    Default Black iron gas pipe through concrete

    This is a black iron gas pipe in a garage. Meter is outside. Is there an issue with the concrete being in direct contact with the mortar? If so, is there a relatively easy fix or does the gas need to be shut off temporarily and the pipe removed to sleeve it?

    If there is an issue, can you please include a code reference if one applies?

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Inspection Referral

  2. #2
    Join Date
    Mar 2007
    Location
    Santa Rosa, CA
    Posts
    3,154

    Default Re: Black iron gas pipe through concrete

    Quote Originally Posted by Dave Rose View Post
    This is a black iron gas pipe in a garage. Meter is outside. Is there an issue with the concrete being in direct contact with the mortar? If so, is there a relatively easy fix or does the gas need to be shut off temporarily and the pipe removed to sleeve it?

    If there is an issue, can you please include a code reference if one applies?
    Quote Originally Posted by Dave Rose View Post
    This is a black iron gas pipe in a garage. Meter is outside. Is there an issue with the concrete being in direct contact with the mortar? If so, is there a relatively easy fix or does the gas need to be shut off temporarily and the pipe removed to sleeve it?

    If there is an issue, can you please include a code reference if one applies?
    I see there has been no answer from the teeming masses. I do not recall any restriction based solely on the pipe penetrating through concrete, although a sleeve would be a good idea for a couple of reasons. I can see no evidence of excessive corrosion.

    The only restriction that I recall is underground gas piping run through a foundation wall and/or a slab. Those are both covered in the UPC and IRC.

    Department of Redundancy Department
    Supreme Emperor of Hyperbole
    http://www.FullCircleInspect.com/

  3. #3
    Join Date
    Mar 2007
    Location
    New Mexico
    Posts
    1,352

    Default Re: Black iron gas pipe through concrete

    That is the way I see it through stucco here on every house. I don't see a problem with it. Yes, under the slab is a big difference.

    Jim Robinson
    New Mexico, USA

  4. #4
    Dave Rose's Avatar
    Dave Rose Guest

    Default Re: Black iron gas pipe through concrete

    Thank to those who responded. Her local gas company "black tagged" her meter (not sure what that means) after seeing this...I did the inspection months ago.


  5. #5
    Join Date
    Mar 2007
    Location
    Plano, Texas
    Posts
    4,245

    Default Re: Black iron gas pipe through concrete

    Quote Originally Posted by Dave Rose View Post
    This is a black iron gas pipe in a garage. Meter is outside. Is there an issue with the concrete being in direct contact with the mortar? If so, is there a relatively easy fix or does the gas need to be shut off temporarily and the pipe removed to sleeve it?

    If there is an issue, can you please include a code reference if one applies?
    If this is through a structural wall such as a concrete foundation, there should be a relieving arch or a sleeve (2 nominal sized larger, I think). Stucco and brick veneer are different.

    Last edited by Jim Luttrall; 08-29-2017 at 08:16 AM.
    Jim Luttrall
    www.MrInspector.net
    Plano, Texas

  6. #6
    Join Date
    Dec 2008
    Location
    Maryland
    Posts
    2,809

    Default Re: Black iron gas pipe through concrete

    Quote Originally Posted by Dave Rose View Post
    Thank to those who responded. Her local gas company "black tagged" her meter (not sure what that means) after seeing this...I did the inspection months ago.
    Red tag I know. Black tag please explain what it signifies. to

    Galvanized pipe has been found upon due to possible flaking. Uncoated pipe in concrete does deteriat faster though it is all about moisture.


  7. #7
    Join Date
    Mar 2007
    Location
    Santa Rosa, CA
    Posts
    3,154

    Default Re: Black iron gas pipe through concrete

    Quote Originally Posted by Dave Rose View Post
    Thank to those who responded. Her local gas company "black tagged" her meter (not sure what that means) after seeing this...I did the inspection months ago.
    Hey Dave,

    Did you ever get an answer as to why it was "black-tagged" and what the heck that means?

    Department of Redundancy Department
    Supreme Emperor of Hyperbole
    http://www.FullCircleInspect.com/

  8. #8
    Join Date
    Mar 2007
    Location
    Plano, Texas
    Posts
    4,245

    Default Re: Black iron gas pipe through concrete

    This is what I was thinking of:
    P2603.4 Pipes through foundation walls.
    A pipe that passes through a foundation wall shall be provided with a relieving arch or a pipe sleeve shall be built into the foundation wall. The sleeve shall be two pipe sizes greater than the pipe passing through the wall.
    (Borrowed from Jerry's post on another thread)

    Jim Luttrall
    www.MrInspector.net
    Plano, Texas

  9. #9
    Join Date
    Mar 2007
    Location
    Santa Rosa, CA
    Posts
    3,154

    Default Re: Black iron gas pipe through concrete

    Quote Originally Posted by Jim Luttrall View Post
    This is what I was thinking of:
    (Borrowed from Jerry's post on another thread)
    Augh! You beat me to it!

    Department of Redundancy Department
    Supreme Emperor of Hyperbole
    http://www.FullCircleInspect.com/

  10. #10
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: Black iron gas pipe through concrete

    But ... but ... but ... that's not a "foundation wall".

    Use one of the other references I posted for penetrations through exterior walls.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  11. #11
    Join Date
    Mar 2007
    Location
    Santa Rosa, CA
    Posts
    3,154

    Default Re: Black iron gas pipe through concrete

    Quote Originally Posted by Jerry Peck View Post
    But ... but ... but ... that's not a "foundation wall". Use one of the other references I posted for penetrations through exterior walls.
    Wait, it's not? It sure looks like one. Is a stemwall different from a foundation wall?

    Department of Redundancy Department
    Supreme Emperor of Hyperbole
    http://www.FullCircleInspect.com/

  12. #12
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: Black iron gas pipe through concrete

    Quote Originally Posted by Dave Rose View Post
    This is a black iron gas pipe in a garage. Meter is outside.
    Quote Originally Posted by Gunnar Alquist View Post
    Wait, it's not? It sure looks like one. Is a stemwall different from a foundation wall?
    That is going through a block wall, from outside to inside into a garage, the meter is outside the wall - at least that is what the original post said.

    That wall is no different than a block wall at the rear porch with a gas line going through it, or from outside to inside to a fireplace, or into a kitchen, etc.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  13. #13
    Join Date
    Sep 2017
    Location
    WV
    Posts
    34

    Default Re: Black iron gas pipe through concrete

    Quote Originally Posted by Dave Rose View Post
    This is a black iron gas pipe in a garage. Meter is outside. Is there an issue with the concrete being in direct contact with the mortar? If so, is there a relatively easy fix or does the gas need to be shut off temporarily and the pipe removed to sleeve it?

    If there is an issue, can you please include a code reference if one applies?
    Should have a sleeve with the annular space sealed to prevent weather and rodent intrusion. It is in the NFGC and in the FG section of the plumbing codes. A poly spit sleeve is the easiest fix and a little silicone caulk. Hardest part is chipping out the mortar of what looks like a nice job.