    Default roof felt touching water heater vent pipe

    I see this frequently in attics- the gas appliance vent pipe has proper clearance from the trusses and sheathing but the roof felt paper is touching the vent pipe. Do you call this?

    IMG_4430.JPG

    Similar Threads:
    Member Benefits1
    I have not failed. I've just found 10,000 ways that won't work. (Thomas Edison)

  2. #2
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: roof felt touching water heater vent pipe

    Ever try to set that stuff on fire? Or accidentally set it on fire ... yeah, they catch on fire and are thus combustible material ... and need to be called out.

    Laziness on the roofer's part is not an excuse for doing/not doing something, although laziness on the roofer's part could allow/cause the house to burn down.

    ! inch clearance minimum is typical for double wall Type B gas vents, and 6 inches for single wall gas vents.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  3. #3
    Join Date
    Mar 2007
    Location
    Near Philly, Pa.
    Posts
    1,682

    Default Re: roof felt touching water heater vent pipe

    why would you not call it out?

    Keep the fire in the fireplace.