Results 1 to 4 of 4
  1. #1
    Join Date
    Mar 2007
    Location
    Chicago, IL
    Posts
    2,797

    Default Refrigerant line protection at studs and top plates

    Does the IRC require refrigeration lines to be protected where they pass through studs and top plates (similar to the protection required for NM wiring)?

    Similar Threads:
    Crawl Space Creeper
    Michael Thomas
    Paragon Property Services Inc., Chicago IL
    http://paragoninspects.com

  2. #2
    James Duffin's Avatar
    James Duffin Guest

    Default Re: Refrigerant line protection at studs and top plates

    IRC Section M1308.2 says yes.


  3. #3
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,036

    Default Re: Refrigerant line protection at studs and top plates

    To add to James 'yes' ... the protection if closer to that required for plumbing pipes than for NM cable.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  4. #4
    Join Date
    Mar 2007
    Location
    Chicago, IL
    Posts
    2,797

    Default Re: Refrigerant line protection at studs and top plates

    Thanks as always to you both.

    Michael Thomas
    Paragon Property Services Inc., Chicago IL
    http://paragoninspects.com

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •