Results 1 to 3 of 3
  1. #1
    Scott Lynch's Avatar
    Scott Lynch Guest

    Default Wiring in A/C disconnect box

    Last edited by Scott Lynch; 12-20-2007 at 04:45 PM.
    Member Benefits1

  2. #2
    Join Date
    Aug 2007
    Location
    Memphis TN.
    Posts
    4,311

    Default Re: Wiring in A/C disconnect box

    Scott

    The 14 gauge wire is not connected to this HVAC disconnect box and should be enclosed in it's own box.

    Last edited by Billy Stephens; 12-10-2007 at 05:27 PM. Reason: HVAC
    It Might have Choked Artie But it ain't gone'a choke Stymie! Our Gang " The Pooch " (1932)
    Billy J. Stephens HI Service Memphis TN.

  3. #3
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: Wiring in A/C disconnect box

    That's the low voltage wiring ... see it coming out of the fitting with the power conductors?

    *NOT ALLOWED* in the same raceway or enclosure as the power conductors.

    By the way, you also wrote up the white wire with the red tape, right?

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •