Results 1 to 13 of 13
  1. #1
    Join Date
    Sep 2007
    Location
    San Antonio TX
    Posts
    88

    Default How would you write this up

    How would you write this up.
    Thanks

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Inspection Referral

  2. #2
    Richard Stanley's Avatar
    Richard Stanley Guest

    Default Re: How would you write this up

    Open knock outs in j-box and panel.
    debris in panel.
    Double lugged breakers - looks like.
    Can't tell - Are breakers rated for aluminum, Is wire size correct?


  3. #3
    Jesse R Reyes's Avatar
    Jesse R Reyes Guest

    Default Re: How would you write this up

    Appears that there is a meter next to the panel. There should be a main breaker. The aluminum wire is blistering. Overload. The panel is in hazards conditions. Recommend that the panel be Ungraded and that an Electrical Contractor may further evaluations.


  4. #4
    Join Date
    Mar 2007
    Location
    Spring Hill (Nashville), TN
    Posts
    5,851

    Default Re: How would you write this up

    Quote Originally Posted by Zibby Swieca View Post
    How would you write this up.
    Thanks
    I would report; "This is a fire waiting to happen. Call an electrician now".

    Scott Patterson, ACI
    Spring Hill, TN
    www.traceinspections.com

  5. #5
    Join Date
    Mar 2007
    Location
    Chicago, IL
    Posts
    2,797

    Default Re: How would you write this up

    Closer look:

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images

  6. #6
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: How would you write this up

    "Open knock outs in j-box ... "

    Non-weatherproof box and cover not rated for use outdoors and installed outdoors, also has open knock out - replace with weatherproof box and cover approved for use outdoors (i.e., in "wet locations").

    Is that asbestos cement siding shingles?

    Service equipment has melted insulation which indicates overheating, typically caused by loose connections.

    Service equipment currently has 5 main breakers and space for one more, make sure not to install two breakers in the remaining double pole main breaker location.

    Open knock outs in service equipment has allowed animals/birds to bring combustible debris into the enclosure, combustible debris is in contact with, or close proximity to, energized components - this could lead to fire or electrical shock. Open knock out into wall cavity allows animals/birds to enter into the wall cavity.

    What appears to be the grounding electrode conductor is bolted together - if this is the grounding electrode conductor this is not allowed until after the first grounding electrode,

    That will do for starters to get and electrical contractor out there to correct everything you listed, and everything they find, and everything they create while making corrections.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  7. #7
    Donald Merritt's Avatar
    Donald Merritt Guest

    Default Re: How would you write this up

    Look for a dead bird or mouse.


  8. #8
    Join Date
    Mar 2007
    Location
    Georgetown, KY
    Posts
    538

    Default Re: How would you write this up

    Breakers installed with "on" in the down position.

    I like Scott's but always find it necessary (in my own mind and in good reporting practices) to expound a little bit on "why" it's a fire hazard.

    Erby Crofutt, Georgetown, KY - Read my Blog here: Erby the Central Kentucky Home Inspector B4 U Close Home Inspections www.b4uclose.com www.kentuckyradon.com
    Find on Facebook at: https://www.facebook.com/B4UCloseInspections

  9. #9
    James Duffin's Avatar
    James Duffin Guest

    Default Re: How would you write this up

    It looks like a NEMA 3R box mounted sideways. It's made to be mounted verticle...not horizontal.


  10. #10
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: How would you write this up

    Erby, James,

    The photo was just taken sideways. The box (enclosure) is installed vertically - look at the grain in the siding.

    I know, photos should always be taken with 'up' being 'up', or, when trying to fit more into the photo, rotating the photo before using it anywhere so that 'up' is 'up'.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  11. #11
    Join Date
    Mar 2007
    Location
    Healdsburg, CA
    Posts
    1,741

    Default Re: How would you write this up

    Don't forget "over-fusing!"

    Jerry McCarthy
    Building Code/ Construction Consultant

  12. #12
    Shannon Guinn's Avatar
    Shannon Guinn Guest

    Default Re: How would you write this up

    Quote Originally Posted by Scott Patterson View Post
    I would report; "This is a fire waiting to happen. Call an electrician now".
    I concur with Scott.


  13. #13
    Shannon Guinn's Avatar
    Shannon Guinn Guest

    Default Re: How would you write this up

    I also concur with Jerry.


Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •