a service panel be considered grounded with only metalli conduit

    In that case, "the meter is grounded as above," service equipment requires bonding.

    Can you please describe the (GEC) in your meter situation please.
    I ask because you appear to be having a hard time describing the equipment.
    Where does it start or end, what is it connected to, both ends.
    Also what is the conductor/cable and gauge of the cable?
    Do not open or touch anything PLEASE!

    Random question, is the meter a disconnect? Breakers at the metering box?

    Here is a link from Mike H. on grounding and bonding.
    http://ecmweb.com/code-basics/ground...nding-part-1-3
    As you can see it is in three parts. It is not simple and admittedly to me some took time to be familiar with the full scope of bonding, grounding and the equipment. And that is just single phase current.

    PS: Sorry for the editing.

    Last edited by ROBERT YOUNG; 08-27-2016 at 05:52 AM. Reason: adding
    Robert Young's Montreal Home Inspection Services Inc.
    Call (514) 489-1887 or (514) 441-3732
    Our Motto; Putting information where you need it most, "In your hands.”

  6. #6
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: Can a service panel be considered grounded with only metalli conduit

    My recollection is that the NEC says that the GEC terminates in the service equipment, but also allows it to terminate in the meter (I don't have my codes with me).

    The meter enclosure and the service equipment enclosure are to be bonded together (thus the specificity of grounding bushings in reference service equipment - but keep in mind that grounding bushings are not an approved "continuous" fitting connection).

    Also, some utilities like to try to enforce their regulations beyond where their regulations stop and the NEC starts.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  7. #7
    Join Date
    Oct 2010
    Location
    MONTREAL QUEBEC-CANADA
    Posts
    2,075

    Default Re: Can a service panel be considered grounded with only metalli conduit

    Jerry, when you get back, I say when you get back because typically you are away from your PC when you say, (I don't have my codes with me). I would like to clarify something.
    At times ground rods and GEC cables are required for both, the meter and service equipment if I am not mistaken.
    If you could clarify this it would be much appreciated.

    Have a good outing.


    Robert Young's Montreal Home Inspection Services Inc.
    Call (514) 489-1887 or (514) 441-3732
    Our Motto; Putting information where you need it most, "In your hands.”

  8. #8
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: Can a service panel be considered grounded with only metalli conduit

    Robert,

    Sometimes a meter is installed remotely from the service equipment, sometimes a meter is not related to service equipment - either way the metal meter enclosure is required to be grounded.

    How the meter is used and wired controls how it is grounded.

    Keep in mind that all grounding electrodes installed for a service/structure are required to be bonded together.

    Also, only the first GEC from the service equipment is required to be continuous and not spliced.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  9. #9
    Join Date
    Oct 2010
    Location
    MONTREAL QUEBEC-CANADA
    Posts
    2,075

    Default Re: Can a service panel be considered grounded with only metalli conduit

    Quote Originally Posted by Jerry Peck View Post
    Robert,

    Sometimes a meter is installed remotely from the service equipment, sometimes a meter is not related to service equipment - either way the metal meter enclosure is required to be grounded.

    How the meter is used and wired controls how it is grounded.

    Keep in mind that all grounding electrodes installed for a service/structure are required to be bonded together.

    Also, only the first GEC from the service equipment is required to be continuous and not spliced.
    That I understand. Thanks.
    When are two ground rods required.

    Robert Young's Montreal Home Inspection Services Inc.
    Call (514) 489-1887 or (514) 441-3732
    Our Motto; Putting information where you need it most, "In your hands.”

  10. #10
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: Can a service panel be considered grounded with only metalli conduit

    Quote Originally Posted by ROBERT YOUNG View Post
    When are two ground rods required.
    When using ground rods one must test and document less than 25 ohms to earth ... or install a second ground rod.

    Being as few contractors have the proper equipment or use the proper method of testing ... or want to spend the time to only prove there is not less than 25 ohms to ground ... simply drive a second gground rod.

    Here is the worst case I've seen: electrical contractor installed the second ground rod 5 feet from the first ground rod (6 feet is the minimum separation between ground rods) ... he grabbed the top of the second ground rod with his Channel Locks (or other brand) and pulled the ground rod out of the ground, moved about 3 feet, asked if this was good, then shoved the ground rod down into the earth ... as I stood there watching in bewilderment.

    The sand allowed to rods to be shoved in an pulled back out that easily.

    Of course, though, that raised another question - minimum depth.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  11. #11
    Join Date
    Oct 2010
    Location
    MONTREAL QUEBEC-CANADA
    Posts
    2,075

    Default Re: Can a service panel be considered grounded with only metalli conduit

    Quote Originally Posted by Jerry Peck View Post
    When using ground rods one must test and document less than 25 ohms to earth ... or install a second ground rod.

    Being as few contractors have the proper equipment or use the proper method of testing ... or want to spend the time to only prove there is not less than 25 ohms to ground ... simply drive a second gground rod.

    Here is the worst case I've seen: electrical contractor installed the second ground rod 5 feet from the first ground rod (6 feet is the minimum separation between ground rods) ... he grabbed the top of the second ground rod with his Channel Locks (or other brand) and pulled the ground rod out of the ground, moved about 3 feet, asked if this was good, then shoved the ground rod down into the earth ... as I stood there watching in bewilderment.

    The sand allowed to rods to be shoved in an pulled back out that easily.

    Of course, though, that raised another question - minimum depth.
    I think 6 feet is the required minimum depth but material conduction is the essence of the GEC and equipment.

    I used a small excavator to remove a ground once. I have even used a car jack.
    When the electrician removed the ground rod effortlessly with channel locks he should have considered conductivity.
    Senseless grounding at that point.
    Wow.

    Robert Young's Montreal Home Inspection Services Inc.
    Call (514) 489-1887 or (514) 441-3732
    Our Motto; Putting information where you need it most, "In your hands.”

  12. #12
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: Can a service panel be considered grounded with only metalli conduit

    Quote Originally Posted by ROBERT YOUNG View Post
    I think 6 feet is the required minimum depth but material conduction is the essence of the GEC and equipment.
    The minimum depth to the top of the ground rod is at permanent moisture level, the minimum rod length is 8 feet.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  13. #13
    Join Date
    Oct 2010
    Location
    MONTREAL QUEBEC-CANADA
    Posts
    2,075

    Default Re: Can a service panel be considered grounded with only metalli conduit

    Quote Originally Posted by Jerry Peck View Post
    The minimum depth to the top of the ground rod is at permanent moisture level, the minimum rod length is 8 feet.
    Just checking to see if you are paying attention.

    Robert Young's Montreal Home Inspection Services Inc.
    Call (514) 489-1887 or (514) 441-3732
    Our Motto; Putting information where you need it most, "In your hands.”

  14. #14
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: Can a service panel be considered grounded with only metalli conduit

    How deep is minimum moisture level?

    Depends.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  15. #15
    Join Date
    Oct 2010
    Location
    MONTREAL QUEBEC-CANADA
    Posts
    2,075

    Default Re: Can a service panel be considered grounded with only metalli conduit

    Quote Originally Posted by Jerry Peck View Post
    How deep is minimum moisture level?

    Depends.
    Conductivity.
    Think of this, slab construction ufer is not 8' deep.
    Another grounding principle but, the proper conduction exists.

    Thanks.

    Robert Young's Montreal Home Inspection Services Inc.
    Call (514) 489-1887 or (514) 441-3732
    Our Motto; Putting information where you need it most, "In your hands.”

  16. #16
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: Can a service panel be considered grounded with only metalli conduit

    Quote Originally Posted by ROBERT YOUNG View Post
    Conductivity.
    Think of this, slab construction ufer is not 8' deep.
    Another grounding principle but, the proper conduction exists.

    Thanks.
    A concrete encased electrode is a completely different animal and has completely different requirements.

    It's about 'intended'... or 'hopeful' ... 'conductivity to earth' ... as in 'three ground rods are not required', the second, yes - a third, no. If two don't do it, don't bother with a third.

    Ground rings are a different matter - typically ground rings around communication power transformers (all the ones I've inspected anyway) have a ground rod at each corner and typically one in the center of each side that exceeds 10 feet (5 foot spacing in the engineered system) with the ground ring conductor exothermically welded to the ground rods. Special enclosures were installed over and around each connection which required a special tool to open (I still have the one the AT&T guys gave me).

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  17. #17

    Default Re: Can a service panel be considered grounded with only metalli conduit

    Quote Originally Posted by ROBERT YOUNG View Post
    In that case, "the meter is grounded as above," service equipment requires bonding.

    Can you please describe the (GEC) in your meter situation please.
    I ask because you appear to be having a hard time describing the equipment.
    Where does it start or end, what is it connected to, both ends.
    Also what is the conductor/cable and gauge of the cable?
    Do not open or touch anything PLEASE!

    Random question, is the meter a disconnect? Breakers at the metering box?

    Here is a link from Mike H. on grounding and bonding.
    http://ecmweb.com/code-basics/ground...nding-part-1-3
    As you can see it is in three parts. It is not simple and admittedly to me some took time to be familiar with the full scope of bonding, grounding and the equipment. And that is just single phase current.

    PS: Sorry for the editing.
    Robert

    This is a simple meter mounted on the outside of the house typically connected to the 100 amp Service Panel for Jerry (main breaker box for most of us) by 1 1/4" ridged conduit with less than a 10 foot run. wire would be #4 copper and #6 ground wire from the ground rod runs unbroken through the meter base and the ridged conduit to the service panel inside the house. grounding bushing are required at the meter base and the service panel.

    Is this clearer. This what the utility wants the question is are they adding to the NEC or is this correct?

    Thanks enjoy your answers

    Don

    - - - Updated - - -

    Quote Originally Posted by ROBERT YOUNG View Post
    In that case, "the meter is grounded as above," service equipment requires bonding.

    Can you please describe the (GEC) in your meter situation please.
    I ask because you appear to be having a hard time describing the equipment.
    Where does it start or end, what is it connected to, both ends.
    Also what is the conductor/cable and gauge of the cable?
    Do not open or touch anything PLEASE!

    Random question, is the meter a disconnect? Breakers at the metering box?

    Here is a link from Mike H. on grounding and bonding.
    http://ecmweb.com/code-basics/ground...nding-part-1-3
    As you can see it is in three parts. It is not simple and admittedly to me some took time to be familiar with the full scope of bonding, grounding and the equipment. And that is just single phase current.

    PS: Sorry for the editing.
    Robert

    This is a simple meter mounted on the outside of the house typically connected to the 100 amp Service Panel for Jerry (main breaker box for most of us) by 1 1/4" ridged conduit with less than a 10 foot run. wire would be #4 copper and #6 ground wire from the ground rod runs unbroken through the meter base and the ridged conduit to the service panel inside the house. grounding bushing are required at the meter base and the service panel.

    Is this clearer. This what the utility wants the question is are they adding to the NEC or is this correct?

    Thanks enjoy your answers

    Don


  18. #18
    Join Date
    Oct 2010
    Location
    MONTREAL QUEBEC-CANADA
    Posts
    2,075

    Default Re: Can a service panel be considered grounded with only metalli conduit

    [QUOTE=Don Hawley;268342]Robert

    This is a simple meter mounted on the outside of the house typically connected to the 100 amp Service Panel for Jerry (main breaker box for most of us) by 1 1/4" ridged conduit with less than a 10 foot run. wire would be #4 copper and #6 ground wire from the ground rod runs unbroken through the meter base and the ridged conduit to the service panel inside the house. grounding bushing are required at the meter base and the service panel.

    Is this clearer. This what the utility wants the question is are they adding to the NEC or is this correct?

    Thanks enjoy your answers

    Don /QUOTE]

    Thanks!
    Jerry says its like trying to to nail jello to a tree. Ha ha ha

    Not quite sure but I did run past an article in Mike Holt's site but had to go out for an inspection.
    I will try to find the article again later on.

    Last edited by ROBERT YOUNG; 08-28-2016 at 10:12 AM.
    Robert Young's Montreal Home Inspection Services Inc.
    Call (514) 489-1887 or (514) 441-3732
    Our Motto; Putting information where you need it most, "In your hands.”

  19. #19
    Join Date
    Oct 2010
    Location
    MONTREAL QUEBEC-CANADA
    Posts
    2,075

    Default Re: Can a service panel be considered grounded with only metalli conduit

    Quote Originally Posted by Jerry Peck View Post
    A concrete encased electrode is a completely different animal and has completely different requirements.
    I concur.
    I think I mentioned that is my post.

    Robert Young's Montreal Home Inspection Services Inc.
    Call (514) 489-1887 or (514) 441-3732
    Our Motto; Putting information where you need it most, "In your hands.”

  20. #20
    Join Date
    Oct 2010
    Location
    MONTREAL QUEBEC-CANADA
    Posts
    2,075

    Default Re: Can a service panel be considered grounded with only metalli conduit

    NEC 250.24(A)(1)
    Grounding electrode conductor must connect the neutral conductor to (a) grounding electrode at the:
    1: Service drop
    2: Meter enclosure. As in your case.
    3: Service disconnect.

    A. Either location is fine with the NEC. The rule states that the grounding electrode conductor must connect the service neutral conductor to the grounding electrode at any accessible location, from the load end of the service drop or service lateral up to and including the service disconnecting means [250.24(A)(1)].

    If you return to post #5, is the meter the service disconnect or a metering box only?
    Sorry I am asking again.

    Robert Young's Montreal Home Inspection Services Inc.
    Call (514) 489-1887 or (514) 441-3732
    Our Motto; Putting information where you need it most, "In your hands.”

  21. #21

    Default Re: Can a service panel be considered grounded with only metalli conduit

    Quote Originally Posted by ROBERT YOUNG View Post
    NEC 250.24(A)(1)
    Grounding electrode conductor must connect the neutral conductor to (a) grounding electrode at the:
    1: Service drop
    2: Meter enclosure. As in your case.
    3: Service disconnect.

    A. Either location is fine with the NEC. The rule states that the grounding electrode conductor must connect the service neutral conductor to the grounding electrode at any accessible location, from the load end of the service drop or service lateral up to and including the service disconnecting means [250.24(A)(1)].

    If you return to post #5, is the meter the service disconnect or a metering box only?
    Sorry I am asking again.
    The first disconnect will be at the service panel (main breaker box)


  22. #22
    Join Date
    Oct 2010
    Location
    MONTREAL QUEBEC-CANADA
    Posts
    2,075

    Default Re: Can a service panel be considered grounded with only metalli conduit

    As to your inquiries "1: Our local utility requires a continuous unbroken ground wire from the ground rod through the meter to the neutral buss in the service panel on new construction. Many of the older services we inspect do not have a ground wire from the meter in and rely only on the conduit for grounding. 2: How do you handle this, 3: does the NEC require the continuous ground wire or is this local preference"

    Looks like I have beaten off more than I can chew.
    I would handle this by calling a local AHJ.

    Robert Young's Montreal Home Inspection Services Inc.
    Call (514) 489-1887 or (514) 441-3732
    Our Motto; Putting information where you need it most, "In your hands.”

  23. #23
    Join Date
    Oct 2010
    Location
    MONTREAL QUEBEC-CANADA
    Posts
    2,075

    Default Re: Can a service panel be considered grounded with only metalli conduit

    Quote Originally Posted by Jerry Peck View Post
    Robert,

    Sometimes a meter is installed remotely from the service equipment, sometimes a meter is not related to service equipment - either way the metal meter enclosure is required to be grounded.

    How the meter is used and wired controls how it is grounded.

    Keep in mind that all grounding electrodes installed for a service/structure are required to be bonded together.

    Also, only the first GEC from the service equipment is required to be continuous and not spliced.
    I know this was covered before. If not here at Inspection news, than at your favourite association, well at least mine although I think it was here.
    Separate grounding rods placed within the required distance allowed. One for the meter, one for the service equipment.

    Sorry to go off thread.

    Robert Young's Montreal Home Inspection Services Inc.
    Call (514) 489-1887 or (514) 441-3732
    Our Motto; Putting information where you need it most, "In your hands.”

  24. #24
    Join Date
    Nov 2010
    Location
    Brentwood, NY
    Posts
    4

    Default Re: Can a service panel be considered grounded with only metalli conduit

    Quote Originally Posted by ROBERT YOUNG View Post
    Conductivity.
    Think of this, slab construction ufer is not 8' deep.
    Another grounding principle but, the proper conduction exists.

    Thanks.
    250.53 (G) Requires:
    -8 foot length of the rod electrode to be in contact with the soil
    -Minimum 8 foot driven depth....except when:
    ----Rock bottom is encountered...it is permitted to be
    ------driven at an oblique angle (up to 45 degrees) OR
    ------Buried in a minimum 30 inch deep trench

    Donald W. Kane, PE


  25. #25
    Join Date
    Aug 2008
    Location
    Maryland
    Posts
    1,970

    Default Re: Can a service panel be considered grounded with only metalli conduit

    To Robert Y, some utilities do not allow grounding in the meter socket.

    - - - Updated - - -

    Quote Originally Posted by Don Hawley View Post
    The first disconnect will be at the service panel (main breaker box)
    The first disconnect will be the service. It does not need to be a panel. Also a panel can have a main breaker without being a service.

    All answers based on unamended National Electrical codes.

  26. #26
    Join Date
    Aug 2008
    Location
    Maryland
    Posts
    1,970

    Default Re: Can a service panel be considered grounded with only metalli conduit

    Quote Originally Posted by Jerry Peck View Post
    The minimum depth to the top of the ground rod is at permanent moisture level, the minimum rod length is 8 feet.
    Can you cite this requirement ? The NEC only says flush or below grade and at least 8 foot in contact with the soil.

    All answers based on unamended National Electrical codes.