Results 1 to 7 of 7
  1. #1
    Join Date
    Apr 2014
    Location
    VA
    Posts
    1

    Default Roof Trusses Bearing

    The following Roof Truss connection was made on a new house under construction. The 2x4 ledger strip is nailed to the LVL. No other support. Is this acceptable?
    IMG_44242.jpg


    Thanks,

    NM

    Similar Threads:
    Member Benefits1

  2. #2
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: Roof Trusses Bearing

    Quite possibly okay if ... IF ... if that ledger was SYP ... and IF it was bolted / nailed as specified to the member it is attached to .. and IF it was done in accordance with the approved truss engineering plan.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  3. #3
    Join Date
    Feb 2008
    Location
    Chicago IL
    Posts
    2,048

    Default Re: Roof Trusses Bearing

    As Jerry mentioned possible but highly unlikely. Require Developer to provide approved plans by licensed architect and review what is on those plans.

    www.aic-chicago.com
    773/844-4AIC
    "The Code is not a ceiling to reach but a floor to work up from"

  4. #4
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: Roof Trusses Bearing

    I was looking on my phone earlier - now on my computer ... and I will add another caveat: those trusses still don't look like they were field cut to fit that way ... but if they were field cut ...

    Whenever you see engineered trusses ... the key word in that is "engineered" and the "engineering" is all important. It all depends on what the engineering states.

    No approved engineering available, have a structural engineer design appropriate repairs (and "no repairs needed" may be "appropriate" ... all based on the signed and sealed engineer's letter).

    If there is approved engineering available (and there should be as engineered trusses are an engineered system), then it all depends on what the engineering shows.

    It is not uncommon to have heel bearing trusses like that for various situations ... but the trusses are not to be field modified to be like that (and those do not look like they were cut off in the field).

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  5. #5
    Join Date
    Aug 2011
    Location
    Hercules, CA
    Posts
    159

    Default Re: Roof Trusses Bearing

    I agree, the shop drawings from the manufacturer should show the support location conditions. I have never seen a truss bearing condition where the support is on the end grain of the wood as shown in the photo. I would be skeptical. Also, the vertical web must be laterally braced.

    Thom Huggett, PE, SE, CBO

  6. #6
    Join Date
    Oct 2010
    Location
    MONTREAL QUEBEC-CANADA
    Posts
    2,075

    Default Re: Roof Trusses Bearing

    Bearing would be the same as for joists. 1.5"

    Cornice overhang? Likely not much load.

    Robert Young's Montreal Home Inspection Services Inc.
    Call (514) 489-1887 or (514) 441-3732
    Our Motto; Putting information where you need it most, "In your hands.”

  7. #7
    Join Date
    Oct 2010
    Location
    MONTREAL QUEBEC-CANADA
    Posts
    2,075

    Default Re: Roof Trusses Bearing

    Morning Mark.
    Likely trusses require further fastening. ie: Mechanical hangers at the LVL.
    Ledger are used in deck. Same principle for the trusses I believe.

    I would look at/for;a. Fastener placement/spacing, b.Faster type, size and c. Count.

    LVL; Crown should face up. Doulded up; should be laminated/fastened together crowns facing each other opposing any bow.

    Best

    Robert Young's Montreal Home Inspection Services Inc.
    Call (514) 489-1887 or (514) 441-3732
    Our Motto; Putting information where you need it most, "In your hands.”