    Default six throws to shut off power ?

    Hello group. I bought a new home 17 years ago and recently had a pre-inspection done.

    The inspector said we do not have a main breaker. And the "six throws to shut off power" could not be determined.

    Can you tell me by looking if this type has the six throws?inside.jpgOutside.jpg

    Similar Threads:
    Inspection Referral

  2. #2
    Join Date
    Mar 2007
    Location
    Plano, Texas
    Posts
    185

    Default Re: six throws to shut off power ?

    I'm thinking I can do it in 5! Unless there is a submarine connected to that top outdoor breaker.
    Looks like it says Sub Panel but we don't have those any longer....do we?
    Outside is service and it looks like the top breaker turns off the indoor panel.


  3. #3
    Join Date
    Oct 2010
    Location
    MONTREAL QUEBEC-CANADA
    Posts
    2,075

    Default Re: six throws to shut off power ?

    six throws to shut off power , Misnomer.
    225.33 says that you cannot have more than six means of disconnet at the second structure.

    (A) General. The service disconnecting means for each service permitted by 230.2, or for each set of service entrance conductors permitted by 230.40, Exception No. 1, 3, 4, or 5, shall consist of not more than six switches or sets of circuit breakers, or a combination of not more than six switches and sets of circuit breakers, mounted in a single enclosure, in a group of separate enclosures, or in or on a switchboard.

    This code rule is for the electric service only. It does not apply to sub-fed panels

    http://www.inspectionnews.net/home_i...off-panel.html

    Last edited by ROBERT YOUNG; 02-13-2017 at 05:30 PM.
    Robert Young's Montreal Home Inspection Services Inc.
    Call (514) 489-1887 or (514) 441-3732
    Our Motto; Putting information where you need it most, "In your hands.”

  4. #4
    Join Date
    Mar 2012
    Location
    Lansdale, PA
    Posts
    876

    Default Re: six throws to shut off power ?

    It is hard to see the label, at least viewing on my phone. It appears that the panel was designed to have six 240 volt breakers. As it is now there are less than six. If too many 120 breakers are added you could exceed 6.


  5. #5
    Join Date
    Dec 2008
    Location
    Maryland
    Posts
    2,809

    Default Re: six throws to shut off power ?

    George,
    The HI may be saying that since he did not remove the panel cover next to the meter he could not determine that the panel completely controlled all service. Else it would appear that the 5 shown would meet the requirements.


  6. #6
    Join Date
    Jun 2008
    Location
    Maryland
    Posts
    1,096

    Default Re: six throws to shut off power ?

    If the top breaker on the outdoor panel shuts off the indoor (sub) panel, its fine as is. Did the inspector pull either cover?


  7. #7

    Default Re: six throws to shut off power ?

    In NC the primary panel must be able to be shut down with 6 hand moments or less. Based on the information provided you would need 5 so barring other issues it is ok. The other panel is the distributions panel

    Jeff Zehnder - Home Inspector, Raleigh, NC
    http://www.jjeffzehnder.com/
    http://carolinahomeinspections.com/

  8. #8
    Join Date
    Mar 2013
    Location
    Md and or PA
    Posts
    137

    Default Re: six throws to shut off power ?

    Quote Originally Posted by George Eberle View Post
    Hello group. I bought a new home 17 years ago and recently had a pre-inspection done.

    The inspector said we do not have a main breaker. And the "six throws to shut off power" could not be determined.

    Can you tell me by looking if this type has the six throws?inside.jpgOutside.jpg
    I would suggest you get your money back ! If the "inspector" could not figure out this most basic item............................


  9. #9
    Join Date
    Dec 2008
    Location
    Maryland
    Posts
    2,809

    Default Re: six throws to shut off power ?

    Quote Originally Posted by jack davenport View Post
    I would suggest you get your money back ! If the "inspector" could not figure out this most basic item............................
    Could it have been a Certified Professional ????