Results 1 to 4 of 4

Thread: A/C shout Off

  1. #1
    Join Date
    Sep 2007
    Location
    San Antonio TX
    Posts
    88

    Default A/C shout Off

    Shut off for A/C compressor appears to be improperly located about 1' above ground.

    Would you call that out.
    How about stairs 2 in. out of level
    Thanks.

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    OREP Insurance

  2. #2
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: A/C shout Off

    Quote Originally Posted by Zibby Swieca View Post
    Shut off for A/C compressor appears to be improperly located about 1' above ground.

    Would you call that out.


    What says it cannot be mounted that way?

    Nothing. HOWEVER ... I would (and have) write it up as unsafe for the person who has to work on it. I ask my client 'Would you want to find your a/c technician or electrician laying on the ground beneath that, dead? The looks on their faces are priceless - they understand quite readily.

    By the way, that's a dryer vent cap, not a wall flashing, that the refrigerant lines are coming out of.

    And the service side of that condenser unit looks like it is facing the wall, and it is required to have at least 36" clearance in front of the service access area.

    How about stairs 2 in. out of level
    Now THAT is a problem, the maximum slope for a tread is 1/4" per foot, cross slope or in the direction of travel.

    "Assumption": The stair width is 3 feet. 3 feet times 1/4" per foot equals 3/4" maximum tread slope for a 3 foot wide stairway.

    That stair (with the "assumption" that it is 3 feet wide) slopes 2/3" per foot, that's .667 inch per foot, which is almost 11/16" per foot slope.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  3. #3
    Join Date
    Mar 2007
    Location
    Spring Hill (Nashville), TN
    Posts
    5,851

    Default Re: A/C shout Off

    Quote Originally Posted by Clay White View Post
    What about the A/C being located next to an openable window? Any requirements there?

    Nope!

    Scott Patterson, ACI
    Spring Hill, TN
    www.traceinspections.com

  4. #4
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: A/C shout Off

    Quote Originally Posted by Clay White View Post
    What about the A/C being located next to an openable window? Any requirements there?
    Clay,

    The key is you said (and the photo shows) "next to".

    If, however, that was "under" or "below" the operable window, *and*, that is an EERO, then it would be a problem as it would interfere with escape and rescue. If it was under an operable window which was not an EERO, then it would just be *stupid*.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •