    Sep 2008
    so so, California
    Default Ash dump under home
    Doesn't seem right to have an ash dump under the home in a crawlspace. Just looks like a fire hazard if the door is left open or whatever... Im sure there's nothing for this NFPA or ICC wise..is there?
    Oct 2007
    Wichita, KS
    Default Re: Ash dump under home
    From NFPA 211, 2019 Edition (and it's been there for many years):
    7.1.4.5 Cleanout openings and doors shall not be obstructed. Combustible material located or projected beyond the face of the chimney shall be kept a minimum of 18 in. (457 mm) away from the cleanout opening.
    7.1.4.6 Cleanout doors shall be permanently marked with a message equivalent to the following:
    WARNING: DO NOT OBSTRUCT. KEEP COMBUSTIBLE MATERIAL AT LEAST 18 in. (457 mm) AWAY FROM THIS DOOR.
    11.2.8 Ash Dumps. Cleanouts, if provided, shall be accessible and located so that ash removal will not create a hazard to combustible materials.
    Warmest Regards,
    Bart Ogden, President
    Home Safe Hearth & Chimney, Inc.
    Wichita, KS
    CSIA Master Chimney Sweep
    NFI Master Hearth Professional
    Sep 2008
    so so, California
    You are the man. much thanks
    It appears to me that the ash dump is located in an addition. By the concrete steps in the background it looks like this was originally the exterior of the house and has been closed in. I guess the door and firebox floor trap need to be sealed.
    And don't forget the plywood above is not installed with its face grain perpendicular to the supports.
    Sep 2008
    so so, California
    Well played sir...Good eye JP.