    Just wondering what everyone thought about CSST?

    CSST Settlement - Home Page

    I will sit back before I comment.

    Similar Threads:
    OREP Insurance

  2. #2
    Join Date
    Mar 2007
    Location
    Charlotte NC Licensed in NC and SC
    Posts
    597

    Default Re: CSST

    Just recently had a client call the manuf. (Tracpipe) and ask about this.

    I had been recommending the pipes be bonded to the GEC but Tracpipe says they only recommend it in high lightning zones, my area is a low to medium zone.

    Only one builder grounds theirs around here, all others never heard of it.

    No AHJ's around here are requiring it either, until permits pulled after 9/2007 then they (Meck. County)require the additional bonding to the GEC instead of just the bonding achieved through the furnace valve/cabinet.


    The new CSST called counterstrike has a black sheathing and does not need the additional bonding according to the manuf.

    Last edited by Bruce King; 01-28-2008 at 07:38 AM. Reason: new information added

  3. #3
    Join Date
    Mar 2007
    Location
    Philadelphia PA
    Posts
    3,177

    Default Re: CSST

    This has also been discussed a few times in the archives - try a search there.

    "There is no exception to the rule that every rule has an exception." -James Thurber, writer and cartoonist (1894-1961)
    www.ArnoldHomeInspections.com

  4. #4
    Mike Parks's Avatar
    Mike Parks Guest

  5. #5
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: CSST

    Code REQUIRES all metal gas piping be bonded to ground.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  6. #6

    Default Re: CSST

    Re: CSST
    WARDFLEX STEPSAVER

    Mike - thanks for the link. Click on their applications link and look at "furnaces and water heaters" - they're using black pipe!

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Jim
    Arlington VA
    ASHI, NOVA ASHI, VAREI

  7. #7
    Join Date
    Mar 2007
    Location
    Connecticut
    Posts
    1,828

    Default Re: CSST

    It dosen't matter what we think. What matters is what happens if we do not report what we see and know to be an item of concern. How much concern is left up to Laywers. Thats what they are for. We just see the ball and throw it at them.


  8. #8
    Join Date
    Mar 2007
    Location
    Spring Hill (Nashville), TN
    Posts
    5,851

    Default Re: CSST

    Well, as CSST is metal pipe, it needs to be grounded. What harm can come from grounding it even if the manufacturer does not require it.

    I started reporting ungrounded CSST about a year ago. I seldom get any arguments over it being grounded and when I do I just send a snip of the code to the folks.

    The problem is that the CSST pipe is so thin that lighting will punch a hole in it unlike black pipe. With the ground wire this gives the lighting a path to the ground. Kind of a simple explanation but I think it covers it fairly well.

    Scott Patterson, ACI
    Spring Hill, TN
    www.traceinspections.com

  9. #9
    Join Date
    Mar 2007
    Location
    Philadelphia PA
    Posts
    3,177

    Default Re: CSST

    If the CSST is connected to hard-pipe which is bonded, you're ok, according to Gastite.


  10. #10
    Nolan Kienitz's Avatar
    Nolan Kienitz Guest

    Default Re: CSST

    Quote Originally Posted by Mike Parks View Post
    Just wondering what everyone thought about CSST?

    CSST Settlement - Home Page

    I will sit back before I comment.
    Settlement regarding CSST closed last fall (2007). That website has been about for some time.

    As for CSST I don't have any particular problems with it as long as it is installed correctly.

    Frisco, TX (where I get a lot of HIs) is one of the highest hit rates for lightning strikes in the U.S.. They also have some of the strongest additional grounding requirements for residential construction. It is not just CSST that Frisco has written 'additional' grounding requirments for.

    Why wait ... GA and comment.


  11. #11
    Join Date
    Mar 2007
    Location
    Plano, Texas
    Posts
    4,245

    Default Re: CSST

    Nolan and others, I see the additional bonding in the Frisco new construction, but I have not found any specific information on their website. Do you have anything from them on that? I am guessing it is not just CSST bonding but whole house lightening protection.

    Also, I found something about a automatic flow shutoff valve on the gas entrance and branch piping. Any information on that?

    Jim Luttrall
    www.MrInspector.net
    Plano, Texas

  12. #12
    Jake Guerrero's Avatar
    Jake Guerrero Guest

    Default Re: CSST

    Jim,

    I've got a copy of the schematic for the gas pipe bonding from Frisco that also mentions an excessive gas flow shut-off valve.

    Let me know if you want me to send it to you. Since it's a scanned document and the lettering is small, I don't think it will post here on the forum very well.


  13. #13
    Nolan Kienitz's Avatar
    Nolan Kienitz Guest

    Default Re: CSST

    Quote Originally Posted by Jim Luttrall View Post
    Nolan and others, I see the additional bonding in the Frisco new construction, but I have not found any specific information on their website. Do you have anything from them on that? I am guessing it is not just CSST bonding but whole house lightening protection.

    Also, I found something about a automatic flow shutoff valve on the gas entrance and branch piping. Any information on that?
    Jim,

    Attached are a few scanned pages from a bunch of information I got from one of the Frisco City Code Officials. I went over to the "city hall" on Main West of Preston last summer to chat about some radiant barrier requirements I had heard about.

    Anyway ... I left with a bunch of hardcopy information from the official. The attached pages are from a 38-page document that is a supplement guideline to help residential house builders ... verbiage taken from the cover page.

    I think this may also answer your automatic flow shutoff valve question.

    Attached Files Attached Files

  14. #14
    Join Date
    Mar 2007
    Location
    Plano, Texas
    Posts
    4,245

    Default Re: CSST

    Thanks Nolan, thats what I was looking for!
    I guess the Frisco fire marshal had a big hand in drafting those standards.
    I have not see anything else as strict as theirs.
    I was at the TAREI meeting where one of the P.E. that does windstorm certifications said that the new standards for CSST required bonding at each section, but there is nothing like that on any of the manufacturer's sites except the single bonding location.
    Thanks, Jim

    Jim Luttrall
    www.MrInspector.net
    Plano, Texas

  15. #15
    Join Date
    Mar 2007
    Location
    Plano, Texas
    Posts
    4,245

    Default Re: CSST

    Jake shared this diagram with me. This is from Frisco, TX (the place where the CSST litigation started).
    I found it very interesting. Basically, they have amended to require bonding everything in the attic which is where most equipment is located here. I guess the idea is to try and afford some lightening protection.
    Also notice the gas flow shut off requirement.
    Thanks Jake.
    Jim

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Last edited by Jim Luttrall; 01-29-2008 at 03:09 PM.
    Jim Luttrall
    www.MrInspector.net
    Plano, Texas

  16. #16
    Join Date
    Apr 2007
    Location
    WESTMINSTER CO
    Posts
    1,152

    Default Re: CSST

    jake

    could you fax that schematic over to me---i'm in colorado and we have alot of lightning--i can't make out anything from the thread

    thanks charlie

    303-465-1811


  17. #17
    Jake Guerrero's Avatar
    Jake Guerrero Guest

    Default Re: CSST

    Charlie,

    Send me your email address and I'll attach and send it to you...easier for me.

    Jake


  18. #18
    Join Date
    Apr 2007
    Location
    WESTMINSTER CO
    Posts
    1,152

  19. #19
    Join Date
    Mar 2007
    Location
    Garland, TX
    Posts
    652

    Default Re: CSST

    Last few pages of this doc. have clear diagrams

    http://www.ciatx.org/downloadables/C...e_Brochure.pdf

    Charlie, I guess the hyperlink didn't attach correctly

    Last edited by BARRY ADAIR; 03-02-2008 at 09:41 AM.
    badair http://www.adairinspection.com Garland, TX 75042
    Commercial-Residential-Construction-EIFS-Stucco-ACMV-Infrared Thermography
    life is the random lottery of events followed by numerous narrow escapes...accept the good

  20. #20
    Join Date
    Apr 2007
    Location
    WESTMINSTER CO
    Posts
    1,152

    Default Re: CSST

    hey barry

    what doc. and what diagrams

    charlie


  21. #21
    Nolan Kienitz's Avatar
    Nolan Kienitz Guest

    Default Re: CSST

    Quote Originally Posted by CHARLIE VAN FLEET View Post
    hey barry

    what doc. and what diagrams

    charlie
    Its an Adobe PDF file.


  22. #22
    Join Date
    Apr 2007
    Location
    WESTMINSTER CO
    Posts
    1,152

    Default Re: CSST

    NOLAN
    DON'T WANT TO SOUND STUPID BUT WHERE DO I GO TO VIEW--YOUR WEB SITE--SORRY
    CHARLIE


  23. #23
    Nolan Kienitz's Avatar
    Nolan Kienitz Guest

    Default Re: CSST

    Quote Originally Posted by CHARLIE VAN FLEET View Post
    NOLAN
    DON'T WANT TO SOUND STUPID BUT WHERE DO I GO TO VIEW--YOUR WEB SITE--SORRY CHARLIE
    Charlie,

    Just click on my website URL at the bottom of this post. It will take you to the front page of the site.


  24. #24
    Join Date
    Apr 2007
    Location
    WESTMINSTER CO
    Posts
    1,152

    Default Re: CSST

    now i got it thanks nolan


  25. #25
    Robert Alexander's Avatar
    Robert Alexander Guest

    Default Re: CSST

    Funny thing is, even if something is NOT code (minimum building standard), if it poses a safety issue to my client, I write it up - period. We are NOT code (minimalist) inspectors. We are supposed to provide "value-add" to our clients (and protect ourselves along the way). We should definitely have code knowledge, but not all r/r write-ups I do are purely based on meeting or not meeting code requirements.

    I get tired of contractors citing code to me and I started using "professional workmanlike manner" or safety reasons to back up my recommendations for repair or replacement. I also try to be very specific about WHAT I am calling out and WHY.

    So many inspectors use the catch all phrase of "consult with licensed XYZ professional for repair recommendations..." blah, blah. Where is the value in that?

    O.K., what was it we were talking about anyway?... (-:

    Last edited by Robert Alexander; 05-08-2008 at 05:50 AM.

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •