    Default TANKLESS WATER HEATER MOUNTED DIRECTLY BEHIND AC CONDENSER



    Tankless water heater mounted directly behind AC condenser. Less than 18 inches separates the condenser and water heater.

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Inspection Referral

  2. #2
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: TANKLESS WATER HEATER MOUNTED DIRECTLY BEHIND AC CONDENSER

    At a minimum:

    Mechanical equipment (it is) requires minimum 30" working space in front of the service access - that removable front cover.

    Electrical equipment (it is) requires 36" instead of just 30" in front of it.

    There may be other clearance issues too.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  3. #3
    Join Date
    Apr 2008
    Location
    McKinney Texas
    Posts
    501

    Default Re: TANKLESS WATER HEATER MOUNTED DIRECTLY BEHIND AC CONDENSER

    Quote Originally Posted by Jerry Peck View Post
    At a minimum:

    Mechanical equipment (it is) requires minimum 30" working space in front of the service access - that removable front cover.

    Electrical equipment (it is) requires 36" instead of just 30" in front of it.

    There may be other clearance issues too.
    Thanks Jerry.

    Gene


  4. #4
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: TANKLESS WATER HEATER MOUNTED DIRECTLY BEHIND AC CONDENSER

    Gene,

    I forgot to add - depending on the location of the service access area of that condenser unit (can't tell from the photo) those two clearances also apply to the condenser unit.

    Condenser unit service access is something which is frequently missed, and some condenser units are configured such that the service access is a debatable issue (which is where the installation instructions come into play - what they show is where the service access clearances and working space goes).

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  5. #5
    Join Date
    Apr 2008
    Location
    McKinney Texas
    Posts
    501

    Default Re: TANKLESS WATER HEATER MOUNTED DIRECTLY BEHIND AC CONDENSER

    Quote Originally Posted by Jerry Peck View Post
    Gene,

    I forgot to add - depending on the location of the service access area of that condenser unit (can't tell from the photo) those two clearances also apply to the condenser unit.

    Condenser unit service access is something which is frequently missed, and some condenser units are configured such that the service access is a debatable issue (which is where the installation instructions come into play - what they show is where the service access clearances and working space goes).

    Got it, thanks Jerry.

    Gene