Results 1 to 5 of 5
  1. #1
    K Robertson's Avatar
    K Robertson Guest

    Question Please help Identify This

    Found this in a service panal today. Anyone have any idea what it is and can it be installed this way. It was tapped into the 60 amp A/C Breaker and grounded to the neutral bus. ??


    The buyer said he thought it was some type of remote access devise.

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Last edited by K Robertson; 04-14-2007 at 08:21 PM. Reason: more information added
    Member Benefits1

  2. #2
    Join Date
    Mar 2007
    Location
    georgia
    Posts
    112

    Default Re: Please help Identify This

    looks like a lightining arrestor and no it is not installed correctly most breakers only allow one wire under the terminal.


  3. #3
    Tim Moreira's Avatar
    Tim Moreira Guest

    Default Re: Please help Identify This

    Here's what I found in the 05 NEC:

    Not exectally sure how or if it applies. Maybe Jerry can clarify this for us.

    280.2 Definition.
    Surge Arrester. A protective device for limiting surge voltages by discharging or bypassing surge current, and it also prevents continued flow of follow current while remaining capable of repeating these functions.

    280.3 Number Required.
    Where used at a point on a circuit, a surge arrester shall be connected to each ungrounded conductor. A single installation of such surge arresters shall be permitted to protect a number of interconnected circuits, provided that no circuit is exposed to surges while disconnected from the surge arresters.

    230.82 Equipment Connected to the Supply Side of Service Disconnect.
    Only the following equipment shall be permitted to be connected to the supply side of the service disconnecting means:
    (3) Instrument transformers (current and voltage), high-impedance shunts, load management devices, and surge arresters.

    ???


  4. #4
    Join Date
    Mar 2007
    Location
    Philadelphia PA
    Posts
    3,177

    Default Re: Please help Identify This

    Whatever it is, probably a surge device of some kind, it shouldn't be inside the panel enclosure.

    "There is no exception to the rule that every rule has an exception." -James Thurber, writer and cartoonist (1894-1961)
    www.ArnoldHomeInspections.com

  5. #5
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,036

    Default Re: Please help Identify This

    Quote Originally Posted by John Arnold View Post
    Whatever it is, probably a surge device of some kind, it shouldn't be inside the panel enclosure.
    Right.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •