Results 1 to 22 of 22
  1. #1
    Join Date
    Mar 2010
    Location
    Ocala Florida
    Posts
    138

    Default 30 amp single pole breaker for 240v water heater

    1983 manufactured home (in sub / remote panel. I've not come across this before: 4500 watt water heater has only a 30 amp single pole breaker. Need help to explain why this IS or IS Not okay. It is the first breaker down below the main on the left side. Thanks, Mark

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    OREP Insurance

  2. #2
    Join Date
    Dec 2008
    Location
    Maryland
    Posts
    2,809

    Default Re: 30 amp single pole breaker for 240v water heater

    Can't see to well on phone, but it looks like a double pole 240 breaker 2nd down on left side.


  3. #3
    Join Date
    Mar 2010
    Location
    Ocala Florida
    Posts
    138

    Default Re: 30 amp single pole breaker for 240v water heater

    Quote Originally Posted by Garry Sorrells View Post
    Can't see to well on phone, but it looks like a double pole 240 breaker 2nd down on left side.
    Gary thanks but no it is the first down just under the main breaker on left.


  4. #4
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,040

    Default Re: 30 amp single pole breaker for 240v water heater

    Mark,

    Did you verify that the top left, single pole, 30 amp breaker shut the water heater off?

    I'm thinking the panel is mislabeled (breakers moved around over the years to add/remove/replace breakers).

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  5. #5
    Join Date
    Dec 2008
    Location
    Maryland
    Posts
    2,809

    Default Re: 30 amp single pole breaker for 240v water heater

    Did you look at the heater wiring?
    Heater can run with only one heating element wired.
    What is the wire going into heater?


  6. #6
    Join Date
    Mar 2010
    Location
    Ocala Florida
    Posts
    138

    Default Re: 30 amp single pole breaker for 240v water heater

    Quote Originally Posted by Jerry Peck View Post
    Mark,

    Did you verify that the top left, single pole, 30 amp breaker shut the water heater off?

    I'm thinking the panel is mislabeled (breakers moved around over the years to add/remove/replace breakers).
    Jerry, you were right. I went back out and found the 30 amp double pole (for water heater) in the main exterior panel not labeled. But could not find what the 30 amp single pole in the sub panel was for. This was a 4 pt inspect. and the home was filled to the max with tenants personal items / furniture and she was a little put out at the second visit so didn't figure it out. It was wired correctly with #10 so just let it go at that. Now; my question is: In what possible situation would you use a 30 amp single pole breaker. I'm thinking maybe some type of window ac which was not present. Home has brand new central ac package unit. As always, thanks for your help.


  7. #7
    Join Date
    Mar 2010
    Location
    Ocala Florida
    Posts
    138

    Default Re: 30 amp single pole breaker for 240v water heater

    Quote Originally Posted by Garry Sorrells View Post
    Did you look at the heater wiring?
    Heater can run with only one heating element wired.
    What is the wire going into heater?
    Gary, Unit is 4500 watt dual element with #10 wire. Thanks


  8. #8
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,040

    Default Re: 30 amp single pole breaker for 240v water heater

    Quote Originally Posted by Garry Sorrells View Post
    Did you look at the heater wiring?
    Heater can run with only one heating element wired.
    What is the wire going into heater?
    Quote Originally Posted by mark petty View Post
    Gary, Unit is 4500 watt dual element with #10 wire. Thanks
    Only one element is on at at time.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  9. #9
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,040

    Default Re: 30 amp single pole breaker for 240v water heater

    Quote Originally Posted by mark petty View Post
    Now; my question is: In what possible situation would you use a 30 amp single pole breaker. I'm thinking maybe some type of window ac which was not present.
    Some, many?, motors/appliances are setup to be wired either 120 volts or 240 volts by the installer, depending on what is provided.

    It may be possible that there was an old air conditioner there wired 30A 120v.

    Is the wire going to the single pole 30 amp breaker a #10?

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  10. #10
    Join Date
    Apr 2013
    Location
    High Springs, Florida
    Posts
    174

    Default Re: 30 amp single pole breaker for 240v water heater

    Why do you need all this for a simple 4 Point insurance inspection?


    www.1stproinspection.com

    Certified Master Inspector
    Like Us On Facebook
    https://www.facebook.com/1stproinspection/

  11. #11
    Join Date
    Mar 2007
    Location
    Santa Rosa, CA
    Posts
    3,154

    Default Re: 30 amp single pole breaker for 240v water heater

    What are motor home plugs rated at?

    Department of Redundancy Department
    Supreme Emperor of Hyperbole
    http://www.FullCircleInspect.com/

  12. #12
    Join Date
    Apr 2013
    Location
    High Springs, Florida
    Posts
    174

    Default Re: 30 amp single pole breaker for 240v water heater

    Quote Originally Posted by Gunnar Alquist View Post
    What are motor home plugs rated at?
    Yep! 30 amps


    www.1stproinspection.com

    Certified Master Inspector
    Like Us On Facebook
    https://www.facebook.com/1stproinspection/

  13. #13
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,040

    Default Re: 30 amp single pole breaker for 240v water heater

    Quote Originally Posted by Gunnar Alquist View Post
    What are motor home plugs rated at?
    30 amps, 120 volt for some (let's you plug into almost any camping site).

    50 amps, 120 volt / 240 volt (but no 240 volt loads) for others - a 50 amp service for a motor home restricts the motor home from plugging into some?/most? national parks and some state parks as they only have 20 amp / 30 amp supply.

    Pop-ups and travel trailers are likely 20 amp, with some being 30 amp (travel trailers likely have 30 amp, and some even have 50 amp).

    But ...

    Mark said:
    1983 manufactured home


    Which is not a motor home.

    Even a 1983 "mobile home" likely had a 50 amp service - regular 120 volt / 240 volt (which allows 240 volt loads.


    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  14. #14
    Join Date
    Mar 2010
    Location
    Ocala Florida
    Posts
    138

    Default Re: 30 amp single pole breaker for 240v water heater

    Quote Originally Posted by Jerry Peck View Post
    30 amps, 120 volt for some (let's you plug into almost any camping site).

    50 amps, 120 volt / 240 volt (but no 240 volt loads) for others - a 50 amp service for a motor home restricts the motor home from plugging into some?/most? national parks and some state parks as they only have 20 amp / 30 amp supply.

    Pop-ups and travel trailers are likely 20 amp, with some being 30 amp (travel trailers likely have 30 amp, and some even have 50 amp).

    But ...

    Mark said:


    Which is not a motor home.

    Even a 1983 "mobile home" likely had a 50 amp service - regular 120 volt / 240 volt (which allows 240 volt loads.[/COLOR]
    Thanks everyone; great help!


  15. #15
    Join Date
    Apr 2013
    Location
    High Springs, Florida
    Posts
    174

    Default Re: 30 amp single pole breaker for 240v water heater

    I have inspected many rv parks and most provide 60 amp down here.
    However , I want to know from the OP question what does this have to do with a Florida 4 Point inspection.


    www.1stproinspection.com

    Certified Master Inspector
    Like Us On Facebook
    https://www.facebook.com/1stproinspection/

  16. #16
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,040

    Default Re: 30 amp single pole breaker for 240v water heater

    Quote Originally Posted by Roy Lewis View Post
    I have inspected many rv parks and most provide 60 amp down here.
    60 amp?

    For an RV park or an older mobile home park?

    The standard RV cords and plugs, and the standard RV power boxes, are 50 amp / 30 amp / 20 amp combinations (the 20 amp receptacles are, of course, GFCI protected.

    However , I want to know from the OP question what does this have to do with a Florida 4 Point inspection.
    He didn't say the 30 amp breaker had anything to do with a Florida 4 Point inspection. He was questioning the water heater breaker at the time.

    Are you saying that looking at the water heater, the electrical panel, breakers, and wiring are NOT part of a Florida 4 Point Inspection? Seems as though something caught you by surprise and you are trying to figure it out by pressing Mark for what he does and why.

    This is what IS SUPPOSED TO BE DONE for a Florida 4 Point Inspection:
    https://www.citizensfla.com/document...6-3a796c675a7f

    Are you NOT doing that?

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  17. #17
    Join Date
    Mar 2007
    Location
    Santa Rosa, CA
    Posts
    3,154

    Default Re: 30 amp single pole breaker for 240v water heater

    Quote Originally Posted by Jerry Peck View Post
    30 amps, 120 volt for some (let's you plug into almost any camping site).

    50 amps, 120 volt / 240 volt (but no 240 volt loads) for others - a 50 amp service for a motor home restricts the motor home from plugging into some?/most? national parks and some state parks as they only have 20 amp / 30 amp supply.
    Pop-ups and travel trailers are likely 20 amp, with some being 30 amp (travel trailers likely have 30 amp, and some even have 50 amp).
    But ...
    Mark said:
    Which is not a motor home.
    Even a 1983 "mobile home" likely had a 50 amp service - regular 120 volt / 240 volt (which allows 240 volt loads.[/COLOR]
    But...
    That doesn't mean that a manufactured/mobile home owner cannot own a motor home or travel trailer.

    However, presumably Mark would have noticed a 30A 120V outlet at the exterior of the home.

    Department of Redundancy Department
    Supreme Emperor of Hyperbole
    http://www.FullCircleInspect.com/

  18. #18
    Join Date
    Oct 2010
    Location
    MONTREAL QUEBEC-CANADA
    Posts
    2,075

    Default Re: 30 amp single pole breaker for 240v water heater

    Quote Originally Posted by mark petty View Post
    1983 manufactured home (in sub / remote panel. I've not come across this before: 4500 watt water heater has only a 30 amp single pole breaker. Need help to explain why this IS or IS Not okay. It is the first breaker down below the main on the left side. Thanks, Mark
    To find the current draw, you just divide this number by the voltage at which it operates, which is either 120 volts or 240 volts. Then, multiply this number by 125 percent. An easy way to do this is to divide it by 100 and then multiply it by 125. The rating of your circuit breaker must be larger than this total.

    Robert Young's Montreal Home Inspection Services Inc.
    Call (514) 489-1887 or (514) 441-3732
    Our Motto; Putting information where you need it most, "In your hands.”

  19. #19
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,040

    Default Re: 30 amp single pole breaker for 240v water heater

    Quote Originally Posted by Gunnar Alquist View Post
    But...
    That doesn't mean that a manufactured/mobile home owner cannot own a motor home or travel trailer.
    One of my thoughts too ... followed by 'nah, not with them living in an old 1983 mobile home'.

    Could be, but I reasoned that off the list ... possibly erroneously ... except that a mobile home has an outside service box it connects to, so I figured why run to the mobile home box, then back out, why not just run it from from the outside service at the pole/pedestal? (There are potential reasons why, but now we're really going into the guesswork aspect.)

    Last edited by Jerry Peck; 07-17-2019 at 06:08 AM. Reason: Speelin'
    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  20. #20
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,040

    Default Re: 30 amp single pole breaker for 240v water heater

    Quote Originally Posted by ROBERT YOUNG View Post
    Why do you say it is a 120V single pole OCPD and not 1P - 120/240 Square D 120/240 V OCPD?
    Robert,

    Some of your recent posts have me concerned about you ...

    Such as a one pole (single pole) breaker being "and not 1P - 120/240" .. a 240 volt breaker has to poles (oh, I got an error on the link, said site could not be reached).

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  21. #21
    Join Date
    Mar 2007
    Location
    Santa Rosa, CA
    Posts
    3,154

    Default Re: 30 amp single pole breaker for 240v water heater

    Quote Originally Posted by Jerry Peck View Post
    One of my thoughts too ... followed by 'nah, not with them living in an old 1983 mobile home'.
    You're probably right.

    Department of Redundancy Department
    Supreme Emperor of Hyperbole
    http://www.FullCircleInspect.com/

  22. #22
    Join Date
    Oct 2010
    Location
    MONTREAL QUEBEC-CANADA
    Posts
    2,075

    Default Re: 30 amp single pole breaker for 240v water heater

    Quote Originally Posted by Jerry Peck View Post
    Robert,

    Some of your recent posts have me concerned about you ...

    Such as a one pole (single pole) breaker being "and not 1P - 120/240" .. a 240 volt breaker has to poles (oh, I got an error on the link, said site could not be reached).
    Sorry. I will try to do better.

    Robert Young's Montreal Home Inspection Services Inc.
    Call (514) 489-1887 or (514) 441-3732
    Our Motto; Putting information where you need it most, "In your hands.”

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •