    Default Double taped breakers

    I have a local sparky telling the seller that it is OK to double tap breakers. Seller’s agent tells the buyer’s agent his guy says it’s ok. Now the buyer is questioning my very good agent on whether we are competent or not. Can anyone provide me with a code reference; all I can find on short notice is 408.1 dealing with double taping neutrals. Yes this is an emergency we need to provide an answer by tomorrow morning.

    Similar Threads:
    Crawl Space Creeper

  2. #2
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: Double taped breakers

    Quote Originally Posted by Don Hawley View Post
    I have a local sparky telling the seller that it is OK to double tap breakers. Seller’s agent tells the buyer’s agent his guy says it’s ok. Now the buyer is questioning my very good agent on whether we are competent or not. Can anyone provide me with a code reference; all I can find on short notice is 408.1 dealing with double taping neutrals. Yes this is an emergency we need to provide an answer by tomorrow morning.
    NEC (basically any edition in the last 30-40 years) 110.3(B).

    That states that all listed and labeled electrical equipment are to be installed and used in accordance with the information include in their listing and labeling.

    If the breaker does not specifically ... specifically ... state that it is listed for use with more than one conductor, then continue to 110.14 (also basically any edition in the last 30 years or so) which states that terminals for aluminum ... and for more than one conductor ... shall be so identified. Many people miss that last part 'for more than one conductor' shall be so identified.

    Just make sure it is not one of the breakers with terminal designed to accept two conductors.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  3. #3
    Join Date
    Oct 2010
    Location
    MONTREAL QUEBEC-CANADA
    Posts
    2,075

    Default Re: Double taped breakers

    You posted this on NACHI emergency forum.
    I just posted 110.3(B).

    Like a Cutler Hammer breaker.


    Robert Young's Montreal Home Inspection Services Inc.
    Call (514) 489-1887 or (514) 441-3732
    Our Motto; Putting information where you need it most, "In your hands.”

  4. #4
    Join Date
    Aug 2008
    Location
    Maryland
    Posts
    1,970

    Default Re: Double taped breakers

    What size and brand of breaker? A picture might help.

    All answers based on unamended National Electrical codes.

  5. #5

    Default Re: Double taped breakers

    Quote Originally Posted by ROBERT YOUNG View Post
    You posted this on NACHI emergency forum.
    I just posted 110.3(B).

    Like a Cutler Hammer breaker.
    Thanks Guys

    Yes I posted this twice and got good answers both places

    I see a lot of Square D breakers rated for two wires not many Cutler Hammer always have to look twice at any double tap.

    I am guessing my alter ego electrician also does landscaping and snow removal, never get questioned on this by a qualified electrician


  6. #6
    Join Date
    Jan 2008
    Location
    Northern Wisconsin
    Posts
    8

    Default Re: Double taped breakers

    To my knowledge, the only circuit breakers that may be rated for double taps(same conductor make and size) are the Square-D QO and homeline series.


  7. #7
    Join Date
    Aug 2008
    Location
    Maryland
    Posts
    1,970

    Default Re: Double taped breakers

    Quote Originally Posted by Thomas Kessel View Post
    To my knowledge, the only circuit breakers that may be rated for double taps(same conductor make and size) are the Square-D QO and homeline series.
    Cutler-Hammer also has some listed for two conductors .

    All answers based on unamended National Electrical codes.

  8. #8
    Join Date
    Feb 2009
    Location
    Southern Vancouver Island
    Posts
    4,607

    Default Re: Double taped breakers

    Jim is correct, Cutler-Hammer as well as Square D in the US.

    In Canada, HI's should know that the Schneider brand HO breakers are also rated for two connections.
    Schneider owns the Square D and Federal Pioneer brands. The Schneider panels are white and sold through Home Depot. The HO-style breakers have double jaws similar to the Square D style.

    Even though 2 connections are permitted on those breakers, they should both be the same gauge, so watch for that too.

    John Kogel, RHI, BC HI Lic #47455